Quote:
Originally Posted by dad911 View Post
Not Correct, Often use (multiple) 15A receptacles on a 20A circuit, done in Kitchens, Dining Rooms, etc. See NEC code section 210.21 (B), and Table 210.21(B)(3)

A 15amp receptacle on a 20 amp circuit will not overload the circuit. You will only be allowed to plug in 15a devices. 20 Amp receptacles/plugs have a 'T' configuration.
I am not sure about that? we usually install 20 amp FGIs in the kitchen (if its on a 20 amp circuit) and be done with it. No law suits.

Old 09-17-2014, 05:34 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #21 (permalink)
Platinum Member
 
dad911's Avatar
 
Join Date: Jul 2001
Location: Leave the gun. Take the cannoli.
Posts: 21,100
Quote:
Originally Posted by Red88Carrera View Post
That would never fly in NY, and I would never install it. The 15amp device/receptacle could melt down before the breaker ever tripped. Especially with an extension cord.


15 amp device has parallel prongs, 20 amp device has 'T' prongs. Can't plug a 20 Amp device into a 15 Amp rated receptacle. I may be wrong, but NY State appears to have adopted NEC (National Electrical Code)
Old 09-17-2014, 05:56 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #22 (permalink)
Un-Registered User
 
Join Date: Apr 2007
Location: Upstate New York
Posts: 902
Quote:
Originally Posted by dad911 View Post


15 amp device has parallel prongs, 20 amp device has 'T' prongs. Can't plug a 20 Amp device into a 15 Amp rated receptacle. I may be wrong, but NY State appears to have adopted NEC (National Electrical Code)
You're preaching to the choir. We all know that the inpector has the final say. I can tell you that around here, no inspector is going to allow a 15amp receptacle on a 20 amp feeder. I wouldn't either.
Try plugging a 50/100' extension cord into a 15amp receptacle that has a 20amp feeder, and use it to power an RV A/C unit for the weekend. Then tell us what happens. That kind of stuff happens all the time. My family's safety is worth more than that.
__________________
Don
1988 Targa
Old 09-17-2014, 06:37 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #23 (permalink)
You do not have permissi
 
john70t's Avatar
 
Join Date: Aug 2001
Location: midwest
Posts: 39,985
Quote:
Originally Posted by Red88Carrera View Post
Are you saying you use a 20amp breaker on a 15amp outlet?
Good point.
A 15amp outlet shouldn't be used on a 20amp circuit(weakest link in the chain)

One thing I like is a cross-over between adjacent rooms.
If one leg goes out there is still a single light/outlet, or it's within extension cord reach.
It does makes labeling a bit more complicated though.
Write the breaker# under the outlet.

Last edited by john70t; 09-17-2014 at 06:49 PM..
Old 09-17-2014, 06:46 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #24 (permalink)
Registered
 
Join Date: Mar 2004
Location: Los Angeles
Posts: 17,437
I put in lots of kitchens over the years, I have only had two inspectors check the panel for that. Most know our work or are just too lazy to check it.

Last edited by look 171; 09-17-2014 at 11:14 PM..
Old 09-17-2014, 06:56 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #25 (permalink)
1966 - 912 - SOLD
 
lane912's Avatar
 
Join Date: May 2008
Location: oak grove, OREGON
Posts: 3,193
I like to run out 30A circuits with 10/5 soo from a portable three phase distro box to power stage back line and monitor power. for the back line break out boxes I have a pass through box with three, 20A duplex one on each phase and backed up by a 20A breaker on the box-
__________________
i was too tired to be pretty last night!
Old 09-17-2014, 08:22 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #26 (permalink)
 
Cars & Coffee Killer
 
legion's Avatar
 
Join Date: Sep 2004
Location: State of Failure
Posts: 32,246
So far, this is what I have learned:

-Separate circuits for lights vs. outlets
-Conduit and GFCIs on outlets on walls against concrete
-No more 13 outlets per circuit

Remaining questions:
-It is my understanding that code requires an outlet every 6 feet, is this correct?
-What gauge wire should I use for outlets?
-What amperage breaker should I use for outlets?
-At what height should I mount outlets at?
__________________
Some Porsches long ago...then a wankle...
5 liters of VVT fury now
-Chris

"There is freedom in risk, just as there is oppression in security."
Old 09-18-2014, 07:21 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #27 (permalink)
Platinum Member
 
dad911's Avatar
 
Join Date: Jul 2001
Location: Leave the gun. Take the cannoli.
Posts: 21,100
Quote:
Originally Posted by legion View Post
So far, this is what I have learned:

-Separate circuits for lights vs. outlets
-Conduit and GFCIs on outlets on walls against concrete
-No more 13 outlets per circuit

Remaining questions:
-It is my understanding that code requires an outlet every 6 feet, is this correct?
-What gauge wire should I use for outlets?
-What amperage breaker should I use for outlets?
-At what height should I mount outlets at?
You can use Romex if you staple to a stud of the the framed walls in basement, not foundation wall.

