Generator size, is it possible to go too big (kw question)

I need a 3 phase, 480v generator to run a deep well pump. The the pump looks like it needs 15 kw ish peak...
So I'm looking at generators. Diesel type. Only thing remotely close to my price range is a 40kw unit.
So the question is; would it be safe to assume with less load the generator will run more efficient (less fuel) then say a smaller 25 kw unit? Also, I would hate to use this generator only to power a pump.

Thanks Guys

__________________
85 928S; LSx conversion, 5 speed with LSD.

IRR... What IRR!
Old 04-22-2018, 09:01 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #1 (permalink)
Registered
 
Join Date: Jun 2009
Location: St Paul MN
Posts: 3,145
Garage
Yes, but with a diesel youíll get glazing of the cylinders ( I think thatís the issue)if you donít run it hard on a regular basis. I only run the one at work when it has a load on it and every few years the service company brings out the load bank and runs it hard.
__________________
Rutager West

1977 911S Targa Chocolate Brown
Old 04-23-2018, 01:46 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #2 (permalink)
Information Overloader
 
Join Date: Mar 2003
Location: NW Lower Michigan
Posts: 17,700
If you run a Diesel engine under 60% of its capacity for prolonged periods you could experience wet stacking, which is unburned fuel leaking past the cylinders.

Short periods of wet stacking is not too damaging but repeatedly and for prolonged periods your maintenance costs will skyrocket.
Old 04-23-2018, 02:45 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #3 (permalink)
canna change law physics
 
red-beard's Avatar
 
Join Date: Jul 2000
Location: Houston, Tejas
Posts: 39,648
Garage
Standby generators regularly run in the 30% region. They are sized for in rush current.

Gen size = voltage * inrush current(s) * (100 - allowable voltage say in %).

Typical allowable voltage sag is 20-30% depending on the device.

In rush is 3-5 times the operating current, unless you use a soft starter or VFD.
__________________
James
The pessimist complains about the wind; the optimist expects it to change; the engineer adjusts the sails.- William Arthur Ward (1921-1994)
Red-beard for President, 2020
Old 04-23-2018, 02:54 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #4 (permalink)
canna change law physics
 
red-beard's Avatar
 
Join Date: Jul 2000
Location: Houston, Tejas
Posts: 39,648
Garage
Quote:
Originally Posted by Crowbob View Post
If you run a Diesel engine under 60% of its capacity for prolonged periods you could experience wet stacking, which is unburned fuel leaking past the cylinders.

Short periods of wet stacking is not too damaging but repeatedly and for prolonged periods your maintenance costs will skyrocket.
Most diesel engines do not run at 60% load.
__________________
James
The pessimist complains about the wind; the optimist expects it to change; the engineer adjusts the sails.- William Arthur Ward (1921-1994)
Red-beard for President, 2020
Old 04-23-2018, 02:55 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #5 (permalink)
canna change law physics
 
red-beard's Avatar
 
Join Date: Jul 2000
Location: Houston, Tejas
Posts: 39,648
Garage
Quote:
Originally Posted by AZ_porschekid View Post
I need a 3 phase, 480v generator to run a deep well pump. The the pump looks like it needs 15 kw ish peak...
So I'm looking at generators. Diesel type. Only thing remotely close to my price range is a 40kw unit.
So the question is; would it be safe to assume with less load the generator will run more efficient (less fuel) then say a smaller 25 kw unit? Also, I would hate to use this generator only to power a pump.

Thanks Guys
Is this backup power, or will it run the pump all the time?
__________________
James
The pessimist complains about the wind; the optimist expects it to change; the engineer adjusts the sails.- William Arthur Ward (1921-1994)
Red-beard for President, 2020
Old 04-23-2018, 02:57 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #6 (permalink)
 
....
 
Arizona_928's Avatar
 
Join Date: Feb 2008
Location: some ****hole
Posts: 8,028
Quote:
Originally Posted by red-beard View Post
Is this backup power, or will it run the pump all the time?
It will run the pump only, probably a total of 15 hrs a week.

I guess worst case I'll get wet stacking, and have to change the oil more often... Not bad.
__________________
85 928S; LSx conversion, 5 speed with LSD.

IRR... What IRR!

Last edited by Arizona_928; 04-23-2018 at 06:54 AM..
Old 04-23-2018, 06:50 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #7 (permalink)
Get off my lawn!
 
GH85Carrera's Avatar
 
Join Date: Nov 2007
Location: Oklahoma
Posts: 60,272
Garage
That must be one bad mama jama pump. Wow.

