Generator size, is it possible to go too big (kw question)
I need a 3 phase, 480v generator to run a deep well pump. The the pump looks like it needs 15 kw ish peak...
So I'm looking at generators. Diesel type. Only thing remotely close to my price range is a 40kw unit. So the question is; would it be safe to assume with less load the generator will run more efficient (less fuel) then say a smaller 25 kw unit? Also, I would hate to use this generator only to power a pump. Thanks Guys
dolor et pavor Copyright |
Yes, but with a diesel you’ll get glazing of the cylinders ( I think that’s the issue)if you don’t run it hard on a regular basis. I only run the one at work when it has a load on it and every few years the service company brings out the load bank and runs it hard.
Rutager West 1977 911S Targa Chocolate Brown |
Information Overloader
If you run a Diesel engine under 60% of its capacity for prolonged periods you could experience wet stacking, which is unburned fuel leaking past the cylinders.
Short periods of wet stacking is not too damaging but repeatedly and for prolonged periods your maintenance costs will skyrocket. |
canna change law physics
Standby generators regularly run in the 30% region. They are sized for in rush current.
Gen size = voltage * inrush current(s) * (100 - allowable voltage say in %). Typical allowable voltage sag is 20-30% depending on the device. In rush is 3-5 times the operating current, unless you use a soft starter or VFD.
James The pessimist complains about the wind; the optimist expects it to change; the engineer adjusts the sails.- William Arthur Ward (1921-1994) Red-beard for President, 2020 |
It will run the pump only, probably a total of 15 hrs a week.
I guess worst case I'll get wet stacking, and have to change the oil more often... Not bad.
dolor et pavor Copyright Last edited by Arizona_928; 04-23-2018 at 07:54 AM.. |
That must be one bad mama jama pump. Wow.
My pump is just a 220 1.5 HP pump but it only produces 18 GPM. Enough to water the yard, which is why I put in the well. 3 phase and 480 volt is a serious pump.
Glen 49 Year member of the Porsche Club of America 1985 911 Carrera; 2017 Macan 1986 El Camino with Fuel Injected 350 Crate Engine My Motto: I will never be too old to have a happy childhood! |
3.4 Bigger is better
What is the HP of the pump? A Lima Mac generator is good for starting 1HP WITH 1KW.
Other generators need to be over-sized to get the same motor starting. I do this everyday day with the ag market. A 40KW wouldn't break in properly. Once broken in it would be just fine. Most engines use fuel based on HP load which is 1.5HP to generate 1KW electricity. I have big engines with the same load a smaller one and use about the same amount of fuel
Michael 88 911 Diamond Blue CE Carrera 3.4 HC3.4 member 2020 Honda Passport Last edited by 88-diamondblue; 04-23-2018 at 12:17 PM.. |
Wet stacking comes from not running the engine up to operating temperature. You can run it at 40% capacity if you do it long enough to get it hot.
![]() Anyone make anything of this? The unit produces 480v and assuming 3 phase (even my abb friends want to agree to 3 phase) deawoo engine that is practically new. Zero blow by at 220 hours.
dolor et pavor Copyright Last edited by Arizona_928; 04-23-2018 at 06:54 PM.. |
![]() Here's the one from the engine
The 40kW generator will work fine, assuming you're running all the time. You might be able to go smaller if you install a soft starter on the water pump motor. That generator is only 32kW PRIME, so it might have a soft starter already.
well that one is bought and paid for. the seller claimed it was a 40kw.... so 32kw and a soft start and everything will work. I hope! it was only a few grand so nothing too much was invested.
Its starting system is interesting. it has one of these.
dolor et pavor Copyright Last edited by Arizona_928; 04-23-2018 at 09:08 PM.. |
I didn’t know Lucas made generators!
we have a 100kw on the radar site here at work. the site only loads it down about 20% so the load bank comes on and loads it down to about 60%, about another 40kw.
