PTO Generator Question for PPOT Farmers/engineers

Say a 15 KW (16 Peak) PTO driven generator requires "at least a 30 HP tractor" to operate. Does this mean 30 HP at the PTO for the generator to operate at full load? I ask because I have a 23 HP tractor and am wondering if it will operate this generator if peak loads do not exceed say 10KW (my house with a well pump and electric water heater, lights. microwave)?

Old 09-30-2011, 06:10 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #1 (permalink)
canna change law physics
 
red-beard's Avatar
 
Join Date: Jul 2000
Location: Houston, Tejas
Posts: 43,366
Garage
Quote:
Originally Posted by Crowbob View Post
Say a 15 KW (16 Peak) PTO driven generator requires "at least a 30 HP tractor" to operate. Does this mean 30 HP at the PTO for the generator to operate at full load? I ask because I have a 23 HP tractor and am wondering if it will operate this generator if peak loads do not exceed say 10KW (my house with a well pump and electric water heater, lights. microwave)?
16 kW is a bit over 21.5 hp. Assuming 85% mechanical to electrical efficiency at maximum load you need about 25 hp. If you are not running peak load, it should work. But, you need to ensure that the pulley ratios are correct as well, so the generator runs the right speed.
__________________
James
The pessimist complains about the wind; the optimist expects it to change; the engineer adjusts the sails.- William Arthur Ward (1921-1994)
Red-beard for President, 2020
Old 09-30-2011, 06:22 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #2 (permalink)
Information Overloader
 
Join Date: Mar 2003
Location: NW Lower Michigan
Posts: 29,361
Thanks, Red. The tractor manual says the PTO is estimated at 17.7 HP (13.2 KW). The gen. requires the standard 540 rpm which the tractor generates @ 3142 rpm.

So, at about 85% efficiency and a peak load of 10KW I'd still be well within the capacity of the tractor?

I can't imagine the well, elec. heater, microwave and a few lights would exceed 10KW. Even then, were I to operate the house off the gen, I could temporarily disable the water heater just to be safe, correct?
Old 09-30-2011, 06:35 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #3 (permalink)
Registered
 
Seahawk's Avatar
 
Join Date: Jul 2004
Location: Maryland
Posts: 31,423
Quote:
Originally Posted by Crowbob View Post
Say a 15 KW (16 Peak) PTO driven generator requires "at least a 30 HP tractor" to operate. Does this mean 30 HP at the PTO for the generator to operate at full load? I ask because I have a 23 HP tractor and am wondering if it will operate this generator if peak loads do not exceed say 10KW (my house with a well pump and electric water heater, lights. microwave)?
I have a 1500kw Winco PTO generator that for peak load requires 30hp. I run it with my 23hp tractor. I also have a 35hp tractor but I prefer to use the small units.

I spent a lot of time talking with the Winco folks and the MF dealer before I bought it. Both said it would work fine at less than peak loads. When I had the house wired for the generator to "plug" into the house, I made sure that the maximum circuit load was 2/3's the peak KW, which runs pretty much everything other than the HVAC.

PM and I can go into the details. We average about 5 days without power every year so it has been a blessing.
__________________
1996 FJ80.
Old 09-30-2011, 06:45 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #4 (permalink)
canna change law physics
 
red-beard's Avatar
 
Join Date: Jul 2000
Location: Houston, Tejas
Posts: 43,366
Garage
Quote:
Originally Posted by Crowbob View Post
Thanks, Red. The tractor manual says the PTO is estimated at 17.7 HP (13.2 KW). The gen. requires the standard 540 rpm which the tractor generates @ 3142 rpm.

So, at about 85% efficiency and a peak load of 10KW I'd still be well within the capacity of the tractor?

I can't imagine the well, elec. heater, microwave and a few lights would exceed 10KW. Even then, were I to operate the house off the gen, I could temporarily disable the water heater just to be safe, correct?
Again, the efficiency of the generator will be around 85-90% (check with the manufacturer). I think you'll be able to do about 11-12 kW peak.

Playing with the numbers for your PTO, scaling up for a 30hp and comparing that to the generator, I'm getting an efficiency of 87%, right in line with what I'm thinking.

If the generator is 220VAC, you might consider a 50 amp breaker from the generator. This will be both a good safety device (disconnect) and limit the power to your house from the unit.
__________________
James
The pessimist complains about the wind; the optimist expects it to change; the engineer adjusts the sails.- William Arthur Ward (1921-1994)
Red-beard for President, 2020
Old 09-30-2011, 08:01 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #5 (permalink)
Unconstitutional Patriot
 
turbo6bar's Avatar
 
Join Date: Apr 2000
Location: volunteer state
Posts: 5,620
Quote:
Originally Posted by Seahawk View Post
I have a 1500kw Winco PTO generator that for peak load requires 30hp. I run it with my 23hp tractor. I also have a 35hp tractor but I prefer to use the small units.
1500 kW, eh?

Looks like bearded one has addressed your question, crowbob. I would like to add that you should not be afraid to run your tractor at PTO speed 24/7. The guys on tractorbynet say tractors can do this work day and night as long as it has clean fluid and air.

I was considering adding an overdrive to the finish mower, so I could run lower rpms and still keep blade tip speed up. Guys were saying I won't save much fuel running at lower rpms. The fuel consumption is related to load and not rpm.
Old 09-30-2011, 10:11 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #6 (permalink)
 
Registered
 
wdfifteen's Avatar
 
Join Date: Mar 2008
Location: SW Ohio
Posts: 29,264
Garage
What kind of tractor is this? A "23 hp tractor" should have 23 horsepower at the PTO, since that is where the power is measured from in the official OECD ratings tests.
__________________
.
Old 09-30-2011, 12:32 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #7 (permalink)
Information Overloader
 
Join Date: Mar 2003
Location: NW Lower Michigan
Posts: 29,361
Kubota. The manual says PTO is estimated at 17.7 HP (13.2 kW). 540 rpm at 3142 engine rpm.

Old 09-30-2011, 12:40 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #8 (permalink)
Reply


 


All times are GMT -8. The time now is 04:32 AM.


 
Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2025, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2025 Pelican Parts, LLC - Posts may be archived for display on the Pelican Parts Website -    DMCA Registered Agent Contact Page
 

DTO Garage Plus vBulletin Plugins by Drive Thru Online, Inc.