Electrical Help Needed

About 7 years ago, I installed a new wiring system for my shop, barn, and a couple of other outbuildings. All 4 of the circuits are serviced by a sub-panel, which was installed by our electrician. I did all of the other wiring myself (I've done similar projects several times over the last 20+ years). The circuits are all very simple - just a bunch of outlets with a few switched outlets for fluorescent lighting. There are no 3-way switches anywhere.

Everything worked fine upon installation, and continued to work fine until a couple of weeks ago. I went out to the barn to plug in a battery charger, and no power. Went to the box and found that the circuit breaker had tripped. That seemed odd, but I just reset it and continued on. A couple of days later, I went to turn on overhead lights, and same circuit was tripped. Strange. Reset it and continued. Last week, I encountered the same thing. This time, when I reset the circuit, I heard a "pop" coming from the barn, and the breaker tripped again. As far as I can tell, there was no load on the circuit when the breaker tripped.

So, I'm figuring that there must be a short somewhere in that circuit. A couple of questions: 1. Why would a short suddenly manifest itself after 7+ years? 2. Is there a way to track down the source without disconnecting everything? The "pop" I heard was coming from a junction box in the barn. When I removed the cover, the large wire nut (joining 6 neutral wires) was burnt to a crisp.

Any advice appreciated! Thanks for reading!

Mike

__________________
Mike Hinton
'06 Cayman S Carmon Red, '05 Cayenne Turbo Black, '87 Carrera Granite Green, '72 911T Aubergine,
'74 914 1.8 Marathon Blue, '64 356C Aubergine
Old 02-11-2013, 01:34 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #1 (permalink)
Moderator
 
Bill Verburg's Avatar
 
Join Date: Dec 2000
Posts: 26,395
Garage
Quote:
Originally Posted by mikehinton View Post
About 7 years ago, I installed a new wiring system for my shop, barn, and a couple of other outbuildings. All 4 of the circuits are serviced by a sub-panel, which was installed by our electrician. I did all of the other wiring myself (I've done similar projects several times over the last 20+ years). The circuits are all very simple - just a bunch of outlets with a few switched outlets for fluorescent lighting. There are no 3-way switches anywhere.

Everything worked fine upon installation, and continued to work fine until a couple of weeks ago. I went out to the barn to plug in a battery charger, and no power. Went to the box and found that the circuit breaker had tripped. That seemed odd, but I just reset it and continued on. A couple of days later, I went to turn on overhead lights, and same circuit was tripped. Strange. Reset it and continued. Last week, I encountered the same thing. This time, when I reset the circuit, I heard a "pop" coming from the barn, and the breaker tripped again. As far as I can tell, there was no load on the circuit when the breaker tripped.

So, I'm figuring that there must be a short somewhere in that circuit. A couple of questions: 1. Why would a short suddenly manifest itself after 7+ years? 2. Is there a way to track down the source without disconnecting everything? The "pop" I heard was coming from a junction box in the barn. When I removed the cover, the large wire nut (joining 6 neutral wires) was burnt to a crisp.

Any advice appreciated! Thanks for reading!

Mike
Is any of the wire separate tnn wire in conduit? I had a similar occurrence after 10 yrs in service except the breakers and GFI didn't trip, there was just no power in one leg. The wire had apparently been nicked when pulled and it took all those years of arcing to ground to finally erode the wire to the point that it would no longer conduct. The funny thing was that per code all the conduit was plastic except where the nick was, under a paved drive. At that point code called for metal conduit which facilitated the arc.
__________________
Bill Verburg
'76 Carrera 3.6RS(nee C3/hotrod), '95 993RS/CS(clone)
| Pelican Home |Rennlist Wheels |Rennlist Brakes |
Old 02-11-2013, 01:45 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #2 (permalink)
Registered
 
Join Date: May 2002
Location: St Louis
Posts: 4,211
Are those Ground fault interrupters in the sub panel?
__________________
Rick
88 Cab
Old 02-11-2013, 01:51 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #3 (permalink)
Registered
 
Join Date: Mar 2008
Location: Chicagoland
Posts: 2,695
1) bad flourescent ballast
1b) condensation water+rust bubble?
1c) rodents?

guessing the real fault is somewhere downstream of that wire nut. wire nut just acted as a slow burn fuse.
Old 02-11-2013, 01:58 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #4 (permalink)
gruppe f
 
mikehinton's Avatar
 
Join Date: Sep 2008
Location: Walla Walla, WA
Posts: 301
Garage
All wire in the circuits is 12/2 Romex, so no separate TNN wires. All conduit is EMT above ground and PVC below. No GFI outlets anywhere in the system.

