an electrical question

have a circuit protected by a ground fault outlet. I have my outdoor lights and fountain pump on it. Lights go off and on using an analog time clock. I have the fountain on a z wave plug adapter.

Landscape lights are all LED and when the circuit switches on each night there is no issue. I try to work the pump, the ground fault kicks when the in rush load from the pump occurs. I am fairly certain the ground fault is a 15amp outlet.

Can anyone tell me what the issue might be? Do I up size the GF outlet to say 20amp. Pump runs fine when I reset the GF outlet after it has tripped. Thoughts?

__________________
'86 944T black/red, chip, fuchs 8's and 9's- Sold
'97 Boxster silver/red, big mistake - Sold
'99 C2, silver/black, RoW M030 - sold
"69 912 white w/ '86 3.2L (like the pic, just not the pic)
Old 07-31-2019, 07:47 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #1 (permalink)
Registered
 
peppy's Avatar
 
Join Date: Aug 2007
Location: Kenbridge VA
Posts: 4,269
Not an expert, but I think electric motors can trip GFI outlets. That's why refrigerators don't have to have them.

Going to a 20A GFI depends on the wire size and the amperage of the breaker.
__________________
Peppy
2011 BMW 335d
1988 Targa 3.4
2001 Jetta TDI dead
1982 Chevette Diesel SOLD
Old 07-31-2019, 08:00 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #2 (permalink)
Platinum Member
 
dad911's Avatar
 
Join Date: Jul 2001
Location: Leave the gun. Take the cannoli.
Posts: 20,936
If it one of those cheap fountain pumps, try replacing it. There may be a reason it's tripping, like moisture in the case

Or test it on the bathroom GFI circuit and see it it trips that too.
__________________
The truth is that while those on the left - particularly the far left - claim to be tolerant and welcoming of diversity, in reality many are quite intolerant of anyone not embracing their radical views. - Charlie Kirk
Old 07-31-2019, 08:11 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #3 (permalink)
You do not have permissi
 
john70t's Avatar
 
Join Date: Aug 2001
Location: midwest
Posts: 39,824
Quote:
Originally Posted by peppy View Post
Not an expert, but I think electric motors can trip GFI outlets. That's why refrigerators don't have to have them.
A few years back I installed GFIs to the kitchen at mom's snowbird condo.
They worked fine for months after that.

What I didn't realize (or check) was that the fridge was series-wired to that last countertop outlet...
It shouldn't have been wired that way by today's electric code, I believe.
Microwave and hair driers also want their own separate breaker.

She left for the rest of the year and the GFI tripped at some point during that time.
And the house checker did not notice the smell.

When we returned, there were maggots and black puddles on the floor and the inside was black hell.
The fridge did not restart.
It was 'an experience'.
Old 07-31-2019, 09:15 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #4 (permalink)
Brew Master
 
cabmandone's Avatar
 
Join Date: Jul 2013
Location: Delphos OH
Posts: 32,062
Garage
You'd have to check the supply wire size to determine if you could go up to a 20 amp. Generally you need at least 12/2 with ground for a 20 amp circuit. It sounds like the GFI is tripping with only the pump so it would seem there is an issue with the pump. It's my understanding that a GFCI doesn't protect against over current.
__________________
Nick

Last edited by cabmandone; 07-31-2019 at 10:45 AM..
Old 07-31-2019, 10:42 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #5 (permalink)
Registered
 
Join Date: Oct 2005
Location: Capistrano Beach, Ca.
Posts: 7,235
Quote:
Originally Posted by cabmando View Post
You'd have to check the supply wire size to determine if you could go up to a 20 amp. Generally you need at least 12/2 with ground for a 20 amp circuit. It sounds like the GFI is tripping with only the pump so it would seem there is an issue with the pump. It's my understanding that a GFCI doesn't protect against over current.
This is my understanding as well (bold.)

GFCI monitor amp differential between the HOT and NEUTRAL lines. If the amps drawn by the HOT is more than the "return" amps of the NEUTRAL, the GFCI trips because there is a "leakage" of current somewhere in the circuit.

