Have not sized transformers for motor loads for a long time, but how many HP is your compressor? never mind I looked at your link 5hp 22A, looks like it is rated for 31A. The starting current for that compressor motor would be pretty high.
__________________
87 930, Last edited by 908/930; 06-06-2020 at 10:54 AM.. |
||
![]() |
|
Platinum Member
Join Date: Jul 2001
Location: Leave the gun. Take the cannoli.
Posts: 20,989
|
I believe that rating is for the boost/buck portion of the transformer(12/24v)
Follow the link shaun posted and it's 30/60 amp.
__________________
The truth is that while those on the left - particularly the far left - claim to be tolerant and welcoming of diversity, in reality many are quite intolerant of anyone not embracing their radical views. - Charlie Kirk |
||
![]() |
|
Registered
Join Date: Dec 2001
Location: Cambridge, MA
Posts: 44,367
|
Pulled transformer apart, wiring is charred. No time for inspection. More to come.
Interestingly, the dryer did work plugged into it so it may be salvageable. Or not.
__________________
Tru6 Restoration & Design |
||
![]() |
|
Registered
|
first thought is undersized
__________________
Chris the more i learn, the less i know |
||
![]() |
|
....
Join Date: Feb 2008
Posts: 18,807
|
So would there be a benefit to oversizing a transformer for longevity purposes?
__________________
dolor et pavor Copyright |
||
![]() |
|
Registered
Join Date: Sep 2009
Location: North of You
Posts: 9,160
|
It's probably salvageable. Check continuity with a multimeter on primary and secondary. Check the operating temp with a laser thermometer. Hot=early death. Cool=infinite life.
__________________
"A machine you build yourself is a vote for a different way of life. There are things you have to earn with your hands." |
||
![]() |
|
![]() |
Registered
Join Date: Dec 2001
Location: Cambridge, MA
Posts: 44,367
|
I'll post some pics tomorrow of the wiring.
__________________
Tru6 Restoration & Design |
||
![]() |
|
Registered
Join Date: Dec 2001
Location: Cambridge, MA
Posts: 44,367
|
X2 and X3 got mighty hot.
![]() ![]() ![]()
__________________
Tru6 Restoration & Design |
||
![]() |
|
Registered
Join Date: Sep 2009
Location: North of You
Posts: 9,160
|
I think you can save it. It should be hi-potted to be sure it's okay.
Put a fan on it when it runs next time...and a cooling plate too if needed.
__________________
"A machine you build yourself is a vote for a different way of life. There are things you have to earn with your hands." |
||
![]() |
|
Platinum Member
Join Date: Jul 2001
Location: Leave the gun. Take the cannoli.
Posts: 20,989
|
The wires actually look good to the transformer. Looks like (from hundreds of miles away) this connection in this spot arced and failed:
![]() Looks like the smoke released from the connections, not the transformer. If you want to test the transformer, you should get a 'continuity' reading for each individual coil to see if it burned open. Disconnect all the wires, with an ohmmeter there should be able to get a measurement at each coil (greater than infinity). X1 & X2, X3 & X4, H1 & H2, H3 & H4. The 2 X coils should read about the same, as should the 2 H coils.
__________________
The truth is that while those on the left - particularly the far left - claim to be tolerant and welcoming of diversity, in reality many are quite intolerant of anyone not embracing their radical views. - Charlie Kirk |
||
![]() |
|
Registered
Join Date: Dec 2001
Location: Cambridge, MA
Posts: 44,367
|
Thanks '90 and Dad.
The failure is at the junction of X2 and X3. That junction burned the connector off and melted away the exposed twisted wires. ![]()
__________________
Tru6 Restoration & Design |
||
![]() |
|
Platinum Member
Join Date: Jul 2001
Location: Leave the gun. Take the cannoli.
Posts: 20,989
|
![]() What gauge is this wire? How many amp breaker on this circuit? Based on the Compressor specs, should be 30A breaker, and wire at least 10AWG.
__________________
The truth is that while those on the left - particularly the far left - claim to be tolerant and welcoming of diversity, in reality many are quite intolerant of anyone not embracing their radical views. - Charlie Kirk |
||
![]() |
|
Registered
Join Date: Dec 2001
Location: Cambridge, MA
Posts: 44,367
|
Just looked, it's 12/3 solid Romex.
__________________
Tru6 Restoration & Design |
||
![]() |
|
Platinum Member
Join Date: Jul 2001
Location: Leave the gun. Take the cannoli.
Posts: 20,989
|
Then I suspect you can clean up the connections, and your back in business.
__________________
The truth is that while those on the left - particularly the far left - claim to be tolerant and welcoming of diversity, in reality many are quite intolerant of anyone not embracing their radical views. - Charlie Kirk |
||
![]() |
|
Registered
Join Date: Dec 2001
Location: Cambridge, MA
Posts: 44,367
|
Any idea why it did what it did? Should I at least get the 10/3 wire?
__________________
Tru6 Restoration & Design |
||
![]() |
|
Platinum Member
Join Date: Jul 2001
Location: Leave the gun. Take the cannoli.
Posts: 20,989
|
In general, 12 wire feeds are rated for 20 amps and protected by a 20 amp breaker.
The compressor specs say it draws 22 amps, and recommend a 30 amp breaker, which would typically be #10 wire. If it's a long way to the panel, or if there is a 20 amp breaker on #12, you should probably address this.
__________________
The truth is that while those on the left - particularly the far left - claim to be tolerant and welcoming of diversity, in reality many are quite intolerant of anyone not embracing their radical views. - Charlie Kirk Last edited by dad911; 06-07-2020 at 08:30 AM.. |
||
![]() |
|
Registered
Join Date: Dec 2001
Location: Cambridge, MA
Posts: 44,367
|
it's a 30A breaker. A professional electrician ran the wire 60 feet or so from the box to the new outlet which was for a silkscreen exposure unit. I think it had a 4500W metal halide bulb. Took massive amounts of e-. The brightness was incredible. I will have to look at what gauge wire the electrician ran.
__________________
Tru6 Restoration & Design |
||
![]() |
|
Registered
Join Date: Dec 2001
Location: Cambridge, MA
Posts: 44,367
|
The transformer is next to the outlet with the compressor.
__________________
Tru6 Restoration & Design |
||
![]() |
|
![]() |
Platinum Member
Join Date: Jul 2001
Location: Leave the gun. Take the cannoli.
Posts: 20,989
|
Quote:
I didn't sleep in a Holiday Inn, and I'm more familiar with Residential than Commercial, but in general the wire is sized for the load, then a breaker is sized to protect the wire, if that makes sense. #12 is generally rated for 20amp, #10 for 30amp (copper). The specs for the compressor say 22 amp, 30amp breaker. If you have been getting by not tripping a 20 amp breaker, and it's a short run to the panel, you can probably leave well enough alone. If it's a 30 amp breaker on #12 wire, that's not allowed residential, and I suspect commercial also. If it's a long run to the panel, you would also get less voltage drop with #10 wire.
__________________
The truth is that while those on the left - particularly the far left - claim to be tolerant and welcoming of diversity, in reality many are quite intolerant of anyone not embracing their radical views. - Charlie Kirk |
||
![]() |
|
Platinum Member
Join Date: Jul 2001
Location: Leave the gun. Take the cannoli.
Posts: 20,989
|
So the #12 just goes a few feet from transformet to the outlet? Definitely swap.