Make Bruins Great Again
 
Por_sha911's Avatar
 
Join Date: Dec 2003
Location: TN
Posts: 20,816
Garage
Quote:
Originally Posted by Shaun @ Tru6 View Post
...I just want it done right and don't trust professionals because the few times I've used them I've been disappointed or feel ripped off. I mean it took me an hour...
I imagine there are a lot of folks that say the same thing about Porsche repair shops until they have to bring their car in on a flat bed with extra damage from their DIY repairs.

__________________
--------------------------------------
Joe
See Porsche run. Run, Porsche, Run: `87 911 Carrera
Old 12-09-2017, 07:10 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #101 (permalink)
Registered
 
DanielDudley's Avatar
 
Join Date: Jan 2007
Posts: 11,758
If you look at the very first picture in this thread, you can see that the connection that is now a problem was already corroded. You need a new box, and you need to figure out if the wires running out of the box are sufficient for your load, although they probably are.

I would use a pro, and I would get it inspected and approved. There are liability reasons for the above, and even though I know a lot about electricity, that is the reason why I would want someone else to do this job and have it inspected.
Also, If I were renting a place, I would consider this to be at least partly the landlords responsibility as regards repairs, unless I were intending to upgrade the system.

That box is literally toast. I had a similar problem in my house, and I replaced the box and upgraded to a 200 amp system, at which time I upgraded the system in my shop to 100 amps. I never looked back.

This could all have been done some time ago, and done right. I'm pretty sure that at some time in the recent past, that screw was red hot, as in RED hot. Electricians are usually licensed and insured, as are inspectors. It is in their best interest to use their knowledge and experience to do a good job for you. They have seen all this 100 times.

At some point I would have to ask myself, ''Well, since I didn't foresee THIS, what else don't I know ?''. Aside from having good connections, code compliance requirements have changed over the years. You want to be in compliance, inspected, and have a trail of liability heading away from you, unless you have the kind of insurance that will cover you in any foreseen or unforeseen instances heading into the future.

New work needs to be inspected, and you need a new box. That one is toast. Done, dead, deceased.

Last edited by DanielDudley; 12-10-2017 at 02:48 AM..
Old 12-10-2017, 02:28 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #102 (permalink)
Registered
 
DanielDudley's Avatar
 
Join Date: Jan 2007
Posts: 11,758


''This Parrot wouldn't move if you put 4000 volts through it. It's bleeding demised...''

Last edited by DanielDudley; 12-10-2017 at 02:46 AM..
Old 12-10-2017, 02:30 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #103 (permalink)
Registered
 
Join Date: May 2017
Posts: 15,530
Be sure your home (fire ) insurance is paid up.
Old 12-10-2017, 04:56 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #104 (permalink)
Registered
 
enzo1's Avatar
 
Join Date: Jul 2008
Location: OK
Posts: 12,730
Quote:
Originally Posted by Sooner or later View Post
Be sure your home (fire ) insurance is paid up.
Yes, because Sooner or later....
__________________
76' 911s Signature Edition
Old 12-10-2017, 06:57 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #105 (permalink)
Registered
 
Join Date: Sep 2009
Location: North of You
Posts: 9,160
A couple of notes...

The line wires look to be the same size as the load wires, so the pole fuses are likely 100 Amp, the code applies to the service provider too.

You might have an unbalanced load, I would guess the center phase sees close to 100 Amps regularly. You could address that with some rewiring, but I don't think it's worth the effort. You know how to fix it.

You have proper sized conductors and a working breaker (I think). The risk of a fire is minimal.

You could do a few tests with a clamp on ammeter, you may have outgrown your 100 Amp.
__________________
"A machine you build yourself is a vote for a different way of life. There are things you have to earn with your hands."
Old 12-10-2017, 07:53 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #106 (permalink)
 
Back in the saddle again
 
masraum's Avatar
 
Join Date: Oct 2001
Location: Central TX west of Houston
Posts: 55,841
Quote:
Originally Posted by Shaun @ Tru6 View Post
Thanks, I stand on a palette when working on it. Also I wrapped the screwdriver with EPDM; thought that a direct connection would kill me good. It's snowing today so not going to touch it until tomorrow. I may end up making a copper blade for the center.

I agree, I don't understand who would make such a crappy box given the surface area and quality of materials.
So not barefoot on a wet copper plate that's sitting on bare ground while using the plug in blade for an interchangeable screwdriver?
__________________
Steve
'08 Boxster RS60 Spyder #0099/1960
- never named a car before, but this is Charlotte.
'88 targa SOLD 2004 - gone but not forgotten
Old 12-10-2017, 01:56 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #107 (permalink)
You do not have permissi
 
john70t's Avatar
 
Join Date: Aug 2001
Location: midwest
Posts: 39,824
https://www.bing.com/search?q=electrocution+video+clips&pc=MOZI&form=MOZTSB
Old 12-10-2017, 02:20 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #108 (permalink)
Registered
 
Shaun @ Tru6's Avatar
 
Join Date: Dec 2001
Location: Cambridge, MA
Posts: 44,264
Quote:
Originally Posted by masraum View Post
So not barefoot on a wet copper plate that's sitting on bare ground while using the plug in blade for an interchangeable screwdriver?
Don't forget the battery clamps on my nipples. ACDC, gotta love it.

__________________
Tru6 Restoration & Design
Old 12-10-2017, 02:38 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #109 (permalink)
Registered
 
Shaun @ Tru6's Avatar
 
Join Date: Dec 2001
Location: Cambridge, MA
Posts: 44,264
Quote:
Originally Posted by 1990C4S View Post
A couple of notes...

