I hear what everyone is saying and I will submit a photo of the codes on the wires (tonight, after my day job).

Yes, I am using what I have laying around however, it is the wire that was recommended by my electrician when installing 220v for my dryer. I purchased a 100' spool which was about $300 and I am using the remaining for my stove/oven. Regardless, I will report back on the exact specifications. The wire is not Romex, I merely used romex as an example as this is very thick individual strands that are encased in a black wrap which states 600v plus a bunch of other stuff.

My primary question was about the conduit as I thought that would be the safest until our plant engineer told me he didn't think I should be doing that. However, on all of my projects, I want to follow the proper code. I have a friend that is a contractor that will be coming over this weekend to review my work.


Last edited by Tidybuoy; 04-23-2021 at 08:42 AM..
Old 04-22-2021, 12:42 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #21 (permalink)
Registered
 
Join Date: Mar 2004
Location: Los Angeles
Posts: 17,412
Quote:
Originally Posted by Tidybuoy View Post
I hear what everyone is saying and I will submit a photo of the codes on the wires (tonight, after my day job).

Yes, I am using what I have laying around however, it is the wire that was recommended by my electrician when installing 220v for my dryer. I purchased a 150' spool which was about $300 and I am using the remaining for my stove/oven. Regardless, I will report back on the exact specifications. The wire is not Romex, I merely used romex as an example as this is very thick individual strands that are encased in a black wrap which states 600v plus a bunch of other stuff.

My primary question was about the conduit as I thought that would be the safest until our plant engineer told me he didn't think I should be doing that. However, on all of my projects, I want to follow the proper code. I have a friend that is a contractor that will be coming over this weekend to review my work.
Romex will sweat inside conduit.
Old 04-22-2021, 12:49 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #22 (permalink)
Registered
 
Join Date: Mar 2005
Location: Jersey Shore
Posts: 1,084
Garage
You appear to to have 6/3 romex inserted into fmc.
The potential for heat generation is minimal.
Two 180* phases with a neutral and a ground will offset and cancel. It's not like you are running a single conductor in an enclosed space.
You went over and above sleeving in the fmc, worried about potential damage from rodents and whatnot, but i hope you at least put a bushing on both ends of the conduit.
__________________
Chris
the more i learn, the less i know
Old 04-22-2021, 01:58 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #23 (permalink)
Registered
 
Join Date: Jun 2003
Location: Fresno, CA
Posts: 7,787
Quote:
Originally Posted by carambola View Post
i hope you at least put a bushing on both ends of the conduit.
On the fuse box end, there is a solid 1" heavy conduit that comes out of the circuit breaker box downwards and then curves into the foundation (about 5' total) of the house and ends. This is something that must stay as it is cemented into the house.

After that, my flexible conduit is connected via a threaded connection to the permanent fuse box pipe.

The flexible conduit is then routed to it's final destination and strapped to the bottom of the 4x6 floor joists under the house. The flexible conduit is then routed up and thru the wall to it's final destination.

I will take photos of the wiring tonight to help determine if it needs to be inside conduit or not. We'll go from there. My only regret is that I'm gonna have to crawl under the house again - I too old for this S#!T
Old 04-22-2021, 02:28 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #24 (permalink)
Registered
 
Join Date: Mar 2005
Location: Jersey Shore
Posts: 1,084
Garage
If you do it right, it's an ab workout.
__________________
Chris
the more i learn, the less i know
Old 04-22-2021, 02:38 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #25 (permalink)
Senior Member
 
Superman's Avatar
 
Join Date: Feb 2000
Location: Lacey, WA. USA
Posts: 25,310
You'd think that over-designing the installation would get you a pat on the back. Using the proper non-conduit cable, and then protecting it in conduit. Makes sense, but the inspector may very possibly fail it. I knew of one installation which the inspectors failed, causing the builder to start over. It was "direct burial" cable, perfectly suited for just burying (at the proper depth). Builder pulled it through conduit for extra protection. Fail.

Who knew? Electrical inspectors are persnickety.
__________________
Man of Carbon Fiber (stronger than steel)

Mocha 1978 911SC. "Coco"
Old 04-22-2021, 03:56 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #26 (permalink)
 
You do not have permissi
 
john70t's Avatar
 
Join Date: Aug 2001
Location: midwest
Posts: 39,937
Small tangent:
"Not basement but a crawl space"

What kind of ventilation is going through the foundation there?
Critters will get in and make a home i.e. poop if they can.

Is the underside of the crawl space going to be vapor-barrier sealed from ground or below the joists?
That space where the wire runs through might be considered 'exterior' to code and might require different specs.
IDK.

As a layman, my first thought is a sealed full floor wrap up to the rim/floor joists to prevent ground radon/moisture/fumes from getting into the house.

