Buck-Boost Converter

Who here knows about buck-boost converters?

My shop has 208v 3-phase. My pottery kiln is for 240v 1-phase. I have an available circuit for 208v 1-phase (2 hots and neutral). I'd like to boost voltage from that circuit to 240v, so the kiln works as it should.

Looks like I can buy a buck-boost converter 208v primary to 240v secondary, that is rated for the appropriate amperage (kiln pulls 45A, circuit is on a 60A breaker and 4 gauge wire). Converter is several hundred $ but converting the kiln elements and controller to 208v will cost more.

__________________
1989 3.2 Carrera coupe; 1988 Westy Vanagon, Zetec; 1986 E28 M30; 1994 W124; 2004 S211
What? Uh . . . “he” and “him”?
Old 05-12-2022, 09:50 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #1 (permalink)
canna change law physics
 
red-beard's Avatar
 
Join Date: Jul 2000
Location: Houston, Tejas
Posts: 43,366
Garage
You want a 12 KVA or larger transformer.
__________________
James
The pessimist complains about the wind; the optimist expects it to change; the engineer adjusts the sails.- William Arthur Ward (1921-1994)
Red-beard for President, 2020
Old 05-12-2022, 11:50 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #2 (permalink)
Registered
 
Shaun @ Tru6's Avatar
 
Join Date: Dec 2001
Location: Cambridge, MA
Posts: 44,207
I did this exact job 7 years ago John. I got a BBT for my 240V compressor. Easy to do and works perfectly.

I got this one I am pretty sure.

https://www.grainger.com/product/4LEG1?s_kwcid=AL!2966!3!335651079981!p!!g!!t181052&ef_id=Cj0KCQjw4PKTBhD8ARIsAHChzRIFpjjgVw3Cj64HveWV yVN9341QXfyNjbpgz4MmYRZsMOZeEbpjb1gaAsiBEALw_wcB:G :s&s_kwcid=AL!2966!3!335651079981!p!!g!!t181052&gucid=N:N:PS:Paid:GGL:CSM-2296:AB578S:20500731&gclid=Cj0KCQjw4PKTBhD8ARIsAHChzRIFpjjgVw3Cj64HveWV yVN9341QXfyNjbpgz4MmYRZsMOZeEbpjb1gaAsiBEALw_wcB&gclsrc=aw.ds
__________________
Tru6 Restoration & Design

Last edited by Shaun @ Tru6; 05-12-2022 at 12:21 PM..
Old 05-12-2022, 11:59 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #3 (permalink)
jyl jyl is online now
Registered
 
jyl's Avatar
 
Join Date: Jan 2002
Location: Nor California & Pac NW
Posts: 24,497
Garage
https://www.larsonelectronics.com/product/148856/1-phase-buck-boost-step-up-transformer-208v-primary-240v-secondary-at-46-8-amps-50-60hz

"The MT-BBT-208V-240V-46.8A buck and boost transformer is a single phase unit with a 11 KVA rating and a primary voltage of 208 AC using a maximum of 53.1 amps on the primary side. This step-up transformer has a secondary voltage of 240 and provides up to 46.8 amps available on the secondary side."

https://www.larsonelectronics.com/images/product/Specsheet/148856.PDF

https://www.larsonelectronics.com/images/product/WiringDiagram/148856.PDF

This looks like what I need. US made, $530.
__________________
1989 3.2 Carrera coupe; 1988 Westy Vanagon, Zetec; 1986 E28 M30; 1994 W124; 2004 S211
What? Uh . . . “he” and “him”?

Last edited by jyl; 05-12-2022 at 12:16 PM..
Old 05-12-2022, 12:11 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #4 (permalink)
canna change law physics
 
red-beard's Avatar
 
Join Date: Jul 2000
Location: Houston, Tejas
Posts: 43,366
Garage
NEC requires you put in breakers and other equipment sized for 125% of the maximum load. 45 Amps --> 56.25 or rounded up to 60 Amps.
__________________
James
The pessimist complains about the wind; the optimist expects it to change; the engineer adjusts the sails.- William Arthur Ward (1921-1994)
Red-beard for President, 2020
Old 05-12-2022, 12:20 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #5 (permalink)
jyl jyl is online now
Registered
 
jyl's Avatar
 
Join Date: Jan 2002
Location: Nor California & Pac NW
Posts: 24,497
Garage
Quote:
Originally Posted by red-beard View Post
NEC requires you put in breakers and other equipment sized for 125% of the maximum load. 45 Amps --> 56.25 or rounded up to 60 Amps.
The breaker is 60A. The circuit is wired with 4 ga in dedicated conduit.
__________________
1989 3.2 Carrera coupe; 1988 Westy Vanagon, Zetec; 1986 E28 M30; 1994 W124; 2004 S211
What? Uh . . . “he” and “him”?
Old 05-12-2022, 12:31 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #6 (permalink)
 
canna change law physics
 
red-beard's Avatar
 
Join Date: Jul 2000
Location: Houston, Tejas
Posts: 43,366
Garage
A 60A breaker on the 208 VAC side is undersized. You need a 70A breaker. The #4 wire is fine.

