Another Construction Question: 220v Wiring

This forum is the best as I get all kinds of info here from the brain trust as well as seeing other people's projects for comparison.

I'm moving my oven from one wall to another. I need to move the 220v outlet which I did last weekend. I replaced the original 220v wiring with new wire which spans about 25' from the circuit breaker to the outlet. Basically, I am keeping exactly what I had but just moving to a different area an using new wiring.

My Question: This wiring is run under the house and I put in flexible metal conduit. Someone at work told me that I might not use conduit due to heat generation of the wiring - Can anyone tell me the best practice or code for this. I used large 1.5" flexible metal conduit. The original wiring was in 3/4" flexible conduit but the original wiring was single strand and the new wiring is incased so that all 3+ground is contained (similar to romex but for 220v (actually 600v)). I used the larger conduit simply because I had it and it was a good thing as it was a pain to feed thru it; I would never have gotten it into the smaller conduit.

Any advice would be appreciated.


Last edited by Tidybuoy; 04-22-2021 at 08:46 AM..
Old 04-22-2021, 08:43 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #1 (permalink)
Registered
 
Join Date: Sep 2009
Location: North of You
Posts: 9,160
The heat is determined by the wire size and the current. And the routing means is determined by code.

What size wire did you run?

I think you are probably 100% fine for safety...not sure about code. Did you run 'liqui-tite' conduit with proper fittings at each end? How is it secured to the house?

You wired from the breaker to the new box, right? Not an extension from the old box?

Is the underside of the house 'exterior' or 'basement'?

A pic might be good.
__________________
"A machine you build yourself is a vote for a different way of life. There are things you have to earn with your hands."
Old 04-22-2021, 08:52 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #2 (permalink)
Registered
 
3rd_gear_Ted's Avatar
 
Join Date: Oct 2007
Location: SoCal
Posts: 4,914
Garage
3 wire Romex is rated @ 60 Centigrade (!40 degrees F)
Your house isn't going to burn down the NEC is your friend
__________________
1980 911 - Metzger 3.6L
2016 Cayman S
Old 04-22-2021, 08:58 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #3 (permalink)
Registered
 
Join Date: Sep 2009
Location: North of You
Posts: 9,160
60C is easy to hit on a hot day with undersized wire...which is probably not the case here.
__________________
"A machine you build yourself is a vote for a different way of life. There are things you have to earn with your hands."
Old 04-22-2021, 09:01 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #4 (permalink)
Registered
 
Join Date: Mar 2004
Location: Los Angeles
Posts: 17,409
Can't put Romex in conduit around here, code. If it is Romex, just secure it to the side of the floor joist and come up the wall, done.
Old 04-22-2021, 09:04 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #5 (permalink)
Registered
 
Join Date: Jun 2003
Location: Fresno, CA
Posts: 7,784
Quote:
Originally Posted by 1990C4S View Post
What size wire did you run?
I don't have the specifics here at work but will check tonight. I think it is either 6 or 8 guage. it's very thick and is the exact 220v wire that I used for my dryer which was the correct guage when I did that a few years ago (got advice from an electrician then)

I think you are probably 100% fine for safety...not sure about code. Did you run 'liqui-tite' conduit with proper fittings at each end? How is it secured to the house?
I'm not sure if it is liguid tight and you can see it in the photo below as well as the 220v wiring. This is secured to the floor joists under the house and is about 2' off the ground (exactly the same as the original wiring).

You wired from the breaker to the new box, right? Not an extension from the old box?
Correct - one end connected to breakers and other end connected to outlet box

Is the underside of the house 'exterior' or 'basement'?
Not basement but a crawl space


A pic might be good.
Old 04-22-2021, 09:05 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #6 (permalink)
 
Registered
 
Join Date: Jun 2003
Location: Fresno, CA
Posts: 7,784
Quote:
Originally Posted by look 171 View Post
Can't put Romex in conduit around here, code. If it is Romex, just secure it to the side of the floor joist and come up the wall, done.
It's not romex. I was saying it's encased like romex - basically a black wrapping around all three wires + ground. Vs single strand (unwrapped) like the original). I don't remember all the specifics but definately remember seeing 600v stamped on the sheathing.
Old 04-22-2021, 09:07 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #7 (permalink)
Ayo Irpin, Ukraine!
 
70SATMan's Avatar
 
Join Date: Mar 2004
Location: Santa Cruz, CA
Posts: 12,552
Exactly, conduit is for single strand wiring and if running Romex or equivalent cabling, putting that into conduit creates additional de-rating of the amperage carrying capacity due to heat build up.

If you have cable, ditch the conduit.
__________________
Harmlessly passing gas in the grassland away;
Only dimly aware of a certain smell in the air
Old 04-22-2021, 09:11 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #8 (permalink)
Senior Member
 
Superman's Avatar
 
Join Date: Feb 2000
Location: Lacey, WA. USA
Posts: 25,310
Quote:
Originally Posted by look 171 View Post
Can't put Romex in conduit around here, code. If it is Romex, just secure it to the side of the floor joist and come up the wall, done.
Quote:
Originally Posted by 70SATMan View Post
Exactly, conduit is for single strand wiring and if running Romex or equivalent cabling, putting that into conduit creates additional de-rating of the amperage carrying capacity due to heat build up.

