can you measure from blue to white in both cases (above and below set temp)
And what does the label say on the contactors? Kind of strange all three would go at once, I'm trying to see if they are getting trigger voltage. I think we said each element draws less than 20 amps, so 12 gauge is ok. The total was close to 60, needing heavier service wire. The covering may be for temperature? I hate to re-invent the wheel, but is it time to modernize? one of these, with additional SSR (1 per element): https://smile.amazon.com/Inkbird-Temperature-Thermostat-Controllers-Fahrenheit/dp/B01KNXETWS/ref=sr_1_3?ie=UTF8&qid=1489526227&sr=8-3&keywords=pid+temp+controller
__________________
Political polls are often to give you an opinion, not to find out what your opinion is - Scott Adams Last edited by dad911; 03-14-2017 at 01:27 PM.. |
||
|
|
|
|
Registered
Join Date: Dec 2001
Location: Cambridge, MA
Posts: 44,468
|
I'll measure them tonight. They were 8 or 10V IIRC.
So that controller will replace mine and the SSRs would replace the contactors? I'm all for that given the price. Here's the controller I'm using now. https://www.amazon.com/Precision-Digital-Trident-Temperature-PD765-6R3-20/dp/B01NBMQ3TA/ref=sr_1_6?s=kitchen&ie=UTF8&qid=1489526589&sr=8-6&keywords=precision+digital+trident
__________________
Tru6 Restoration & Design |
||
|
|
|
|
Platinum Member
Join Date: Jul 2001
Location: Leave the gun. Take the cannoli.
Posts: 21,126
|
Quote:
__________________
Political polls are often to give you an opinion, not to find out what your opinion is - Scott Adams |
||
|
|
|
|
Registered
Join Date: Dec 2001
Location: Cambridge, MA
Posts: 44,468
|
I don't think mine has the 24V out. I'll call the company tomorrow, they are local and closed because of the snow.
__________________
Tru6 Restoration & Design |
||
|
|
|
|
Platinum Member
Join Date: Jul 2001
Location: Leave the gun. Take the cannoli.
Posts: 21,126
|
I don't know anything about mercury contactors. I wonder if they need a load to function?
__________________
Political polls are often to give you an opinion, not to find out what your opinion is - Scott Adams |
||
|
|
|
|
Platinum Member
Join Date: Jul 2001
Location: Leave the gun. Take the cannoli.
Posts: 21,126
|
Quote:
https://www.predig.com/pd765
__________________
Political polls are often to give you an opinion, not to find out what your opinion is - Scott Adams |
||
|
|
|
|
|
Registered
Join Date: Dec 2001
Location: Cambridge, MA
Posts: 44,468
|
0V above and below temp between white and blue on the contactors.
White is T2/common. Blue goes to the controller relay. When I check blue against T1 or T3 (black & red), I get 120V. So I think it's the controller. I'll call them tomorrow. Too frustrating.
__________________
Tru6 Restoration & Design |
||
|
|
|
|
Registered
Join Date: Dec 2001
Location: Cambridge, MA
Posts: 44,468
|
Here's the basic wiring diagram for the circuit. Very simple.
__________________
Tru6 Restoration & Design |
||
|
|
|
|
Registered
Join Date: Dec 2001
Location: Cambridge, MA
Posts: 44,468
|
OK, I've fixed it. Works perfectly now. But some interesting details.
It sends 211V to each heating element. Any suggestions on wiring I should use? With that, I can actually do a proper test run. When the relay clicks off at 210F, the volt values go back to the 40-50-60 as above.
__________________
Tru6 Restoration & Design |
||
|
|
|
|
Platinum Member
Join Date: Jul 2001
Location: Leave the gun. Take the cannoli.
Posts: 21,126
|
If it's 20A or under, 12 gauge should be ok.