45A * 240/208 = 51.9A. BUT you must size this up by 125% to meet NEC -> 64.9, round up to 70A
__________________
James
The pessimist complains about the wind; the optimist expects it to change; the engineer adjusts the sails.- William Arthur Ward (1921-1994)
Red-beard for President, 2020
Old 05-12-2022, 12:58 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #7 (permalink)
Registered
 
Join Date: Mar 2005
Location: Northern CA
Posts: 4,703
Quote:
Originally Posted by red-beard View Post
A 60A breaker on the 208 VAC side is undersized. You need a 70A breaker. The #4 wire is fine.

45A * 240/208 = 51.9A. BUT you must size this up by 125% to meet NEC -> 64.9, round up to 70A
Is not having a 70A breaker a safety issue? Why is it not ok to have a lower rated breaker? This assumes the load will not trip the 60A breaker in normal circumstances.
__________________
Sold: 1989 3.2 coupe, 112k miles
Old 05-12-2022, 01:26 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #8 (permalink)
jyl jyl is online now
Registered
 
jyl's Avatar
 
Join Date: Jan 2002
Location: Nor California & Pac NW
Posts: 24,497
Garage
Quote:
Originally Posted by hcoles View Post
Is not having a 70A breaker a safety issue? Why is it not ok to have a lower rated breaker? This assumes the load will not trip the 60A breaker in normal circumstances.
I’d appreciate more explanation of this. What I read was that the breaker can be “at most” 125% of the expected amperage. I can certainly swap in a bigger breaker if need be, just trying to learn.
__________________
1989 3.2 Carrera coupe; 1988 Westy Vanagon, Zetec; 1986 E28 M30; 1994 W124; 2004 S211
What? Uh . . . “he” and “him”?
Old 05-12-2022, 02:37 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #9 (permalink)
canna change law physics
 
red-beard's Avatar
 
Join Date: Jul 2000
Location: Houston, Tejas
Posts: 43,366
Garage
This is how the National Electrical Code specifies you size a breaker and wiring. Yes, you can have a too small breaker, but you are likely to trip it and thermally burn it out over time.
__________________
James
The pessimist complains about the wind; the optimist expects it to change; the engineer adjusts the sails.- William Arthur Ward (1921-1994)
Red-beard for President, 2020

Last edited by red-beard; 05-12-2022 at 02:55 PM..
Old 05-12-2022, 02:47 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #10 (permalink)
canna change law physics
 
red-beard's Avatar
 
Join Date: Jul 2000
Location: Houston, Tejas
Posts: 43,366
Garage
__________________
James
The pessimist complains about the wind; the optimist expects it to change; the engineer adjusts the sails.- William Arthur Ward (1921-1994)
Red-beard for President, 2020
Old 05-12-2022, 02:56 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #11 (permalink)
jyl jyl is online now
Registered
 
jyl's Avatar
 
Join Date: Jan 2002
Location: Nor California & Pac NW
Posts: 24,497
Garage
Thanks James!
__________________
1989 3.2 Carrera coupe; 1988 Westy Vanagon, Zetec; 1986 E28 M30; 1994 W124; 2004 S211
What? Uh . . . “he” and “him”?
Old 05-12-2022, 05:54 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #12 (permalink)
jyl jyl is online now
Registered
 
jyl's Avatar
 
Join Date: Jan 2002
Location: Nor California & Pac NW
Posts: 24,497
Garage
Not directly related to the BBT, but I’ve decided to rebuild that circuit. The three 4 ga wires are in 3/4” conduit, I’m going to replace with larger, for wire fill rules.

__________________
1989 3.2 Carrera coupe; 1988 Westy Vanagon, Zetec; 1986 E28 M30; 1994 W124; 2004 S211
What? Uh . . . “he” and “him”?
Old 05-13-2022, 04:28 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #13 (permalink)
Reply


 


All times are GMT -8. The time now is 12:13 PM.


 
Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2025, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2025 Pelican Parts, LLC - Posts may be archived for display on the Pelican Parts Website -    DMCA Registered Agent Contact Page
 

DTO Garage Plus vBulletin Plugins by Drive Thru Online, Inc.