If you have cable, ditch the conduit.
I work around electrical inspectors. They will not pass anything that does not follow NEC to the letter. If a cable has not been UL tested and approved to be placed in conduit, then doing so would be inconsistent with code.

I dunno about Vern's black-sheathed cable, but I would guess it is like a black style of Romex. NM rated. If so, then you just staple it to the floor joists. They like to see neat workmanship, BTW.
__________________
Man of Carbon Fiber (stronger than steel)

Mocha 1978 911SC. "Coco"
Old 04-22-2021, 09:21 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #9 (permalink)
Registered
 
Join Date: Jun 2003
Location: Fresno, CA
Posts: 7,784
Thanks All.

My OCD will guarantee neat workmanship (once completed).
Old 04-22-2021, 09:37 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #10 (permalink)
Registered
 
Join Date: Apr 2008
Location: Houston TX
Posts: 8,713
He probably has SO or SOW cord. Does it look like this?

__________________
Mike Bradshaw

1980 911SC sunroof coupe, silver/black
Putting the sick back into sycophant!
Old 04-22-2021, 09:46 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #11 (permalink)
Senior Member
 
Superman's Avatar
 
Join Date: Feb 2000
Location: Lacey, WA. USA
Posts: 25,310
I expect as much, Vern. If nothing else, I can tell by your name. Vern.
__________________
Man of Carbon Fiber (stronger than steel)

Mocha 1978 911SC. "Coco"
Old 04-22-2021, 09:48 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #12 (permalink)
 
Registered
 
Join Date: Mar 2004
Location: Los Angeles
Posts: 17,409
Don't mess around with anything else. Go get a length of Romex and use that. Find out the amperage required by the new oven and get the correct wire size accordingly. Its still cheaper then having something that wouldn't pass code and if it burns or cause any issues, you will be one responsible. Its not worth it. This isn't getting inspected?
Old 04-22-2021, 10:01 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #13 (permalink)
Registered
 
Join Date: Sep 2009
Location: North of You
Posts: 9,160
^^^ Or pull individual conductors through the conduit.
__________________
"A machine you build yourself is a vote for a different way of life. There are things you have to earn with your hands."
Old 04-22-2021, 10:03 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #14 (permalink)
Registered
 
craigster59's Avatar
 
Join Date: Aug 2004
Location: Gilbert, Az
Posts: 21,720
Garage
Quote:
Originally Posted by 1990C4S View Post
^^^ Or pull individual conductors through the conduit.
I was going to say, you could always strip the sheathing and pull it as separate wires.
__________________
---------------------------------------------------------------------------

"There is nothing to be learned from the second kick of a mule" - Mark Twain
Old 04-22-2021, 10:12 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #15 (permalink)
Registered
 
Join Date: Mar 2004
Location: Los Angeles
Posts: 17,409
Quote:
Originally Posted by craigster59 View Post
I was going to say, you could always strip the sheathing and pull it as separate wires.
Noooooo. Don't use that wire. Throw that wire in the trash or use it an an extension cord. Get the required wire by code. normally it is the THHN wire that's needed in conduit. They should have tons at Home Depot or your electrical supply house.
Old 04-22-2021, 10:24 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #16 (permalink)
Senior Member
 
Superman's Avatar
 
Join Date: Feb 2000
Location: Lacey, WA. USA
Posts: 25,310
I do NOT think Vern is trying to cut any corners here. I think he is asking these questions because he wants to do this right.
__________________
Man of Carbon Fiber (stronger than steel)

Mocha 1978 911SC. "Coco"
Old 04-22-2021, 10:40 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #17 (permalink)
Registered
 
Bill Douglas's Avatar
 
Join Date: Jun 2000
Location: bottom left corner of the world
Posts: 22,770
What I do n these situations is ask a friendly electrican what is correct and code, then I do the dogs body work of running the cable etc. then get the electrican to inspect and OK it. Minimal dollars.

Around here electricans like their work but don't like crawling around under floors of drilling holes through old timber.
Old 04-22-2021, 11:11 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #18 (permalink)
Registered
 
Join Date: Sep 2009
Location: North of You
Posts: 9,160
Quote:
Originally Posted by craigster59 View Post
I was going to say, you could always strip the sheathing and pull it as separate wires.
Those wires will not have the appropriate rating. THEW , THHN something like that is correct.

Easiest way is a new wire, no conduit.

Cheapest way is to pull a new red, black, white, and green single conductor.
__________________
"A machine you build yourself is a vote for a different way of life. There are things you have to earn with your hands."
Old 04-22-2021, 11:21 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #19 (permalink)
Registered
 
Join Date: Mar 2004
Location: Los Angeles
Posts: 17,409
Quote:
Originally Posted by Superman View Post
I do NOT think Vern is trying to cut any corners here. I think he is asking these questions because he wants to do this right.
I know he's not. he maybe trying to use what he has lying around. Timber or s piece of steel, its fine but not wires. It must be correct type. Not worth saving a trip to the hardware store or 90 bucks of wires.

Old 04-22-2021, 11:29 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #20 (permalink)
Reply


 


All times are GMT -8. The time now is 11:45 AM.


 
Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2025, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2025 Pelican Parts, LLC - Posts may be archived for display on the Pelican Parts Website -    DMCA Registered Agent Contact Page
 

DTO Garage Plus vBulletin Plugins by Drive Thru Online, Inc.