it is, sort of (per national bldg code):
M1502.4.1 Material and size. Exhaust ducts shall have a smooth interior finish and shall be constructed of metal a minimum 0.016-inch (0.4 mm) thick. The exhaust duct size shall be 4 inches (102 mm) nominal in diameter. M1502.4.3 Transition duct. Transition ducts used to connect the dryer to the exhaust duct system shall be a single length that is listed and labeled in accordance with UL 2158A. 25 foot max, unless specified otherwise by dryer mfg. Deduct 5' each for std 90's, less for sweeps depending on radius. So a run with three 90's can only have 10' of pipe. |
||
|
|
|