water pipe as ground how much is needed

I got a bad leak on my 60+ year old pipe in from the meter
so want to replace the steel 3/4 inch now down to less then 1/2 line with a 1'' PVC line
how much steel line in the dirt makes a good ground of the electric service ?
I plan on leaving about 18 ft of steel as it is under a concrete slab
but not having a direct connection to the main water pipes as the PVC is not a conductor
do I need to run a wire to ground to the supply pipe or is the existing 18 ft sufficient
for grounding my house ?

Old 12-05-2017, 05:58 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #1 (permalink)
Platinum Member
 
dad911's Avatar
 
Join Date: Jul 2001
Location: Leave the gun. Take the cannoli.
Posts: 20,892
New home service has 2 grounds. a 20' rebar in the footing, and 2 ground rods (5' each?)

Water lines, water heaters, etc. should also be connected with bonding wire. Use something like this: https://www.homedepot.com/p/Blackburn-Bronze-Ground-Clamp-1-2-1-in-for-Direct-Burial-JD-B1-15/202907610

Can you re-run the 18' over head or in a wall instead? Concrete and steel don't get along, especially in southern florida.
__________________
Politics is in the eye of the beholder - Rodney Dangerfield
Old 12-05-2017, 06:28 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #2 (permalink)
Baz Baz is online now
G'day!
 
Baz's Avatar
 
Join Date: Sep 2008
Location: New Smyrna Beach, Florida
Posts: 45,417
Garage
Quote:
Originally Posted by nota View Post
I got a bad leak on my 60+ year old pipe in from the meter
so want to replace the steel 3/4 inch now down to less then 1/2 line with a 1'' PVC line
how much steel line in the dirt makes a good ground of the electric service ?
I plan on leaving about 18 ft of steel as it is under a concrete slab
but not having a direct connection to the main water pipes as the PVC is not a conductor
do I need to run a wire to ground to the supply pipe or is the existing 18 ft sufficient
for grounding my house ?
Traditional ground rods are about 8' long - and most homes use two of those - from what I have seen.

I'm no electrician so someone else can post more and better info, I'm sure...
__________________
Old dog....new tricks.....
Old 12-05-2017, 06:32 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #3 (permalink)
Registered
 
T77911S's Avatar
 
Join Date: Oct 2006
Location: MYR S.C.
Posts: 17,321
I would drop a ground rod where the power comes in and run another wire to it from the main panel. I doubt you have a disconnect outside. (new code). or run it to the meter base. have pwr company open it up for you.
__________________
86 930 94kmiles [__] RUNNING:[__] NOT RUNNING: ____77 911S widebody: SOLD
88 BMW 325is 200K+ SOLD
03 BMW 330CI 220K:: [__] RUNNING: [__] NOT RUNNING:
01 suburban 330K:: [__] RUNNING: [__] NOT RUNNING:
RACE CAR:: sold
Old 12-05-2017, 06:34 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #4 (permalink)
Banned
 
Join Date: Jan 2005
Location: cutler bay
Posts: 15,141
have ground on the panel to the steel water pipe
and another by the A/c outside and one for the att phone cable and internets
the last two are just bars driven into the dirt
the panel ground is a couple of feet inside the garage so connected to 20 ft of 3/4 pipe in the ground under a slab then new PVC pipe to the meter and main water lines

is the 20 ft of pipe enough for a good ground for the el panel ?
Old 12-05-2017, 09:18 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #5 (permalink)
canna change law physics
 
red-beard's Avatar
 
Join Date: Jul 2000
Location: Houston, Tejas
Posts: 43,366
Garage
A ground rod is $13 at Home Depot. Buy one and forget about the steel pipe.

https://www.homedepot.com/p/ERICO-5-8-in-x-8-ft-Copper-Ground-Rod-615880UPC/202195738
__________________
James
The pessimist complains about the wind; the optimist expects it to change; the engineer adjusts the sails.- William Arthur Ward (1921-1994)
Red-beard for President, 2020
Old 12-05-2017, 12:25 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #6 (permalink)
 