(sorry for tangent just some random thoughts)
__________________
Meanwhile other things are still happening.
Old 04-22-2021, 04:07 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #27 (permalink)
unindicted co-conspirator
 
looneybin's Avatar
 
Join Date: Jul 2007
Location: Fresno, CA
Posts: 1,660
Yep, just run the bundled wire exposed stapled to the underside of the joists,
Enclosing it in conduit could cause condensation and is not code approved.
Only single strand wire is allowed in conduit
__________________
'03 996 - sport exhaust, sport seats, M030 sport suspension, stability control, IMS Solution
‘86 928S3 - barn find project car
Old 04-22-2021, 06:15 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #28 (permalink)
Registered
 
Join Date: Sep 2009
Location: North of You
Posts: 9,160
Quote:
Originally Posted by carambola View Post
You appear to to have 6/3 romex inserted into fmc.
The potential for heat generation is minimal.
Two 180* phases with a neutral and a ground will offset and cancel. It's not like you are running a single conductor in an enclosed space.
You went over and above sleeving in the fmc, worried about potential damage from rodents and whatnot, but i hope you at least put a bushing on both ends of the conduit.
He already said it's not Romex, I am guessing SOW now.

We aren't debating 'safe' any more, it's to code, or not to code. And my guess is it's not.
__________________
"A machine you build yourself is a vote for a different way of life. There are things you have to earn with your hands."
Old 04-23-2021, 04:30 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #29 (permalink)
Registered
 
wdfifteen's Avatar
 
Join Date: Mar 2008
Location: SW Ohio
Posts: 29,336
Garage
Quote:
Originally Posted by Tidybuoy View Post
The wire is not Romex, I merely used romex as an example as this is very thick individual strands that are encased in a black wrap which states 600v plus a bunch of other stuff.
The "other stuff" should include the wire gauge, which is VERY important.
Look at the oven and see how many amps it draws. I'm sure some of the experts here can take that information and calculate what gauge you need for that length of run.
For a crawl space I would critter-proof the system with new individual wires run through your conduit.
__________________
.
Old 04-23-2021, 08:34 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #30 (permalink)
Registered
 
Join Date: Jun 2003
Location: Fresno, CA
Posts: 7,787
Update:

The code on the wiring is as follows:
Romex (R) Simpull (7M) AWG 6 CU7 CDR With AC 10 Ground Type NM-B 600 Volts

I was incorrect on my previous comments on Romex. My thinking was that this wire is not like common household outlet wiring (i.e., Romex).





Old 04-23-2021, 08:36 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #31 (permalink)
Registered
 
Join Date: Sep 2009
Location: North of You
Posts: 9,160
Since it's not exterior I believe you can run that direct.

Someone from CA should confirm it meets your code.
__________________
"A machine you build yourself is a vote for a different way of life. There are things you have to earn with your hands."
Old 04-23-2021, 08:59 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #32 (permalink)
Registered
 
Join Date: Mar 2004
Location: Los Angeles
Posts: 17,412
Yep. Can't be exposed to light. As long s its under the house and run in-wall, you will be fine. 6 gauge, that's a big puppy. How many amps does this oven draw?
Old 04-23-2021, 09:05 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #33 (permalink)
Evil Genius
 
Rusty Heap's Avatar
 
Join Date: May 2006
Location: On top of my BBQ
Posts: 5,650
Garage
6 awg is a 50 amp circuit
__________________
Life is a big ocean to swim in.

Wag more, bark less.
Old 04-23-2021, 09:07 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #34 (permalink)
Registered
 
Zeke's Avatar
 
Join Date: Jan 2002
Location: Long Beach CA, the sewer by the sea.
Posts: 37,792
Thinking that NM cable cannot be placed in conduit is one of the most perpetrated falsehoods in the electrical trade. In fact, under certain circumstances where damage is imminent, it is required.

However, the issue is conduit wire fill. I didn't look it up but 6/3 with ground in 1.5" conduit should meet wire fill requirements. (In fact, I did look it up, but not in the NEC. Says wire fill must not exceed 53%)

One thing against pulling NM, NMC and NMS cables in any conduit is the pull itself. I would pull the cable into the conduit outside while the conduit ls laid out straight and clamped. Of course I would have determined the needed length first and left a foot of extra cable out at each end for make up.

There are not many cables that cannot be in conduit unless it's buried (wet location). And NM (Romex) is definitely one of those. that can't be used in wet locations. For that you need individual wires rated THWN. In fact MHF (mobile home feeder used a lot for direct burial between buildings) MUST be in conduit once above ground. It is terminated in a panel located as close to the riser as possible and still meet location requirements. (That was just an example for dispelling the myth.)
Old 04-23-2021, 09:32 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #35 (permalink)
Registered
 
Zeke's Avatar
 
Join Date: Jan 2002
Location: Long Beach CA, the sewer by the sea.
Posts: 37,792
Note to the above: when determining wire fill one must measure the widest part of a wire bundle to calculate area by using a pi formula either by radius or diameter to determine the area in a circle form even if the cross section of the cable is not a circle. In the case of 12/2 Romex with ground, that's about 1/2" on the flat side so no way will 1/2" conduit be large enough. 3/4 does that job.
Old 04-23-2021, 09:52 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #36 (permalink)
Registered
 
Join Date: Mar 2005
Location: Jersey Shore
Posts: 1,084
Garage
334.15 (C), you’re good

Old 04-23-2021, 10:58 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #37 (permalink)
Reply


 