Is there a way to test for a short?
__________________
Mike Hinton
'06 Cayman S Carmon Red, '05 Cayenne Turbo Black, '87 Carrera Granite Green, '72 911T Aubergine,
'74 914 1.8 Marathon Blue, '64 356C Aubergine
Old 02-11-2013, 02:24 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #5 (permalink)
Un-Registered User
 
Join Date: Apr 2007
Location: Upstate New York
Posts: 902
Quote:
Originally Posted by mikehinton View Post
When I removed the cover, the large wire nut (joining 6 neutral wires) was burnt to a crisp.
I think you already found the problem. Most likely came loose and burned up over time, causing the symptoms you had.
__________________
Don
1988 Targa

Last edited by Red88Carrera; 02-11-2013 at 02:31 PM..
Old 02-11-2013, 02:27 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #6 (permalink)
 
gruppe f
 
mikehinton's Avatar
 
Join Date: Sep 2008
Location: Walla Walla, WA
Posts: 301
Garage
I did replace the fried wire nut, but that didn't solve the problem...
__________________
Mike Hinton
'06 Cayman S Carmon Red, '05 Cayenne Turbo Black, '87 Carrera Granite Green, '72 911T Aubergine,
'74 914 1.8 Marathon Blue, '64 356C Aubergine
Old 02-11-2013, 02:31 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #7 (permalink)
You do not have permissi
 
john70t's Avatar
 
Join Date: Aug 2001
Location: midwest
Posts: 39,824
Quote:
Originally Posted by Red88Carrera View Post
I think you already found the problem.
Not an electrician but..
There shouldn't be any junction boxes. Definitely not on a main leg.

The wiring from the house to garage sub panel should be continuous and oversized for total load.
That includes lights, compressor, and welder being used at the same time.
Feed wire and breaker should be same stats, or breaker should trip early. That's the safety link.

Then, each leg in garage should be connected individually to bus and breaker.
Old 02-11-2013, 02:54 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #8 (permalink)
Un-Registered User
 
Join Date: Apr 2007
Location: Upstate New York
Posts: 902
If it's NM/B romex it can't be used underground, even in conduit. That's considered a wet location. Romex is not rated for wet locations.
__________________
Don
1988 Targa
Old 02-11-2013, 03:15 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #9 (permalink)
gruppe f
 
mikehinton's Avatar
 
Join Date: Sep 2008
Location: Walla Walla, WA
Posts: 301
Garage
I guess I should have added that the main supply lines to the various buildings are either 6 gauge or 8 gauge individual wires running in PVC conduit. I'm fairly certain that that is the case also for the wires going from the main service entrance panel on the house to the sub panel. I didn't actually witness that installation, but it was done by a well-known electrical contractor here in the Napa Valley.

I don't think there is actually any Romex underground, but if there is, it's the gray stuff that's rated for damp locations.

The junction box I'm referring to takes the feed from the main wires, and distributes it to the outlets and light fixtures in the barn.
__________________
Mike Hinton
'06 Cayman S Carmon Red, '05 Cayenne Turbo Black, '87 Carrera Granite Green, '72 911T Aubergine,
'74 914 1.8 Marathon Blue, '64 356C Aubergine
Old 02-11-2013, 03:28 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #10 (permalink)
Un-Registered User
 
Join Date: Apr 2007
Location: Upstate New York
Posts: 902
Good to hear that. So if I understand correctly, you're saying that the breaker tripped even with everything unplugged and switches turned off? You're absolutely sure of it?
__________________
Don
1988 Targa
Old 02-11-2013, 03:33 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #11 (permalink)
Bollweevil
 
Join Date: Dec 2003
Location: Fulshear, Texanistan
Posts: 3,361
Bad breaker ??
__________________
Jack
74 911 Coupe
2.7L - K21 Option - S suspension
Old 02-11-2013, 04:01 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #12 (permalink)
gruppe f
 
mikehinton's Avatar
 
Join Date: Sep 2008
Location: Walla Walla, WA
Posts: 301
Garage
I'm pretty sure that's correct. I still need to unplug the overhead fluorescent lights, but they are controlled by a switch. I'll check tonight and see if anything else is plugged in down the line. If there's nothing plugged in, it would have to be a short somewhere, correct?
__________________
Mike Hinton
'06 Cayman S Carmon Red, '05 Cayenne Turbo Black, '87 Carrera Granite Green, '72 911T Aubergine,
'74 914 1.8 Marathon Blue, '64 356C Aubergine
Old 02-11-2013, 04:02 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #13 (permalink)
Moderator
 