14 gauge, 15 amp. Outlets within 6 feet from an opening (doorway, etc) then less than 12' apart.

They can be at std heights, and don't need to be GFI, unless there is a chance of getting wet/flood zone.
Old 09-18-2014, 02:34 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #28 (permalink)
Platinum Member
 
dad911's Avatar
 
Join Date: Jul 2001
Location: Leave the gun. Take the cannoli.
Posts: 21,100
Quote:
Originally Posted by lane912 View Post
I like to run out 30A circuits with 10/5 soo from a portable three phase distro box to power stage back line and monitor power. for the back line break out boxes I have a pass through box with three, 20A duplex one on each phase and backed up by a 20A breaker on the box-
3 Phase Residential? Not likely OP has 3 phase service.
Old 09-18-2014, 02:36 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #29 (permalink)
Cars & Coffee Killer
 
legion's Avatar
 
Join Date: Sep 2004
Location: State of Failure
Posts: 32,246
I most certainly do not have 3 phase service.

I looked into it at my old house to run GTAW (TIG) welder, but the cost exceeded what I was willing to put down for a hobby.
__________________
Some Porsches long ago...then a wankle...
5 liters of VVT fury now
-Chris

"There is freedom in risk, just as there is oppression in security."
Old 09-19-2014, 03:55 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #30 (permalink)
Registered User
 
Join Date: Jul 2013
Location: Emerald Isle, NC
Posts: 503
Some older residential has 3-phase, usually to run HVAC equip. It will have a high leg that will read 220v to ground, two other legs which read 110v to ground. Not too common today.

Local code will supersede NEC in many communities. This will often cover the 15a-20a recep mismatch. Some local codes disallow 14ga. branch circuit wiring. Breaker is sized to the wire, not the recep.

Carter
Old 09-19-2014, 04:34 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #31 (permalink)
Moderator
 
Bill Verburg's Avatar
 
Join Date: Dec 2000
Posts: 26,439
Garage
The circuit breaker protects the wire not the outlet, that's why a typical household 20amp breaker wired w/ 12 or even 10 wire, will usually have 15amp outlets. The only time you need a 20amp outlet is for specific high current devices.
__________________
Bill Verburg
'76 Carrera 3.6RS(nee C3/hotrod), '95 993RS/CS(clone)
| Pelican Home |Rennlist Wheels |Rennlist Brakes |
Old 09-19-2014, 03:09 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #32 (permalink)
 
Cars & Coffee Killer
 
legion's Avatar
 
Join Date: Sep 2004
Location: State of Failure
Posts: 32,246
New Question:

What if I have a situation with a "T"?

I have an outlet in one room (A), about a foot from the wall (B), an outlet in the adjacent room about a foot from the wall (C), and another outlet on the wall in the middle of the "T" about five feet in.

Should I:
-Run wiring from A, to C, to B?
OR
-Run wiring from A to a junction, then to B and C?
__________________
Some Porsches long ago...then a wankle...
5 liters of VVT fury now
-Chris

"There is freedom in risk, just as there is oppression in security."
Old 12-04-2014, 10:19 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #33 (permalink)
Unregistered
 
sammyg2's Avatar
 
Join Date: Aug 2000
Location: a wretched hive of scum and villainy
Posts: 55,652
Bah!

I've found that with electricity it's best to use a little creative imagination. Try some stuff and see what works!






Old 12-04-2014, 12:02 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #34 (permalink)
Registered
 
GWN7's Avatar
 
Join Date: Jun 2002
Location: Winnipeg, MB, Canada
Posts: 3,963
While the basement is still open run wires for phone, cable TV and computer.
__________________
Bunch of old cars
Old 12-04-2014, 03:41 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #35 (permalink)
Platinum Member
 
dad911's Avatar
 
Join Date: Jul 2001
Location: Leave the gun. Take the cannoli.
Posts: 21,100
Quote:
Originally Posted by legion View Post
New Question:

What if I have a situation with a "T"?

I have an outlet in one room (A), about a foot from the wall (B), an outlet in the adjacent room about a foot from the wall (C), and another outlet on the wall in the middle of the "T" about five feet in.

Should I:
-Run wiring from A, to C, to B?
OR
-Run wiring from A to a junction, then to B and C?
Typically A>C>B is easiest, and wire is cheap. Simple, less connections=more reliable.

In the second case, the junction must be in a box, and has to be accessible. Also keep in mind that there is a code as to how many wires & devices can be in a box, based on the size of box(cubic inch) and wire gauge.

Old 12-04-2014, 05:07 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #36 (permalink)
Reply


 


All times are GMT -8. The time now is 11:40 PM.


 
Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2025, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2025 Pelican Parts, LLC - Posts may be archived for display on the Pelican Parts Website -    DMCA Registered Agent Contact Page
 

DTO Garage Plus vBulletin Plugins by Drive Thru Online, Inc.