Thanks everyone.
Status: picked up nitrogen tank from a welding supply place, on Monday when the HVAC supply place is open I’ll pick up the VCRT and other stuff, and proceed. Yeah I’m spending money on HVAC tools and the DIY floundering is funny (not so much to me, but to others!) . . . but I have multiple more minisplits to install in the coming year, so it’s worth learning.
__________________
1989 3.2 Carrera coupe; 1988 Westy Vanagon, Zetec; 1986 E28 M30; 1994 W124; 2004 S211 What? Uh . . . “he” and “him”? |
||
![]() |
|
Registered
Join Date: Dec 2001
Location: Cambridge, MA
Posts: 44,200
|
Quote:
I got lucky with a simple recharge of my Sub Zero for $28 all in. I am guessing a pro would have been $300 to $500 and they would have insisted on putting in a new compressor for $1500. That's just the nature of things these days.
__________________
Tru6 Restoration & Design |
||
![]() |
|
Registered
|
The total spend on tools might be a grand, if that. Around here, what would it cost to have an HVAC company install four indoor and two outdoor units and run lines to second story and through closets with electric across the basement? I suspect the bids would be five figures in labor alone.
__________________
1989 3.2 Carrera coupe; 1988 Westy Vanagon, Zetec; 1986 E28 M30; 1994 W124; 2004 S211 What? Uh . . . “he” and “him”? |
||
![]() |
|
G'day!
|
On the subject of tool investment......I'm learning how to repair motorcycle fairings (mostly ABS) right now and am not hesitating to buy whatever tools and materials are needed to do the work.
We're not talking big money here and considering how many fairings I have and the % that need at least some degree of repair makes it a no-brainer as an investment. I also purchased a vacuum pump a while back and have already used it for my truck's AC and at some point will also be installing a mini-split too and will have it for that. Brake tubing flare tools - yep. For my cars' brake lines. Tire change tools and equipment - check. For my motorcycles Etc etc.....whatever is needed to stay as independent as possible.
__________________
Old dog....new tricks..... |
||
![]() |
|
UnRegistered User
|
Quote:
Those valves have two seats. Turn the stem fully in and it will tighten down on the “front seat”. All the way counter clockwise it will close off your access port on the back seat. |
||
![]() |
|
UnRegistered User
|
Is that unit pre-charged?
If so, don’t do what I had suggested. If it is pre charged the valve should be on the front seat and the back access port should be open for you to access the line set side of the system. Is there a shrader valve core in the access fitting? Does the blue hose have a shrader depressor in the female end? |
||
![]() |
|
![]() |
Registered
|
Yes, unit pre-charged.
There is a Schraeder valve in the access port, and a Schraeder depressor in the hose end. I an going to remove the core though.
__________________
1989 3.2 Carrera coupe; 1988 Westy Vanagon, Zetec; 1986 E28 M30; 1994 W124; 2004 S211 What? Uh . . . “he” and “him”? Last edited by jyl; 06-30-2025 at 03:00 PM.. |
||
![]() |
|
Registered
|
Update: hooked up the nitrogen tank to the service port, crack the valve, what’s that hissing?! The adapter (between hose and port) leaks at the port, more than a teeny bit, and tightening doesn’t help. This adapter came with the uber cheap pump and gauges set. Maybe it’s just a crappy freebie thing. Anyway, offered a set of adapters and we’ll see.
__________________
1989 3.2 Carrera coupe; 1988 Westy Vanagon, Zetec; 1986 E28 M30; 1994 W124; 2004 S211 What? Uh . . . “he” and “him”? |
||
![]() |
|
Registered
|
It was that crappy 1/4” to 5/16” adapter. That 10 cent part has cost me a lot of trouble. New adapter, pressurized to 200 psi nitrogen, seems to be holding, will check in the morning. EDIT: next morning, still 200 psi. Then pull vacuum and release refrigerant, repeat for the other lines, hoping no issues.
__________________
1989 3.2 Carrera coupe; 1988 Westy Vanagon, Zetec; 1986 E28 M30; 1994 W124; 2004 S211 What? Uh . . . “he” and “him”? Last edited by jyl; 07-02-2025 at 06:27 AM.. |
||
![]() |
|
Registered
Join Date: Dec 2002
Location: Dahlonega , Georgia
Posts: 14,555
|
Quote:
__________________
2002 Boxster S . Arctic silver + black top/int. Jake Raby 3.6 SS engine " the beast ". GT3 front bumper, GT3 side skirts and GT3 TEK rear diffuser. 1999 996 C4 coupe black/grey with FSI 3.8 engine . Rear diffuser , front spoiler lip with ducktail spoiler . |
||
![]() |
|
Registered
|
![]() All the lines held pressure and pulled vacuum just fine. Bringing them online now. Next to get lineset covers made and installed.
