Just got everything connected and I'm pulling a vacuum unsing the Robinair 15434. Turned pump on about 5 minutes ago and it is running continously. Is this normal? PSI reads neg 30. I'll go shut of the maniold gauges and the pump now to see if it holds a vacuum or I have a leak.
Thanks!
__________________
Mark 1987 911 Coupe Granite Green Metallic My Cousin's Wife's Sister's Husband is a Lawyer. Last edited by mthomas58; 05-10-2008 at 12:28 PM.. |
||
![]() |
|
Original Owner
Join Date: Dec 2002
Location: San Antonio, Texas
Posts: 1,907
|
Yes - normal.
No - do not close the manifold gauges to check for vacuum leaks. Leave them open. Close the Iso-Valve on the 15434 only. That will isolate the pump from the system. Then turn the pump off. Watch the vacuum gauge reading over nite for movement indicating a leak. Before charging, pull vacuum overnite. 5 minutes or 30 minutes won't do the trick except for a basic leak test.
__________________
tsuter 78 911SC Turbo Targa Thaaaats Right!! |
||
![]() |
|
Throw it on the ground!
Join Date: Aug 2006
Location: Atlanta, GA
Posts: 2,566
|
OK thanks. I've had the pump shut off for 30 minutes now and its holding steady at -30 PSI. I've got a nitrogen bottle that I'm going to pressure test at 150 -175 PSI for leaks. If no leaks, I'll pull anther vacuum for 3 hours or so then charge and I should be OK.
__________________
Mark 1987 911 Coupe Granite Green Metallic My Cousin's Wife's Sister's Husband is a Lawyer. |
||
![]() |
|
Throw it on the ground!
Join Date: Aug 2006
Location: Atlanta, GA
Posts: 2,566
|
Holding steady on Nitrogen pressure test at 155 PSI - NO LEAKS!!!!!
![]() ![]() ![]() ![]()
__________________
Mark 1987 911 Coupe Granite Green Metallic My Cousin's Wife's Sister's Husband is a Lawyer. |
||
![]() |
|
UnRegistered User
|
Leak checking with lots of pressure can be a bit deceiving.
Most of the leaks on these systems can be pretty small. You may not notice a pressure drop on the gauges for a quite some period of time. As mentioned before, a vacuum test is a great way of determining if the system is tight. Pull your best vacuum and isolate your vac pump. Look for a loss of vacuum overnight. On small leaks it will be more evident with a vacuum than with pressure. If you find that you can't hold a vacuum, then nitrogen and trace gas in the system and a good electronic leak detector is your friend... Don't forget to consider lubricant (I know how that sounds) when adding refrigerant to the system. You will lose oil when you lose gas... (Oil is a great indicator of a refrigerant leak)
__________________
Bill K. "I started out with nothin and I still got most of it left...." 83 911 SC Guards Red (now gone) And I sold a bunch of parts I hadn't installed yet. |
||
![]() |
|
Registered
|
When I ran this drill, I was surprised at the static pressure variation with temperature. So if you do leave it pressurized over nite you will have to check it at the same temp the next day as your earlier reading. Ken
|
||
![]() |
|
![]() |
Registered
Join Date: Jan 2008
Posts: 19
|
Quote:
Leak testing is done both in a vacuum and pressure. The best available tool for checking under vacuum is a micron gauge - it splits the last 12 inches of mercury into 300,000 microns - I normally pull a car down to 250 microns. Yacht refrigeration manufacturers only warranty units that have been pulled to 250 microns x 4 hrs and I use a dial recorder and add the wheel to the receipts. http://www.achrnews.com/Articles/How_To/b1a8ec2f93f5a010VgnVCM100000f932a8c0____ Anyway - pull the vacuum overnight - the freon permiates into the oil - along with moisture - and pulling the freon out of the oil is only done by holding a heavy vacuum over time. if your gauges don't move for 30 minutes, after closing the manifold, you only know you don't have a bad leak. There is no such thing as a good leak.... The micron gauge is the only effective way to find out how much of a leak you really have. The gauge can be a bit deceiving as your hoses permiate and there condition can actually be read, even when the job is properly done. With the funds you have invested in the nitrogen, vacuum pump, manifold set, and your education - you'll find the micron gauge to be a great tool. http://www.acsource.com/index.asp?PageAction=VIEWPROD&ProdID=561 There are cheaper ones out there - this is just like the model I've been using for 10+ years. Sea Ya, michael |
||
![]() |
|
UnRegistered User
|
+1 on the vac gauge.. It is the best way after a good pull on the vacuum pump to determine if you have any leaks. Also a great way to test your vacuum pumps performance.
One thing to do is change your pump oil regularly after use (clean oil for times between use/ no contaminants left in pump). Change it hot!! Also change your oil before you do your final pull down on the system. The pump will perform better. Back in the day, we would do a triple evac. Breaking vacuum with refrigerant to atmospheric and pulling a vacuum again. Can't do that now though....
__________________
Bill K. "I started out with nothin and I still got most of it left...." 83 911 SC Guards Red (now gone) And I sold a bunch of parts I hadn't installed yet. |
||
![]() |
|
Registered
Join Date: Jan 2008
Posts: 19
|
Quote:
![]() |
||
![]() |
|
Registered
|
Nice to have all the tools you got. You are still missing an important tool. Electronic leak detector. You charge a little refrigerant and pressurize with nitrogen and use the electronic leak detector. I don't trust the vacuum test.