I hear what everyone is saying and I will submit a photo of the codes on the wires (tonight, after my day job).
Yes, I am using what I have laying around however, it is the wire that was recommended by my electrician when installing 220v for my dryer. I purchased a 100' spool which was about $300 and I am using the remaining for my stove/oven. Regardless, I will report back on the exact specifications. The wire is not Romex, I merely used romex as an example as this is very thick individual strands that are encased in a black wrap which states 600v plus a bunch of other stuff. My primary question was about the conduit as I thought that would be the safest until our plant engineer told me he didn't think I should be doing that. However, on all of my projects, I want to follow the proper code. I have a friend that is a contractor that will be coming over this weekend to review my work. Last edited by Tidybuoy; 04-23-2021 at 08:42 AM.. |
||
![]() |
|
Registered
Join Date: Mar 2004
Location: Los Angeles
Posts: 17,412
|
Quote:
|
||
![]() |
|
Registered
|
You appear to to have 6/3 romex inserted into fmc.
The potential for heat generation is minimal. Two 180* phases with a neutral and a ground will offset and cancel. It's not like you are running a single conductor in an enclosed space. You went over and above sleeving in the fmc, worried about potential damage from rodents and whatnot, but i hope you at least put a bushing on both ends of the conduit.
__________________
Chris the more i learn, the less i know |
||
![]() |
|
Registered
Join Date: Jun 2003
Location: Fresno, CA
Posts: 7,787
|
Quote:
After that, my flexible conduit is connected via a threaded connection to the permanent fuse box pipe. The flexible conduit is then routed to it's final destination and strapped to the bottom of the 4x6 floor joists under the house. The flexible conduit is then routed up and thru the wall to it's final destination. I will take photos of the wiring tonight to help determine if it needs to be inside conduit or not. We'll go from there. My only regret is that I'm gonna have to crawl under the house again - I too old for this S#!T ![]() |
||
![]() |
|
Registered
|
If you do it right, it's an ab workout.
__________________
Chris the more i learn, the less i know |
||
![]() |
|
Senior Member
Join Date: Feb 2000
Location: Lacey, WA. USA
Posts: 25,310
|
You'd think that over-designing the installation would get you a pat on the back. Using the proper non-conduit cable, and then protecting it in conduit. Makes sense, but the inspector may very possibly fail it. I knew of one installation which the inspectors failed, causing the builder to start over. It was "direct burial" cable, perfectly suited for just burying (at the proper depth). Builder pulled it through conduit for extra protection. Fail.
Who knew? Electrical inspectors are persnickety.
__________________
Man of Carbon Fiber (stronger than steel) Mocha 1978 911SC. "Coco" |
||
![]() |
|
![]() |
You do not have permissi
Join Date: Aug 2001
Location: midwest
Posts: 39,937
|
Small tangent:
"Not basement but a crawl space" What kind of ventilation is going through the foundation there? Critters will get in and make a home i.e. poop if they can. Is the underside of the crawl space going to be vapor-barrier sealed from ground or below the joists? That space where the wire runs through might be considered 'exterior' to code and might require different specs. IDK. As a layman, my first thought is a sealed full floor wrap up to the rim/floor joists to prevent ground radon/moisture/fumes from getting into the house. (sorry for tangent just some random thoughts)
__________________
Meanwhile other things are still happening. |
||
![]() |
|
unindicted co-conspirator
Join Date: Jul 2007
Location: Fresno, CA
Posts: 1,660
|
Yep, just run the bundled wire exposed stapled to the underside of the joists,
Enclosing it in conduit could cause condensation and is not code approved. Only single strand wire is allowed in conduit
__________________
'03 996 - sport exhaust, sport seats, M030 sport suspension, stability control, IMS Solution ‘86 928S3 - barn find project car |
||
![]() |
|
Registered
Join Date: Sep 2009
Location: North of You
Posts: 9,160
|
Quote:
We aren't debating 'safe' any more, it's to code, or not to code. And my guess is it's not.
__________________
"A machine you build yourself is a vote for a different way of life. There are things you have to earn with your hands." |
||
![]() |
|
Registered
|
Quote:
Look at the oven and see how many amps it draws. I'm sure some of the experts here can take that information and calculate what gauge you need for that length of run. For a crawl space I would critter-proof the system with new individual wires run through your conduit.
__________________
. |
||
![]() |
|
Registered
Join Date: Jun 2003
Location: Fresno, CA
Posts: 7,787
|
Update:
The code on the wiring is as follows: Romex (R) Simpull (7M) AWG 6 CU7 CDR With AC 10 Ground Type NM-B 600 Volts I was incorrect on my previous comments on Romex. My thinking was that this wire is not like common household outlet wiring (i.e., Romex). ![]() ![]() ![]() |
||
![]() |
|
Registered
Join Date: Sep 2009
Location: North of You
Posts: 9,160
|
Since it's not exterior I believe you can run that direct.
Someone from CA should confirm it meets your code.
__________________
"A machine you build yourself is a vote for a different way of life. There are things you have to earn with your hands." |
||
![]() |
|
Registered
Join Date: Mar 2004
Location: Los Angeles
Posts: 17,412
|
Yep. Can't be exposed to light. As long s its under the house and run in-wall, you will be fine. 6 gauge, that's a big puppy. How many amps does this oven draw?
|
||
![]() |
|
Evil Genius
|
6 awg is a 50 amp circuit
__________________
Life is a big ocean to swim in. Wag more, bark less. ![]() |
||
![]() |
|
Registered
Join Date: Jan 2002
Location: Long Beach CA, the sewer by the sea.
Posts: 37,792
|
Thinking that NM cable cannot be placed in conduit is one of the most perpetrated falsehoods in the electrical trade. In fact, under certain circumstances where damage is imminent, it is required.
However, the issue is conduit wire fill. I didn't look it up but 6/3 with ground in 1.5" conduit should meet wire fill requirements. (In fact, I did look it up, but not in the NEC. Says wire fill must not exceed 53%) One thing against pulling NM, NMC and NMS cables in any conduit is the pull itself. I would pull the cable into the conduit outside while the conduit ls laid out straight and clamped. Of course I would have determined the needed length first and left a foot of extra cable out at each end for make up. There are not many cables that cannot be in conduit unless it's buried (wet location). And NM (Romex) is definitely one of those. that can't be used in wet locations. For that you need individual wires rated THWN. In fact MHF (mobile home feeder used a lot for direct burial between buildings) MUST be in conduit once above ground. It is terminated in a panel located as close to the riser as possible and still meet location requirements. (That was just an example for dispelling the myth.) |
||
![]() |
|
Registered
Join Date: Jan 2002
Location: Long Beach CA, the sewer by the sea.
Posts: 37,792
|
Note to the above: when determining wire fill one must measure the widest part of a wire bundle to calculate area by using a pi formula either by radius or diameter to determine the area in a circle form even if the cross section of the cable is not a circle. In the case of 12/2 Romex with ground, that's about 1/2" on the flat side so no way will 1/2" conduit be large enough. 3/4 does that job.
|
||
![]() |
|
Registered
|
334.15 (C), you’re good
|
||
![]() |
|