Electricians, question about tripped circuit

I have a 15amp breaker in the box and when I run multiple items in the garage it keeps tripping. It's been really annoying lately so I've been really careful about running stuff and unplugging items while I use other stuff. Any ways, what if I just change out the 15 to a 20amp would that help or cure the problem?

__________________
Bill
997.2
Old 02-01-2011, 03:41 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #1 (permalink)
abit off center
 
cgarr's Avatar
 
Join Date: Feb 2002
Location: At the Airport Kentwood, MI
Posts: 7,311
Garage
Send a message via Yahoo to cgarr
How hard would it be to pull another line from the garage? Most likely it would even trip a 20amp if it only trips on power up when tools draw the most.

You getting any snow yet?
__________________
______________________
Craig
G2Performance
Twinplug, head work, case savers, rockers arms, etc.

Last edited by cgarr; 02-01-2011 at 04:15 PM..
Old 02-01-2011, 04:13 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #2 (permalink)
Registered
 
Join Date: Dec 2005
Posts: 3,384
You need a new dedicated line or maybe even a new box just for the garage. Call an electrician because this is a standard project for them.
Old 02-01-2011, 04:16 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #3 (permalink)
UnRegistered User
 
billybek's Avatar
 
Join Date: Dec 2007
Location: Calgary
Posts: 8,018
Garage
Upgrading a breaker from 15 amp to 20 might cure the tripping problem....
The wire is most likely 14 gauge and rated for 15 amps. If you put more amps through that wire, it may melt/start a fire.
Your insurance co will not look kindly on this....
__________________
Bill K.
"I started out with nothin and I still got most of it left...."
83 911 SC Guards Red (now gone)
And I sold a bunch of parts I hadn't installed yet.
Old 02-01-2011, 04:22 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #4 (permalink)
wcc wcc is offline
Registered
 
wcc's Avatar
 
Join Date: Aug 2005
Location: Michigan
Posts: 3,381
Oh yeah the snow is coming and blowing around. Well what happened is I tapped into the circuit and added some new outlets not thinking it would be an issue. And it hasn't been for years. It's only an issue now because there is a heater in there now and the deep freezer kicks on/off and when I throw the air compressor or lift in there it trips all the time. What a pain in the butt because it's in the basement. It trips when stuff kicks on and sometimes it's fine and sometimes it trips when stuff kicks off.
__________________
Bill
997.2
Old 02-01-2011, 04:26 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #5 (permalink)
wcc wcc is offline
Registered
 
wcc's Avatar
 
Join Date: Aug 2005
Location: Michigan
Posts: 3,381
Quote:
Originally Posted by billybek View Post
Upgrading a breaker from 15 amp to 20 might cure the tripping problem....
The wire is most likely 14 gauge and rated for 15 amps. If you put more amps through that wire, it may melt/start a fire.
Your insurance co will not look kindly on this....
It's the 14-2 wire and where I tapped in I used 12-2 so would it be ok?
__________________
Bill
997.2
Old 02-01-2011, 04:29 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #6 (permalink)
 
abit off center
 
cgarr's Avatar
 
Join Date: Feb 2002
Location: At the Airport Kentwood, MI
Posts: 7,311
Garage
Send a message via Yahoo to cgarr
I would pull a new line for the heater at least. Do your lights flicker when the compressor is running? 12 is used with 20amp but how long of run too?

__________________
______________________
Craig
G2Performance
Twinplug, head work, case savers, rockers arms, etc.

Last edited by cgarr; 02-01-2011 at 04:35 PM..
Old 02-01-2011, 04:31 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #7 (permalink)
wcc wcc is offline
Registered
 
wcc's Avatar
 
Join Date: Aug 2005
Location: Michigan
Posts: 3,381
The run is short but there are many, 5? Yes the lights flicker when the freezer kicks on. I'm going to take that out of the equation soon because all these issues really came up when I installed it. Maybe I'll just get rid of it and put the stand up one back in the basement and be worry free...
__________________
Bill
997.2
Old 02-01-2011, 04:36 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #8 (permalink)
UnRegistered User
 
billybek's Avatar
 
Join Date: Dec 2007
Location: Calgary
Posts: 8,018
Garage
Can you re wire the whole run with 12 gauge?
If not, then no....
__________________
Bill K.
"I started out with nothin and I still got most of it left...."
83 911 SC Guards Red (now gone)
And I sold a bunch of parts I hadn't installed yet.
Old 02-01-2011, 05:05 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #9 (permalink)
Registered
 
wdfifteen's Avatar
 
Join Date: Mar 2008
Location: SW Ohio
Posts: 29,278
Garage
Quote:
Originally Posted by wcc View Post
there is a heater in there now and the deep freezer kicks on/off and when I throw the air compressor or lift in there it trips all the time.
When the 15 amp breaker trips it is telling you the circuit is overloaded. If you replace it with a 20 the smoke and flames shooting out of the walls will tell you the circuit is overloaded. Either way, you are asking the wires and wire connections to carry more current than they are designed for. You need to have an additional circuit installed.
__________________
.
Old 02-01-2011, 05:13 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #10 (permalink)
wcc wcc is offline
Registered
 
wcc's Avatar
 
Join Date: Aug 2005
Location: Michigan
Posts: 3,381
Oh, I'm sure it can be done but it'll be a a pain now it's all insulated up there. I was trying to find the easy way out but I don't want to cause a fire. Probably running a new wire would be just as difficult. I'll call my electrician to see what he comes up with..
__________________
Bill
997.2
Old 02-01-2011, 05:18 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #11 (permalink)
Registered
 
A930Rocket's Avatar
 
Join Date: Oct 2003
Location: Mount Pleasant, South Carolina
Posts: 14,161
Definately pulling too many amps. Can you run a dedicated line to the fridge, even if it's in conduit on top of the drywall? It should be on one anyway.

