Electricity Question

The basement at my new house isn’t finished but it is (mostly) framed. Each room has a light switch and a light in the ceiling. What it doesn’t have is any electrical sockets. All of the light sockets/switches for the entire basement run off of a single breaker. (30 amp, IIRC.)

Can I run power to new sockets from the light switches, or do I need to add new breakers and run all the way from the panel?

__________________
Some Porsches long ago...then a wankle...
5 liters of VVT fury now
-Chris

"There is freedom in risk, just as there is oppression in security."
Old 09-17-2014, 10:02 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #1 (permalink)
<insert witty title here>
 
Christien's Avatar
 
Join Date: Nov 2004
Location: Hamilton, Ont.
Posts: 7,000
Garage
It all depends on how much power you plan on sending to that circuit. You can google what typical draw is for most household items. Generally though in a case like this I think it would be wisest to run all your plugs off a separate circuit. When it's all just framing and no drywall, it's very easy and quick to do.
__________________
Current: 1987 911 cabrio
Past: 1972 911t 3.0, 1986 911, 1983 944, 1999 Boxster
Old 09-17-2014, 10:07 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #2 (permalink)
Registered
 
Join Date: Sep 2009
Location: North of You
Posts: 9,160
Check your local building code. There will be a maximum number of receptacles on each circuit.
__________________
"A machine you build yourself is a vote for a different way of life. There are things you have to earn with your hands."
Old 09-17-2014, 11:07 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #3 (permalink)
Registered
 
Join Date: Apr 2007
Location: wisconsin
Posts: 2,553
You shouldn't run lights and outlets on the same circuit. Pretty sure thats against code. Appliance trips the circuit, lights go out, you fall... .

Bo
Old 09-17-2014, 11:37 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #4 (permalink)
Registered
 
Join Date: May 2005
Location: trumpistan
Posts: 9,869
Also if you run them with the lights and plug in something that trips the breaker you're going to be in the dark.
__________________
Brandolini’s Law: It takes hours more time, research, and writing to debunk misinformation than it takes to spread it.
Old 09-17-2014, 11:38 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #5 (permalink)
Registered
 
craigster59's Avatar
 
Join Date: Aug 2004
Location: Gilbert, Az
Posts: 21,677
Garage
Run your new outlets on a separate breaker from the panel. Also throw a GFCI in on each run if it may have a chance of water seepage.
__________________
---------------------------------------------------------------------------

"There is nothing to be learned from the second kick of a mule" - Mark Twain
Old 09-17-2014, 12:07 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #6 (permalink)
 
Registered
 
MBAtarga's Avatar
 
Join Date: Jul 2001
Location: Lawrenceville GA 30045
Posts: 7,377
Chris,

Code interpretation allows 13 duplex outlets on the same circuit. And as others have posted, you don't want them to be on the same breaker as light switches.

Mark
__________________
Mark

'83 SC Targa - since 5/5/2001
'06 911 S Aerokit - from 5/2/2016 to 11/14/2018
'11 911 S w/PDK - from 7/2/2021 to ???
Old 09-17-2014, 12:27 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #7 (permalink)
Un-Registered User
 
Join Date: Apr 2007
Location: Upstate New York
Posts: 902
As for the lights...

15amp lights/switches, 15amp wire, + 30amp breaker = potential for fire.
Those that don't understand electricity shouldn't mess with it.
__________________
Don
1988 Targa
Old 09-17-2014, 01:55 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #8 (permalink)
UnRegistered User
 
billybek's Avatar
 
Join Date: Dec 2007
Location: Calgary
Posts: 8,017
Garage
30 amps for lighting?
Ya growin for Colorado?
__________________
Bill K.
"I started out with nothin and I still got most of it left...."
83 911 SC Guards Red (now gone)
And I sold a bunch of parts I hadn't installed yet.
Old 09-17-2014, 02:09 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #9 (permalink)
Registered
 
Join Date: Mar 2004
Location: Los Angeles
Posts: 17,338
Find out your local code requirement. To be safe, no lighting and outlet on same circuit. Keep each room (or two) on the same circuit (4-5 outlets per room?). Bathroom should be on its own outlet circuit even if there's only one outlet that's required by code. Some places, you can get away with 15 amps outlets, but we always run 12 gauge wires and 20amp breakers. Oh, no plastic, metal only, but that's just me overbuilding for only a few bucks more. I found most people would be MORE then happy to pay the difference.
Old 09-17-2014, 03:03 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #10 (permalink)
Un-Registered User
 
Join Date: Apr 2007
Location: Upstate New York
Posts: 902
Quote:
Originally Posted by look 171 View Post
Some places, you can get away with 15 amps outlets, but we always run 12 gauge wires and 20amp breakers.
Are you saying you use a 20amp breaker on a 15amp outlet?
__________________
Don
1988 Targa
Old 09-17-2014, 03:08 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #11 (permalink)
Registered
 
Join Date: May 2002
Location: St Louis
Posts: 4,211
How cheap a builder do you have? The reason there are no outlets down there is they require Ground Fault Circuit Interrupters and against concrete the wire has to be in conduit.
__________________
Rick
88 Cab
Old 09-17-2014, 03:13 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #12 (permalink)
least common denominator
 
scottmandue's Avatar
 
Join Date: Aug 2001
Location: San Pedro,CA
Posts: 22,506
Ya know you don't need to buy that fancy "insulated" wire just twist together some coat hangers! It was good enough for grandpa!