I would first try the pump without the z wave adapter, just to eliminate some issue with that device. If the pump still trips the GCFI, replace the pump or double check the wiring connections for the pump. There seems to be an initial current leak when the pump is first started, but disappears when restarted.
__________________
L.J.
Recovering Porsche-holic
Gave up trying to stay clean
Stabilized on a Pelican I.V. drip

Last edited by ossiblue; 07-31-2019 at 04:42 PM..
Old 07-31-2019, 11:33 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #6 (permalink)
Registered
 
Cajundaddy's Avatar
 
Join Date: Sep 2010
Location: Southern Idaho
Posts: 5,261
Garage
Two possibilities. Either you have a fountain pump with some current leakage to ground or the GFCI has failed and is nuisance tripping. Changing the wire size or breaker will not solve the problem. 99% of the time it is a failed fountain pump so I would test for continuity between hot to ground on the pump wiring. Anything above OL (zero) is a grounded pump that needs replacing.
__________________
2009 Cayman PDK
With a few tweaks
Old 08-01-2019, 09:20 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #7 (permalink)
Get off my lawn!
 
GH85Carrera's Avatar
 
Join Date: Nov 2007
Location: Oklahoma
Posts: 84,752
Garage
We have a small fountain in our front garden, and a large one in our Kio pond for the waterfall for aeration of the water. Both are on GFI circuits. Different circuits, and they do pop on occasion. The one in front got to be overly sensitive, and I just replaced it. The one in back for the Koi pond is a 1/3 HP pump, 3000 GPH of Water @ 5 Ft. of Head pressure. It runs 24/7/365. The GFI has tripped, but once was from ants getting into the electrical box in the garden area, and once was after 10 inches of rain in 24 hours.

So GFI works for electric motors just fine, but they do not cycle on on off like a fridge.
__________________
Glen
49 Year member of the Porsche Club of America
1985 911 Carrera; 2017 Macan
1986 El Camino with Fuel Injected 350 Crate Engine
My Motto: I will never be too old to have a happy childhood!
Old 08-01-2019, 10:40 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #8 (permalink)
Serial Lurker
 
ledhedsymbols's Avatar
 
Join Date: Oct 2005
Location: Mount Vernon WA
Posts: 1,252
Send a message via AIM to ledhedsymbols
Quote:
Originally Posted by Cajundaddy View Post
Two possibilities. Either you have a fountain pump with some current leakage to ground or the GFCI has failed and is nuisance tripping. Changing the wire size or breaker will not solve the problem. 99% of the time it is a failed fountain pump so I would test for continuity between hot to ground on the pump wiring. Anything above OL (zero) is a grounded pump that needs replacing.
Bingo

If the pump tests out, then consider the GFCI recep might be getting soft. It's most likely doing it's job measuring current delta between hot and neutral.
Old 08-01-2019, 04:59 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #9 (permalink)
Registered
 
Rtrorkt's Avatar
 
Join Date: Jul 2010
Location: Where ever I am
Posts: 4,204
Thanks to all who answered. Was forced to put a new pump in (long story) and did so with a high quality fountain pump. There is an in ground connection between the pump wiring and the wire I ran to the outlet. Will check that to be sure the connections are tight. I will get the continuity tested.

Again, thank you all for the considered responses
__________________
'86 944T black/red, chip, fuchs 8's and 9's- Sold
'97 Boxster silver/red, big mistake - Sold
'99 C2, silver/black, RoW M030 - sold
"69 912 white w/ '86 3.2L (like the pic, just not the pic)
Old 08-03-2019, 08:43 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #10 (permalink)
Platinum Member
 
dad911's Avatar
 
Join Date: Jul 2001
Location: Leave the gun. Take the cannoli.
Posts: 20,936
Quote:
Originally Posted by Rtrorkt View Post
......... There is an in ground connection between the pump wiring and the wire I ran to the outlet..........

__________________
The truth is that while those on the left - particularly the far left - claim to be tolerant and welcoming of diversity, in reality many are quite intolerant of anyone not embracing their radical views. - Charlie Kirk
Old 08-03-2019, 01:49 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #11 (permalink)
Reply


 


All times are GMT -8. The time now is 01:59 AM.


 
Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2025, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2025 Pelican Parts, LLC - Posts may be archived for display on the Pelican Parts Website -    DMCA Registered Agent Contact Page
 

DTO Garage Plus vBulletin Plugins by Drive Thru Online, Inc.