__________________
1989 3.2 Carrera coupe; 1988 Westy Vanagon, Zetec; 1986 E28 M30; 1994 W124; 2004 S211 What? Uh . . . “he” and “him”? |
||
![]() |
|
Registered
|
Oops, I was rudely reminded of something I’d forgotten. The outdoor units come pre-charged with enough refrigerant for 33 feet of line total. I have more line than that connected to each outdoor unit. So I’d originally figured I’d install then get someone to add more refrigerant. Then I forgot about that part. When the indoor units threw up an “H3” error code after a couple hours of operation, and I looked up what that code is, I was reminded.
Oh well, time to call an HVAC guy to do that.
__________________
1989 3.2 Carrera coupe; 1988 Westy Vanagon, Zetec; 1986 E28 M30; 1994 W124; 2004 S211 What? Uh . . . “he” and “him”? |
||
![]() |
|
Registered
|
Nice install!
Heads up for something to check when installing a mini-split!!! I'm helping my neighbor install one in his garage this last week. We got the condenser installed outside, the evaporator installed inside, all the electrical connections made and then went to install the copper lines and ran into a huge problem! I guess the supply houses stock compressors and evaporators separately and then ship out as a set. Well both the LG units are 2 ton but they're not the correct matched set. The condenser has 1/2" and 1/4" lines but the evaporator has 5/8" and 3/8" lines. Didn't even occur to me check it or even look at the connections.
__________________
2014 Cayman S (track rat w/GT4 suspension) 1979 930 (475 rwhp at 0.95 bar) |
||
![]() |
|
Registered
|
And why would you ever think to check that? Totally seller’s screwup, they should ship out replacements ASAP.
__________________
1989 3.2 Carrera coupe; 1988 Westy Vanagon, Zetec; 1986 E28 M30; 1994 W124; 2004 S211 What? Uh . . . “he” and “him”? |
||
![]() |
|
Registered
|
Well, update on my minisplit install.
I installed two systems, each 18K BTU outdoor unit connected to two 9K indoor units. Took a considerable time to run the lines through closets and so on. Pressure tested with nitrogen to 200 psi, pulled 500 micron vacuum in lines, had a problem traced to a faulty 1/4” to 5/8” adapter, after I replaced that all looked good. Had HVAC service come add more R32 for the extra long lines. Tech liked my install. One system, on south side of house, worked fine and has continued to work fine. Other system, on north side of house, lost all its refrigerant in a few days. WTF. Got more nitrogen, pressure tested that system, found a flare connection (liquid line at outdoor unit) that was teetering on bad - actually the flare ripped off when I tried to re-torque it. Re-made the flare, this time using a FlareSeal, pressure tested to 400 psi for two days, looks good. So now I need to vacuum out that entire system - all the refrigerant oil and humidity and so on. Disconnect the hose to nitrogen tank and a cloud of oil sprays out. Connected my $100 El-Cheapo Vevor vacuum pump and my Kinda-Cheapo Hilmor micro gauge. They both decide to fail. Replace oil in pump, clean gauge sensor with isopropyl alcohol, no help. Order a new vacuum pump, a Fieldpiece this time. Make a warranty claim with Hilmor, they say they are shipping me a new gauge, but I order a BluVac gauge anyway. The tool budget is by now over $1,500 and I wait for the new gear to arrive. In the meantime I repeatedly pressurize each line - by now I also own a nitrogen tank and regulator - and flip open the valve core removal tool’s valve to blow out more oil. The stuff arrives. Ooo, I feel so pro with this nice kit. I close the service valve to isolate the lines. Pressure test them and blow out oil again. Open service valves, pressurize the whole system, blow oil out again. Close service valves. Hook up vacuum pump and micron gauge to lineset A, pull out down to 350 microns, leave it overnight, next morning reads 650 microns but it’s stable there, not rising. I do the same for lineset B. Okay, I’m sort of satisfied the linesets are tight and mostly purged. Now I open all service valves, and start vacuuming down the entire system. This takes way longer - like 45 minutes to get to 500 microns. I’ve changed the oil in the Fieldpiece once by now. I close off the VCRT and switch off the