With all that you're running, you may want two circuits in the garage.
Old 02-01-2011, 05:26 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #12 (permalink)
 
Registered
 
Oh Haha's Avatar
 
Join Date: Oct 2003
Location: Michigan
Posts: 14,093
Bill,
I would see about running a dedicated circuit for the lift, if anything. I'm not good with 'lectrical stuff so I can't help you out.
__________________
1981 911SC ROW SOLD - JULY 2015
Pacific Blue

Wayne
Old 02-01-2011, 05:52 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #13 (permalink)
Registered
 
Join Date: May 2002
Location: St Louis
Posts: 4,211
Quote:
Originally Posted by wcc View Post
It's the 14-2 wire and where I tapped in I used 12-2 so would it be ok?
Sure.... Only the 14 ga would catch fire.
__________________
Rick
88 Cab
Old 02-01-2011, 07:39 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #14 (permalink)
wcc wcc is offline
Registered
 
wcc's Avatar
 
Join Date: Aug 2005
Location: Michigan
Posts: 3,381
Ok, thanks guys. I won't change it and I'll call an electrican.
__________________
Bill
997.2
Old 02-02-2011, 02:59 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #15 (permalink)
Registered
 
Join Date: Nov 2009
Location: Il
Posts: 113
Do yourself a favor and have a sub panel put in the garage.
Old 02-02-2011, 03:56 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #16 (permalink)
Unoffended by naked girls
 
dhoward's Avatar
 
Join Date: Sep 2002
Location: St. Charles, MO
Posts: 5,894
Garage
Send a message via AIM to dhoward
Or just replace the breaker that's become weak from tripping.
Sparks and flames? C'mon..
Hang an amp probe on it and see what you're really drawing.

Or pay an electrician.
__________________
Dan
1969 911T (sold)
2008 FXDL
www.labreaprecision.com
www.concealedcarrymidwest.com
Old 02-02-2011, 06:38 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #17 (permalink)
UnRegistered User
 
billybek's Avatar
 
Join Date: Dec 2007
Location: Calgary
Posts: 8,018
Garage
Quote:
Originally Posted by dhoward View Post
Or just replace the breaker that's become weak from tripping.
Sparks and flames? C'mon..
Hang an amp probe on it and see what you're really drawing.

Or pay an electrician.
Breakers do get weak with age and continued cycling.
A new 15 amp breaker would be worth trying if you don't have an amp clamp.

Sparks and flames? Sure. That is how homes and garages burn down. Poorly installed and improperly upgraded wiring.
__________________
Bill K.
"I started out with nothin and I still got most of it left...."
83 911 SC Guards Red (now gone)
And I sold a bunch of parts I hadn't installed yet.
Old 02-02-2011, 09:24 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #18 (permalink)
Senior Member
 
Superman's Avatar
 
Join Date: Feb 2000
Location: Lacey, WA. USA
Posts: 25,310
Quote:
Originally Posted by klm2500hd View Post
Do yourself a favor and have a sub panel put in the garage.
Yeah, I know it's expensive and troublesome, but worth it to me. My house was overbuilt and overmaintained by the PO/Builder, and the older I get, the more I like the idea of doing more than the minimum required. I think I went with either 4 or 6 AWG, and an 80A breaker. I don't have a welder out there, but could if I wanted.

It might be possible to detach the existing cable at both ends (and whatever staples exist along the way) and with two people, it may be possible to pull the new cabling through using the old cable.
__________________
Man of Carbon Fiber (stronger than steel)

Mocha 1978 911SC. "Coco"
Old 02-02-2011, 10:58 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #19 (permalink)
N-Gruppe doesn't exist
 
teenerted1's Avatar
 
Join Date: Jun 2005
Location: *%@#ing GPS, where am I? Oh wait I see the Space Needle.
Posts: 4,394
Send a message via AIM to teenerted1
wait until you have a house fire in the middle of the next storm....talk about a pain.
get your electrician involved

__________________
Ted
'70 911T 3.0L "SKIPPY" R-Gruppe #477
'73 914 2.0L SOLD bye bye "lil SMOKEY"
"Silence is Golden, but duct tape is SILVER.”
other flat fours:'77 VWBus 2.0L & 2002 ImprezaTS 2.5L
Old 02-02-2011, 03:09 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #20 (permalink)
Reply

Thread Tools
Rate This Thread
Rate This Thread:

 


All times are GMT -8. The time now is 07:58 AM.


 
Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2025, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2025 Pelican Parts, LLC - Posts may be archived for display on the Pelican Parts Website -    DMCA Registered Agent Contact Page
 

DTO Garage Plus vBulletin Plugins by Drive Thru Online, Inc.