One more question,
You mention it went back to not functioning properly. Is it throwing any codes similar to those that led you to check the vent pipe? Reason I ask is, if the exhaust bent is drooping, after a couple of cycles it will collect enough condensation to cause a blockage in the vent which would prevent the pressure switch from closing.
FWIW, I might be heading down to Washington Courthouse later in the week. If I do and can be of help, you have my number.

__________________
Nick
Old 12-11-2018, 02:39 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #61 (permalink)
Registered
 
wdfifteen's Avatar
 
Join Date: Mar 2008
Location: SW Ohio
Posts: 29,328
Garage
Quote:
Originally Posted by greglepore View Post
Trust me, the intrinsic worth of each hour increases linearly with age
+1000
Maybe even exponentially.
__________________
.
Old 12-11-2018, 02:58 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #62 (permalink)
Registered
 
wdfifteen's Avatar
 
Join Date: Mar 2008
Location: SW Ohio
Posts: 29,328
Garage
Quote:
Originally Posted by cabmando View Post
One more question,
You mention it went back to not functioning properly. Is it throwing any codes similar to those that led you to check the vent pipe? Reason I ask is, if the exhaust bent is drooping, after a couple of cycles it will collect enough condensation to cause a blockage in the vent which would prevent the pressure switch from closing.
FWIW, I might be heading down to Washington Courthouse later in the week. If I do and can be of help, you have my number.
You have been far more than generous. Maybe we could meet somewhere for coffee while you're out if the timing is right. I have met a couple of pelicans, can't hurt to meet another one.
Yes, it's showing the same code, three flashes. That's probably a good diagnosis. I love the challenge of wrestling a problem to the ground, and obviously you do too. PPOT is a great community!
__________________
.
Old 12-11-2018, 03:03 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #63 (permalink)
Registered
 
Join Date: Mar 2005
Location: Jersey Shore
Posts: 1,084
Garage
stupid question, i'm full of them, have you changed the filter?
__________________
Chris
the more i learn, the less i know
Old 12-11-2018, 03:09 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #64 (permalink)
Registered
 
wdfifteen's Avatar
 
Join Date: Mar 2008
Location: SW Ohio
Posts: 29,328
Garage
Quote:
Originally Posted by carambola View Post
stupid question, i'm full of them, have you changed the filter?
LOL!
Yes. And there are no stupid questions. That's just the kind of thing that pounded that flat spot onto my forehead.
__________________
.
Old 12-11-2018, 03:15 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #65 (permalink)
Brew Master
 
cabmandone's Avatar
 
Join Date: Jul 2013
Location: Delphos OH
Posts: 32,153
Garage
FWIW, The reason I mention condensation is because I had that very issue pop up on a system once. I strapped the vent to the proper pitch (it should pitch back to the furnace where the condensation will flow from the condensate drain) and the problem went away. If it was a circuit board issue I don't think that it would cycle a few times before showing up. I suppose it's possible for the IFR (inducer fan relay) to be loose causing it to intermittently work but I think since it worked right after you did the vent cleaning the first time I think it's something vent related. If you decide to try and pitch the vent you want at least 1/2" per 10 foot section sloping back to the furnace. Don't do a hard reset (on and off with the breaker) but rather turn the thermostat down so that the call for heat would end and then switch it off. This is called a "soft reset". The furnace should try to run after a soft reset unless it it locked out due to too many attempts and failures.

If you're willing to have a go at it, I'm willing to advise... And if by coffee you mean a beer, I'd be game.
__________________
Nick

Last edited by cabmandone; 12-11-2018 at 04:12 PM..
Old 12-11-2018, 04:09 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #66 (permalink)
Brew Master
 
cabmandone's Avatar
 
Join Date: Jul 2013
Location: Delphos OH
Posts: 32,153
Garage
Another possible issue that can cause an ignition failure (I'm guessing that's what he 3 flash code means) is a blocked drain. Typically where the small tubes connect to the collector box of the secondary heat exchanger, it will become plugged with water if the condensate drain isn't flowing due to a blocked trap or other obstruction. Another thing I found once was a slight calcium buildup blocking one of the small ports where the tube for the pressure switch attaches to the secondary HE collector.