But seriously, as long as you are going to do it and everything is open doesn't it make sense to go a little "overkill" and run a separate circuit for the wall outlets and lights? Not sure what the purpose for the basement is going to be but if you are going to run tools (shop?) or fancy A/V equipment (mancave?) I would run the extra circuit.
__________________
Gary Fisher 29er
2019 Kia Stinger 2.0t gone
1995 Miata Sold
1984 944 Sold
I am not lost for I know where I am, however where I am is lost. - Winnie the poo.
Old 09-17-2014, 03:16 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #13 (permalink)
Registered
 
Join Date: Mar 2004
Location: Los Angeles
Posts: 17,338
Quote:
Originally Posted by Red88Carrera View Post
Are you saying you use a 20amp breaker on a 15amp outlet?
No,, never
Old 09-17-2014, 03:19 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #14 (permalink)
least common denominator
 
scottmandue's Avatar
 
Join Date: Aug 2001
Location: San Pedro,CA
Posts: 22,506
And yeah +1 on the GFI, another reason to run a separate circuit.
__________________
Gary Fisher 29er
2019 Kia Stinger 2.0t gone
1995 Miata Sold
1984 944 Sold
I am not lost for I know where I am, however where I am is lost. - Winnie the poo.
Old 09-17-2014, 03:38 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #15 (permalink)
Platinum Member
 
dad911's Avatar
 
Join Date: Jul 2001
Location: Leave the gun. Take the cannoli.
Posts: 20,939
Quote:
Originally Posted by legion View Post
The basement at my new house isn’t finished but it is (mostly) framed. Each room has a light switch and a light in the ceiling. What it doesn’t have is any electrical sockets. All of the light sockets/switches for the entire basement run off of a single breaker. (30 amp, IIRC.)
I Highly doubt it's 30 Amp Breaker. Should be 14 gauge wire, 15 Amp Breaker

Quote:
Originally Posted by legion View Post
Can I run power to new sockets from the light switches, or do I need to add new breakers and run all the way from the panel?
As others have said, better not to mix lighting & recepticles.
Quote:
Originally Posted by bpu699 View Post
You shouldn't run lights and outlets on the same circuit. Pretty sure thats against code. Appliance trips the circuit, lights go out, you fall... .

Bo
This.

Quote:
Originally Posted by MBAtarga View Post
Chris,

Code interpretation allows 13 duplex outlets on the same circuit. And as others have posted, you don't want them to be on the same breaker as light switches.

Mark
Correct again

Quote:
Originally Posted by Red88Carrera View Post
As for the lights...

15amp lights/switches, 15amp wire, + 30amp breaker = potential for fire.
Those that don't understand electricity shouldn't mess with it.
Yes, check breaker, SB 14 Gauge wire, 15A Breaker

Quote:
Originally Posted by Red88Carrera View Post
Are you saying you use a 20amp breaker on a 15amp outlet?
Yes, OK per code in some situations, see below. All wire on this circuit needs to be rated for 20A (12 Gauge)

Quote:
Originally Posted by look 171 View Post
No,, never
Not Correct, Often use (multiple) 15A receptacles on a 20A circuit, done in Kitchens, Dining Rooms, etc. See NEC code section 210.21 (B), and Table 210.21(B)(3)

A 15amp receptacle on a 20 amp circuit will not overload the circuit. You will only be allowed to plug in 15a devices. 20 Amp receptacles/plugs have a 'T' configuration.

Last edited by dad911; 09-17-2014 at 04:00 PM..
Old 09-17-2014, 03:56 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #16 (permalink)
Registered
 
Bill Douglas's Avatar
 
Join Date: Jun 2000
Location: bottom left corner of the world
Posts: 22,714
Quote:
Originally Posted by billybek View Post
30 amps for lighting?
Ya growin for Colorado?

My thoughts too. You could grow anything under that sort of lighting.

I use 10 amps for lights and 20 amps for power sockets, 32 amps for cooker.
Old 09-17-2014, 04:08 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #17 (permalink)
Un-Registered User
 
Join Date: Apr 2007
Location: Upstate New York
Posts: 902
Quote:
Originally Posted by dad911 View Post
Not Correct, Often use (multiple) 15A receptacles on a 20A circuit, done in Kitchens, Dining Rooms, etc. See NEC code section 210.21 (B), and Table 210.21(B)(3)

A 15amp receptacle on a 20 amp circuit will not overload the circuit. You will only be allowed to plug in 15a devices. 20 Amp receptacles/plugs have a 'T' configuration.
That would never fly in NY, and I would never install it. The 15amp device/receptacle could melt down before the breaker ever tripped. Especially with an extension cord.
__________________
Don
1988 Targa
Old 09-17-2014, 04:11 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #18 (permalink)
 
Un-Registered User
 
Join Date: Apr 2007
Location: Upstate New York
Posts: 902
Quote:
Originally Posted by Bill Douglas View Post
My thoughts too. You could grow anything under that sort of lighting.

I use 10 amps for lights and 20 amps for power sockets, 32 amps for cooker.
Where are you guys coming up with these numbers? That's why we have standards. There's a difference between "working" and "working safely".
__________________
Don
1988 Targa
Old 09-17-2014, 04:15 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #19 (permalink)
Registered
 
Bill Douglas's Avatar
 
Join Date: Jun 2000
Location: bottom left corner of the world
Posts: 22,714
I'm from a 240 volt country. The numbers?, they are the regulations.

Old 09-17-2014, 05:11 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #20 (permalink)
Reply


 


All times are GMT -8. The time now is 12:07 AM.


 
Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2025, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2025 Pelican Parts, LLC - Posts may be archived for display on the Pelican Parts Website -    DMCA Registered Agent Contact Page
 

DTO Garage Plus vBulletin Plugins by Drive Thru Online, Inc.