My pump is just a 220 1.5 HP pump but it only produces 18 GPM. Enough to water the yard, which is why I put in the well. 3 phase and 480 volt is a serious pump.
__________________
Glen
44 Year member of the Porsche Club of America
1985 911 Carrera; 2017 Macan
1986 El Camino with Fuel Injected 350 Crate Engine
My Motto: I will never be too old to have a happy childhood!
Old 04-23-2018, 09:55 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #8 (permalink)
3.4 Bigger is better
 
88-diamondblue's Avatar
 
Join Date: Nov 2003
Location: South Dakota
Posts: 1,484
What is the HP of the pump? A Lima Mac generator is good for starting 1HP WITH 1KW.
Other generators need to be over-sized to get the same motor starting. I do this everyday day with the ag market. A 40KW wouldn't break in properly. Once broken in it would be just fine. Most engines use fuel based on HP load which is 1.5HP to generate 1KW electricity. I have big engines with the same load a smaller one and use about the same amount of fuel
__________________
Michael

04 996 40th Anniversary
88 911 Diamond Blue CE Carrera 3.4 HC3.4 member
2016 Acura RDX

Last edited by 88-diamondblue; 04-23-2018 at 11:17 AM..
Old 04-23-2018, 11:12 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #9 (permalink)
canna change law physics
 
red-beard's Avatar
 
Join Date: Jul 2000
Location: Houston, Tejas
Posts: 39,648
Garage
Quote:
Originally Posted by 88-diamondblue View Post
What is the HP of the pump? A Lima Mac generator is good for starting 1HP WITH 1KW.
Other generators need to be over-sized to get the same motor starting. I do this everyday day with the ag market. A 40KW wouldn't break in properly. Once broken in it would be just fine. Most engines use fuel based on HP load which is 1.5HP to generate 1KW electricity. I have big engines with the same load a smaller one and use about the same amount of fuel
He said it is 3 phase, 480VAC 15kW, so a 20HP pump.
__________________
James
The pessimist complains about the wind; the optimist expects it to change; the engineer adjusts the sails.- William Arthur Ward (1921-1994)
Red-beard for President, 2020
Old 04-23-2018, 02:09 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #10 (permalink)
Actual Porsche owner
 
wdfifteen's Avatar
 
Join Date: Mar 2008
Location: SW Ohio
Posts: 23,351
Garage
Wet stacking comes from not running the engine up to operating temperature. You can run it at 40% capacity if you do it long enough to get it hot.
__________________
.
Old 04-23-2018, 05:49 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #11 (permalink)
....
 
Arizona_928's Avatar
 
Join Date: Feb 2008
Location: some ****hole
Posts: 8,028


Anyone make anything of this?
The unit produces 480v and assuming 3 phase (even my abb friends want to agree to 3 phase) deawoo engine that is practically new. Zero blow by at 220 hours.
__________________
85 928S; LSx conversion, 5 speed with LSD.

IRR... What IRR!

Last edited by Arizona_928; 04-23-2018 at 05:54 PM..
Old 04-23-2018, 05:50 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #12 (permalink)
 
....
 
Arizona_928's Avatar
 
Join Date: Feb 2008
Location: some ****hole
Posts: 8,028



Here's the one from the engine
__________________
85 928S; LSx conversion, 5 speed with LSD.

IRR... What IRR!
Old 04-23-2018, 05:53 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #13 (permalink)
canna change law physics
 
red-beard's Avatar
 
Join Date: Jul 2000
Location: Houston, Tejas
Posts: 39,648
Garage
The 40kW generator will work fine, assuming you're running all the time. You might be able to go smaller if you install a soft starter on the water pump motor. That generator is only 32kW PRIME, so it might have a soft starter already.
__________________
James
The pessimist complains about the wind; the optimist expects it to change; the engineer adjusts the sails.- William Arthur Ward (1921-1994)
Red-beard for President, 2020
Old 04-23-2018, 06:04 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #14 (permalink)
....
 
Arizona_928's Avatar
 
Join Date: Feb 2008
Location: some ****hole
Posts: 8,028
well that one is bought and paid for. the seller claimed it was a 40kw.... so 32kw and a soft start and everything will work. I hope! it was only a few grand so nothing too much was invested.
Its starting system is interesting. it has one of these.
__________________
85 928S; LSx conversion, 5 speed with LSD.

IRR... What IRR!

Last edited by Arizona_928; 04-23-2018 at 08:08 PM..
Old 04-23-2018, 08:02 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #15 (permalink)
OFF THE BOOST PIPE NOW...
 
A930Rocket's Avatar
 
Join Date: Oct 2003
Location: Mount Pleasant, South Carolina
Posts: 8,302
I didnít know Lucas made generators!
Old 04-24-2018, 12:23 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #16 (permalink)
Registered User
 
T77911S's Avatar
 
Join Date: Oct 2006
Location: MYR S.C.
Posts: 13,586
we have a 100kw on the radar site here at work. the site only loads it down about 20% so the load bank comes on and loads it down to about 60%, about another 40kw.

__________________
86 930 42kmiles [__] RUNNING:[__] NOT RUNNING: ____77 911S widebody: SOLD
88 BMW 325is 200K+ SOLD
05 BMW 330CI 130K:: [__] RUNNING: [__] NOT RUNNING:
08 VOLVO V70 190K:: [__] RUNNING: [__] NOT RUNNING:
90 B2200[__] RUNNING:[] NOT RUNNING:__2000 MER E320 WAGON [] WRECKED:[]RUNNING:
Old 04-24-2018, 03:47 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #17 (permalink)
Reply

Thread Tools
Rate This Thread
Rate This Thread:

 


All times are GMT -8. The time now is 03:19 AM.


 
Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2020, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2020 Pelican Parts, LLC - Posts may be archived for display on the Pelican Parts Website -    DMCA Registered Agent Contact Page
 

DTO Garage Plus vBulletin Plugins by Drive Thru Online, Inc.