A thought on the "rust" in the HE and burner. I'm guessing you're burning propane. If I'm right, it's not all that uncommon for some rust in the Burner and HE. The burners on my old furnace had a lot of rust in them. My issue with many "technicians" is they don't troubleshoot anymore (listen to me! I'm all of 47 talking like the old guys LOL) If your combustion is a concern a good tech should carry a handheld Combustion analyzer. I haven't done HvAC for over 10 years and I own one because I don't like guessing. Analyzing the combustion will give a tech a good idea of the condition of the Heat exchanger and the overall condition of the system. Being old enough to be considered "old school" I can normally look at the flame and tell but a CO Analyzer is a better way to do it.
__________________
Nick

Last edited by cabmandone; 12-11-2018 at 04:22 PM..
Old 12-11-2018, 04:12 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #67 (permalink)
vmb vmb is offline
Registered
 
vmb's Avatar
 
Join Date: Jun 2004
Location: Catonsville, MD
Posts: 286
So, I had a very similar problem the past 3 weeks, with a 9 year old Trane XR90 furnace. Throwing the 4 flash code which indicates a problem with the temperature limit sensor. So, I ordered a new sensor. Didn't fix the problem. After going through the vent checks I noticed that if I unplugged and replugged one of the wire bundles, or just mucked around with it, the furnace would work intermittently. Taking it off I could not see any broken solder joints, and without any experience at troubleshooting a circuit board, I found a brand new one for $125. Just installed it 10 minutes ago and the upstairs is already getting toasty

I'll plug the parts source I used- northamericahvac.com. Customer service was absolutely fantastic, super fast shipping, and they even took the limit sensor back and issued a full refund. In their words, "if it did not fix your issue, please return it and we'll issue a full refund. Thanks!" Really good communication via email.
__________________
Vic
'79 930
'97 Miata M edition
missing my Tony//Kart 125cc shifterkart
Old 12-11-2018, 04:58 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #68 (permalink)
Registered
 
wdfifteen's Avatar
 
Join Date: Mar 2008
Location: SW Ohio
Posts: 29,328
Garage
Quote:
Originally Posted by cabmando View Post
A thought on the "rust" in the HE and burner. I'm guessing you're burning propane. If I'm right, it's not all that uncommon for some rust in the Burner and HE. The burners on my old furnace had a lot of rust in them. My issue with many "technicians" is they don't troubleshoot anymore (listen to me! I'm all of 47 talking like the old guys LOL) If your combustion is a concern a good tech should carry a handheld Combustion analyzer.
.
He had an inspection camera and took video of the inside of the heat exchanger. This was last January when I had the house inspected. He noted the rust, but did not see any cracks. BTW we're burning natural gas.

Welll...

He took the furnace out this morning and found this:



I'm glad I decided to replace this furnace instead of trying to fix it.
Kind of annoyed that neither of the guys who looked at it did a safety check on this 20 years old furnace, they just focused on the immediate problem. A whole lot of effort could have been avoided if they had given the rusty 20 year old heat exchanger more attention to begin with.
__________________
.
Old 12-13-2018, 06:33 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #69 (permalink)
Registered
 
biosurfer1's Avatar
 
Join Date: Oct 2003
Location: Roseville, CA
Posts: 3,066
Start chewing some gum and you'll have that fixed in no time
__________________
1992 968 Polar Silver
2010 Toyota Highlander SE
2006 Lexus LS430 ML
Old 12-13-2018, 07:23 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #70 (permalink)
Brew Master
 
cabmandone's Avatar
 
Join Date: Jul 2013
Location: Delphos OH
Posts: 32,153
Garage
That thing should have been burning really yellow with a crack like that!
PSA: Always have a carbon monoxide detector in your home childrens!
__________________
Nick
Old 12-13-2018, 07:51 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #71 (permalink)
UnRegistered User
 
billybek's Avatar
 
Join Date: Dec 2007
Location: Calgary
Posts: 8,026
Garage
Quote:
Originally Posted by cabmando View Post
That thing should have been burning really yellow with a crack like that!
PSA: Always have a carbon monoxide detector in your home childrens!
Yes. Nasty (not in a good way) crack. I have two CO detectors and my house and should probably have more (one in each bedroom).
The one positive thing about newer furnaces is that the combustion side of the heat exchanger is usually negative in pressure.
Good that you have the thing changed out.
__________________
Bill K.
"I started out with nothin and I still got most of it left...."
83 911 SC Guards Red (now gone)
And I sold a bunch of parts I hadn't installed yet.
Old 12-13-2018, 07:19 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #72 (permalink)
 
The Stick
 
RKDinOKC's Avatar
 
Join Date: Dec 2007
Location: Someplace Safe?
Posts: 17,328
Garage
When mine when out a few years ago could have done the fix route, but listened to my HVAC guy. Got a new one because it was way more efficient. Also ended up doing the install over a Memorial weekend. Told the guy to go fishin it wasn't going to get either hot or cold that weeked. He gave me so much off because of that, couldn't find anything on the internet that size for the price including the install.

__________________
Richard aka "The Stick"
06 Cayenne S Titanium Edition
Old 12-13-2018, 07:41 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #73 (permalink)
Reply


 


All times are GMT -8. The time now is 06:15 PM.


 
Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2025, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2025 Pelican Parts, LLC - Posts may be archived for display on the Pelican Parts Website -    DMCA Registered Agent Contact Page
 

DTO Garage Plus vBulletin Plugins by Drive Thru Online, Inc.