Banned
 
Join Date: Jan 2005
Location: cutler bay
Posts: 15,141
ODD THOUGHT

is the water in a nonconductive pipe a ground ?
Old 12-05-2017, 06:14 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #7 (permalink)
Registered
 
Join Date: Mar 2005
Location: Jersey Shore
Posts: 1,084
Garage
10' of water pipe in ground
two 8' ground rods, minimum 6' apart
20' of rebar in your footing
tie all the grounding together or you make the problem worse
use #6 wire
__________________
Chris
the more i learn, the less i know
Old 12-05-2017, 06:24 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #8 (permalink)
Brew Master
 
cabmandone's Avatar
 
Join Date: Jul 2013
Location: Delphos OH
Posts: 32,050
Garage
I have only one copper ground rod on my service. My outdoor disconnect and my main panel all tie to that single copper ground rod. I'd check code in your area and devise a plan from there. If you can use a ground rod, I'd run a copper ground wire out to it and call it a day.
Old 12-06-2017, 03:10 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #9 (permalink)
Kantry Member
 
oldE's Avatar
 
Join Date: Feb 2001
Location: N.S. Can
Posts: 6,770
Quote:
Originally Posted by nota View Post
ODD THOUGHT

is the water in a nonconductive pipe a ground ?

No.

Best
Les
__________________
Best
Les
My train of thought has been replaced by a bumper car.
Old 12-06-2017, 05:29 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #10 (permalink)
Platinum Member
 
dad911's Avatar
 
Join Date: Jul 2001
Location: Leave the gun. Take the cannoli.
Posts: 20,892
Quote:
Originally Posted by nota View Post
have ground on the panel to the steel water pipe
and another by the A/c outside and one for the att phone cable and internets
the last two are just bars driven into the dirt
the panel ground is a couple of feet inside the garage so connected to 20 ft of 3/4 pipe in the ground under a slab then new PVC pipe to the meter and main water lines

is the 20 ft of pipe enough for a good ground for the el panel ?
Yes, combined with the driven rods you have. Tie all of them together with #6 and the clamp I linked to before.
__________________
Politics is in the eye of the beholder - Rodney Dangerfield
Old 12-06-2017, 05:57 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #11 (permalink)
Make Bruins Great Again
 
Por_sha911's Avatar
 
Join Date: Dec 2003
Location: TN
Posts: 20,800
Garage
Wouldn't using water pipe cause a floating ground problem?
__________________
--------------------------------------
Joe
See Porsche run. Run, Porsche, Run: `87 911 Carrera
Old 12-06-2017, 06:47 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #12 (permalink)
Registered
 
GWN7's Avatar
 
Join Date: Jun 2002
Location: Winnipeg, MB, Canada
Posts: 3,963
Instead of leaving 18' of steel line under a concrete slab why not drill under the slab to replace the 1/2 blocked line that you are using now with a clean clear line? Lots of videos on YouTube on how to do this. At some point that galvanised pipe will block completely or rust thru. Why only do 1/2 the job and then have to redo it again in a couple years?

When I built a house in Ontario the regulations called for two ground rods 6' apart. If I was building on solid rock I could attach the ground wire to both ends of the rods and lay in a shallow trench with 6" of covering overtop. Basically 22' of ground wire buried with the rods attached. I built on sand and was able to drive both rods into the ground with a sledge hammer. Here all is required is the ground wire is attached to the supply side of the water meter line.

__________________
Bunch of old cars
Old 12-06-2017, 03:43 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #13 (permalink)
Reply


 


All times are GMT -8. The time now is 03:57 PM.


 
Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2025, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2025 Pelican Parts, LLC - Posts may be archived for display on the Pelican Parts Website -    DMCA Registered Agent Contact Page
 

DTO Garage Plus vBulletin Plugins by Drive Thru Online, Inc.