The line wires look to be the same size as the load wires, so the pole fuses are likely 100 Amp, the code applies to the service provider too.

You might have an unbalanced load, I would guess the center phase sees close to 100 Amps regularly. You could address that with some rewiring, but I don't think it's worth the effort. You know how to fix it.

You have proper sized conductors and a working breaker (I think). The risk of a fire is minimal.

You could do a few tests with a clamp on ammeter, you may have outgrown your 100 Amp.
Thank you! I disconnected the center blade today. While I look for an electrician, it would be easy to make a 4 gauge wire connector with terminals that would bolt to the bus bar and plug in to the breaker. But won't have time for that this week so just going to leave it as is and start the search. Many thanks for your and dad's continued help.
__________________
Tru6 Restoration & Design
Old 12-10-2017, 02:46 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #110 (permalink)
Registered
 
MBAtarga's Avatar
 
Join Date: Jul 2001
Location: Lawrenceville GA 30045
Posts: 7,377
It's almost been a month. Did you get an electrician to take a look at this breaker/box?
__________________
Mark

'83 SC Targa - since 5/5/2001
'06 911 S Aerokit - from 5/2/2016 to 11/14/2018
'11 911 S w/PDK - from 7/2/2021 to ???
Old 01-03-2018, 05:36 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #111 (permalink)
Registered
 
Shaun @ Tru6's Avatar
 
Join Date: Dec 2001
Location: Cambridge, MA
Posts: 44,264
No, I ended up making the 4 gauge jumper that has worked perfectly, and will continue to I'm sure. Was checking every day, now once a week... it hasn't gotten hot or corroded or anything. But I am going to TIG together a new breaker to bus bar attachment and have it either cadmium or silver plated. The aluminum one I took off is absolute garbage. I'll probably make 2 other breaker to bus bar attachments this summer to replace the other two aluminum ones though they are fine, no corrosion, no sign of getting hot.

In this end, this was a very simple problem: the aluminum breaker to bus bar attachment was junk. Making a new one with solid clean connections has solved the problem. Definitely don't need a new breaker box.
__________________
Tru6 Restoration & Design

Last edited by Shaun @ Tru6; 01-03-2018 at 05:51 PM..
Old 01-03-2018, 05:49 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #112 (permalink)
 
Registered
 
Shaun @ Tru6's Avatar
 
Join Date: Dec 2001
Location: Cambridge, MA
Posts: 44,264
coming up on a year later and my repair has worked perfectly.
__________________
Tru6 Restoration & Design
Old 10-29-2018, 05:58 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #113 (permalink)
New kid in town
 
71T Targa's Avatar
 
Join Date: Nov 2001
Posts: 2,288
It was failing under the oppression of Obama.

Now that Trump is making America great again your breaker can thrive.

Remember that when it's time to vote!

__________________
I wish I still had 9111113443...
Old 10-29-2018, 07:36 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #114 (permalink)
Registered
 
Shaun @ Tru6's Avatar
 
Join Date: Dec 2001
Location: Cambridge, MA
Posts: 44,264
Lol!
__________________
Tru6 Restoration & Design
Old 10-30-2018, 03:12 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #115 (permalink)
Registered
 
Join Date: Sep 2009
Location: North of You
Posts: 9,160
There are lots of sprays you can use to prevent corrosion.

And some you can spray on live wires.
__________________
"A machine you build yourself is a vote for a different way of life. There are things you have to earn with your hands."
Old 10-30-2018, 05:15 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #116 (permalink)
Control Group
 
Tobra's Avatar
 
Join Date: Aug 2005
Location: Carmichael, CA
Posts: 53,469
Garage
Quote:
Originally Posted by Shaun @ Tru6 View Post
That's all I want to know. Other than the poor connection itself with the junk materials, what wiring malady on the floor would cause this, if that is even possible.
Maybe it is all the equipment you have installed in the place. You still don't know what the problem was, so you can't possibly know if you have fixed the issue.

In reading through this thread, I have come to the conclusion you don't have as much sense as I had thought.

You do realize that if there is ever a problem or someone gets hurt, this thread will hang your ass, right?
__________________
She was the kindest person I ever met
Old 10-30-2018, 12:28 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #117 (permalink)
Registered
 
Shaun @ Tru6's Avatar
 
Join Date: Dec 2001
Location: Cambridge, MA
Posts: 44,264
Quote:
Originally Posted by 1990C4S View Post
There are lots of sprays you can use to prevent corrosion.

And some you can spray on live wires.
No corrosion in a year. Clearly the original poor quality materials are what failed, and continued to fail. My high quality repair will outlast the rest of the box.
__________________
Tru6 Restoration & Design
Old 10-30-2018, 01:42 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #118 (permalink)
Registered
 
Join Date: Sep 2009
Location: North of You
Posts: 9,160
You have the approval of at least one electrical engineer.

Your solution is better than another cheap aluminum box from Mexico.
__________________
"A machine you build yourself is a vote for a different way of life. There are things you have to earn with your hands."
Old 10-30-2018, 01:46 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #119 (permalink)
Registered
 
Shaun @ Tru6's Avatar
 
Join Date: Dec 2001
Location: Cambridge, MA
Posts: 44,264
Thank you. If I had time, I would rebuild the whole thing. But it's been working for a year so I'm going to leave it alone for now.

__________________
Tru6 Restoration & Design
Old 10-30-2018, 01:47 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #120 (permalink)
Reply


 