Bill Verburg's Avatar
 
Join Date: Dec 2000
Posts: 26,395
Garage
Quote:
Originally Posted by Red88Carrera View Post
I think you already found the problem. Most likely came loose and burned up over time, causing the symptoms you had.
I didn't see that on first read, I agree that's the problem.

why are 6 whites bonded the only place that many whites should come together is at a sub-panel where they are individually bonded to the bus. Wire nutting that many 12-2 wires is asking for trouble.
__________________
Bill Verburg
'76 Carrera 3.6RS(nee C3/hotrod), '95 993RS/CS(clone)
| Pelican Home |Rennlist Wheels |Rennlist Brakes |
Old 02-11-2013, 04:03 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #14 (permalink)
gruppe f
 
mikehinton's Avatar
 
Join Date: Sep 2008
Location: Walla Walla, WA
Posts: 301
Garage
I already replaced the breaker too
__________________
Mike Hinton
'06 Cayman S Carmon Red, '05 Cayenne Turbo Black, '87 Carrera Granite Green, '72 911T Aubergine,
'74 914 1.8 Marathon Blue, '64 356C Aubergine
Old 02-11-2013, 04:03 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #15 (permalink)
Un-Registered User
 
Join Date: Apr 2007
Location: Upstate New York
Posts: 902
Quote:
Originally Posted by Bill Verburg View Post
I didn't see that on first read, I agree that's the problem.

why are 6 whites bonded the only place that many whites should come together is at a sub-panel where they are individually bonded to the bus. Wire nutting that many 12-2 wires is asking for trouble.
I agree that it's not a good practice, but if there is nothing turned on or plugged in, it wouldn't cause the breaker to trip.
__________________
Don
1988 Targa
Old 02-11-2013, 04:09 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #16 (permalink)
Un-Registered User
 
Join Date: Apr 2007
Location: Upstate New York
Posts: 902
Quote:
Originally Posted by mikehinton View Post
I'm pretty sure that's correct. I still need to unplug the overhead fluorescent lights, but they are controlled by a switch. I'll check tonight and see if anything else is plugged in down the line. If there's nothing plugged in, it would have to be a short somewhere, correct?
I would agree with that. If you find other devices plugged in, check to see what the voltage is on that circuit.
__________________
Don
1988 Targa
Old 02-11-2013, 04:11 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #17 (permalink)
Registered
 
Join Date: Mar 2004
Location: Los Angeles
Posts: 17,337
Look at the connector or clamp. Sometimes they over tighten it or pull on it with the clamp tight and cut the wires. Rodens, or ....

I must run, but I will try to read through the posts and see if I can help you solve it later tonight. It sounds like an easy issue to isolate.
Old 02-11-2013, 04:16 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #18 (permalink)
gruppe f
 
mikehinton's Avatar
 
Join Date: Sep 2008
Location: Walla Walla, WA
Posts: 301
Garage
OK. Got home tonight and made sure everything was unplugged. Circuit still trips after about 60 seconds. I guess the next step is to start disconnecting things at the junction box in order to isolate the "bad" circuit...
__________________
Mike Hinton
'06 Cayman S Carmon Red, '05 Cayenne Turbo Black, '87 Carrera Granite Green, '72 911T Aubergine,
'74 914 1.8 Marathon Blue, '64 356C Aubergine
Old 02-11-2013, 06:39 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #19 (permalink)
Registered
 
Join Date: Mar 2004
Location: Los Angeles
Posts: 17,337
Quote:
Originally Posted by mikehinton View Post
I guess I should have added that the main supply lines to the various buildings are either 6 gauge or 8 gauge individual wires running in PVC conduit. I'm fairly certain that that is the case also for the wires going from the main service entrance panel on the house to the sub panel. I didn't actually witness that installation, but it was done by a well-known electrical contractor here in the Napa Valley.

I don't think there is actually any Romex underground, but if there is, it's the gray stuff that's rated for damp locations.

The junction box I'm referring to takes the feed from the main wires, and distributes it to the outlets and light fixtures in the barn.
I don't know about that gray stuff. We would never use it and some inspectors will not pass it. I actually don't think its code.

Old 02-11-2013, 06:58 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #20 (permalink)
Reply


 


All times are GMT -8. The time now is 05:25 AM.


 
Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2025, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2025 Pelican Parts, LLC - Posts may be archived for display on the Pelican Parts Website -    DMCA Registered Agent Contact Page
 

DTO Garage Plus vBulletin Plugins by Drive Thru Online, Inc.