Mrs WD wants black outlets and covers in the new kitchen. I HATE tamper resistant (IOW use resistant) outlets. The only round black outlets I can find without the tamper resistant defect are 20 amp. The circuit is wired with 12 ga wire and has a 15 amp breaker in the box. Will installing 20 amp outlets cause a problem down the road? Worst case as far as I can see is maybe someone will plug in something big and trip the breaker.
What say you? |
Try Home depot, Model # CR15-E Internet #301387040 ?
|
If it's in the kitchen it's required to be 20A circuit GFCI protected. If the work is being inspected the receptacles would be required to be tamperproof unless they are 5'6" above the floor.
The recpt type and wire size don't matter , the breaker does. I'm not cool with 15A to a kitchen space. Appliances such as bread makers,toasters,coffee makers, griddles when on the same circuit get you over 15 in a hurry. |
While it will work fine, it will not be to code. 12G wire is fine for 20A (14 is not)...but you need to change the breaker. I would upgrade both at the same time.
|
If the issue is to "hide" the outlets, try looking to mount outlet strips under the cabinets. About 20 years ago, I had my kitchen re-done and I hated the idea of putting outlets on the beautiful walls. I had my contractor install both under cabinet lighting and under cabinet outlet strips. When we had our kitchen here redone, I did the same thing.
|
The 20a will be fine on a 15a. circuit. If you have an overload situation the breaker will trip before things meltdown. As long as the wiring and breaker is sized appropriately for the circuit I wouldn't hesitate to put the 20a. receptacles in.
"Worst case as far as I can see is maybe someone will plug in something big and trip the breaker." You hit the nail on the head. It's the breaker that matters. You don't want a 20a breaker on wire that's only good for 15 amps. The wire could potentially meltdown before the breaker would trip. |
Quote:
|
Quote:
I don't care about code, I just don't want tthose damn tamper proof outlets. Now to find some 3/8 box extenders. :( |
Quote:
|
You don't care about code until you want to sell.
|
Quote:
|
|
Kitchen circuits. No more than two receptacles to a circuit. 20 amp. 12 ga. wire. minimum 4 receptacles. Within 1 meter of sink is GFCI. Kitchen receptacles do not need to be arc fault. Tamper proof is not required if the appliance is plugged in and receptacle is considered inaccessible. If you do not care about code, then you should consider cancelling your fire insurance. Do not paint your receptacles and believe me or not, in the long run , it is cheaper to do it right.
|
Quote:
its the WIRE size AND breaker size that matter. the breaker goes with the wire size. you can have a 15a brkr on 12ga wire. you can NOT have a 20a brkr on 14ga wire you CAN NOT (or should not) put a 20a OUTLET on 14ga wire with a 15 or 20a brkr this case the outlet matches the wire size. just remember, the breaker is there to protect the wiring, nothing else. the outlet limits you from connecting a single load that pulls more current than the WIRE can deliver. I prefer to run 12g with 20a outlets as the outlets are a bit beefier. not an electrician btw. |
Quote:
|
Quote:
|
Quote:
|
Quote:
|
Quote:
Well, for starters, every receptacle in the kitchen must be protected by a GFCI as well as the laundry. A recep is required over any counter with a wall behind 2 feet or longer and must not be more than 4' apart. Recep's on each side of the sink must not be more than 2' from edge of said sink. Islands and peninsulas require at least one recep but could be more depending on dimensions. Individual circuits required for DW, GD, Micro, hood, fridge, trash compactor and could be more depending on any one item's electrical draw. Not less than 2 convenience circuits but they are not limited to 1 recep per circuit. Lighting is separate. This is all ad lib from memory, not the way to approach electrical work. So any corrections are welcome. And I didn't even touch on AFCI's which are now required in all areas of the home living space except the baths. The garage, crawl space, attic, and outdoors are not considered living spaces but sunrooms are. |
Correct zeke. This has been discussed before. It also MEETS CODE to use 15a receptacles on 12 gauge 20 amp breakers.
http://forums.pelicanparts.com/off-topic-discussions/983501-confused-about-nec-standard.html |
All times are GMT -8. The time now is 11:37 PM. |
Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2025, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2025 Pelican Parts, LLC - Posts may be archived for display on the Pelican Parts Website