pump. I’ll see where the vacuum stabilizes, hopefully it does. Later today I’ll re-insert the valve cores and vacuum down again, planning to get to 350 ish microns, then see if overnight it holds at least 500 microns. Assuming that works (oh please) then I’ll get my EPA 608 and buy a tank of R32 and learn how to load refrigerant back into the system. I haven’t checked how much I should need but will buy a 20 lb tank. This is taking forever. I’m spending $ on tools. But I think my HVAC service would charge four figures to do this - they charged me $1,200 to replace capacitor and add R410 to the central AC compressor last month, and were only here for an hour. I have a few more minisplits to install in another building, and I figure I should devote some time and money to at least try to learn how to do this myself. Architect got an HVAC company estimate for those, over $40,000 - no way am I spending that, I know the equipment will cost less than $8,000. In the meantime, the south side system has been doing a decent job of keeping the second floor bedrooms cool all by itself - set it at 70F in the two bedrooms it is installed in, and use a fan to circulate cool air to the bedrooms that the non-working north side system is not cooling. So even though we’ve had a couple short heat waves during all of this, the minisplits have been proving their worth even with all the problems. Meanwhile the copper lineset covers have been fabricated and are sitting under a tarp in the backyard, waiting for me to get back on the ladder. Man oh man, 16 oz copper has jumped in price - a 4’ x 10’ sheet went from $260 to $400 in the past month, so the cost of these covers was $2,300 when I had planned more like $1,600. I have 80 feet of copper covers, need to cut and miter and screw to siding, then use my nibbler to cut the excess half sheet into strips to cover the seams. Spendy but I do not want plastic lineset covers on my house. I haven’t spent the whole month doing this - life has gotten in the way, I’ve been out of town, maybe two days devoted to minisplit install in the last 30.
__________________
1989 3.2 Carrera coupe; 1988 Westy Vanagon, Zetec; 1986 E28 M30; 1994 W124; 2004 S211 What? Uh . . . “he” and “him”? Last edited by jyl; 08-17-2025 at 10:05 AM.. |
||
![]() |
|
Registered
Join Date: Jan 2002
Location: Long Beach CA, the sewer by the sea.
Posts: 37,601
|
First of all you are dealing with the wrong HVAC company. Whatever it takes, find an owner/operator that does nothing but service and vet him carefully.
Secondly, see first sentence. I have all the gear too, but I know when to hold and when to fold. |
||
![]() |
|
Registered
|
That’s because you’re a pro. Duffers like me have no idea, we just keep going until failure and defeat. Or until the wife gets mad. And she’s been away this past month.
__________________
1989 3.2 Carrera coupe; 1988 Westy Vanagon, Zetec; 1986 E28 M30; 1994 W124; 2004 S211 What? Uh . . . “he” and “him”? Last edited by jyl; 08-17-2025 at 11:17 AM.. |
||
![]() |
|
Registered
|
![]() I’m putting the micron gauge as far from the vacuum point as I can. I should really buy actual vacuum hoses.
__________________
1989 3.2 Carrera coupe; 1988 Westy Vanagon, Zetec; 1986 E28 M30; 1994 W124; 2004 S211 What? Uh . . . “he” and “him”? |
||
![]() |
|
Friend of Warren
Join Date: Oct 2000
Location: Lincoln, NE
Posts: 16,482
|
I’m starting to think at this point you are as knowledgeable as the HVAC guys you would have hired. Good luck with the refrigerant install.
As you probably know by now, there are plenty of YouTube videos, showing how to test and replace an AC capacitor.
__________________
Kurt V No more Porsches, but a revolving number of motorcycles. |
||
![]() |
|
Registered
Join Date: Jan 2002
Location: Long Beach CA, the sewer by the sea.
Posts: 37,601
|
Quote:
Of course we are talking the refrigerant here, not the scope of all the things inherent with HVAC. Just the electronics troubleshooting is quite a process. My 2016 unit flashes codes when it wants some help much like an engine light on a car. Yeah, there is no reason to pay hundreds for a capacitor that HD has in stock. Buy 2 when you go. They used to be 35 bucks but I haven't had the pleasure in awhile now. |
||
![]() |
|