No water in either panel? Is this a single rental or are there other units on the main service.

__________________
Don
1988 Targa

Last edited by Red88Carrera; 12-07-2011 at 06:27 PM..
Old 12-07-2011, 06:24 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #21 (permalink)
Registered
 
nostatic's Avatar
 
Join Date: Sep 2001
Location: SoCal
Posts: 30,318
Garage
I don't see any (water or critters/droppings). The main is on an exterior wall, the secondary is in the garage.

Good idea on throwing the breakers. I'll wait until Shirley gets home so she can tell me which ones are going out. Not that I don't trust the labeling
Old 12-07-2011, 06:27 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #22 (permalink)
You do not have permissi
 
john70t's Avatar
 
Join Date: Aug 2001
Location: midwest
Posts: 40,502
Just an idea- I thought the grounds are attached to water pipes inside and/or copper rods in the ground outside.
__________________
Meanwhile other things are still happening.
Old 12-07-2011, 06:29 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #23 (permalink)
Registered
 
Join Date: Mar 2005
Location: Jersey Shore
Posts: 1,084
Garage
sounds like you are losing a leg (feeder). if it was the neut then the whole house would flicker and from your description it sounds like multiple circuits. in my mind what is happening is that whatever you are doing is creating heat which opens the connection, the power ceases to flow and you are left without power until the connection cools and resumes contact. i have a feeling that when this is found, it will be quite evident. good luck.
__________________
Chris
the more i learn, the less i know
Old 12-07-2011, 06:32 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #24 (permalink)
Un-Registered User
 
Join Date: Apr 2007
Location: Upstate New York
Posts: 902
Quote:
Originally Posted by carambola View Post
sounds like you are losing a leg (feeder). if it was the neut then the whole house would flicker and from your description it sounds like multiple circuits.
If all the bad devices are on the sub panel it could be a bad neutral. Either way, it's a loose/bad connection.
__________________
Don
1988 Targa

Last edited by Red88Carrera; 12-07-2011 at 06:37 PM..
Old 12-07-2011, 06:35 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #25 (permalink)
Registered
 
nostatic's Avatar
 
Join Date: Sep 2001
Location: SoCal
Posts: 30,318
Garage
Quote:
Originally Posted by carambola View Post
sounds like you are losing a leg (feeder). if it was the neut then the whole house would flicker and from your description it sounds like multiple circuits. in my mind what is happening is that whatever you are doing is creating heat which opens the connection, the power ceases to flow and you are left without power until the connection cools and resumes contact. i have a feeling that when this is found, it will be quite evident. good luck.
The shutting off for hours is new - previously it was just flickering and power cycling (not being off for more than a second, but enough to cycle the cable box, router, etc). Last night was the first time that thing went off and stayed off. Yeah, I know, a bad sign.

There are a small number of outlets that don't seem to be affected, but there have been some times where every light in the house has flickered (though not completely power cycled).

So this likely is an issue at the box rather than in the walls/ceiling? It affects so many of the outlets/lights I'm assuming it would have to be at a somewhat central location.
Old 12-07-2011, 06:41 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #26 (permalink)
 
Registered
 
Join Date: Mar 2005
Location: Jersey Shore
Posts: 1,084
Garage
If you really want to get into this we can. first what you need to do is figure out what circuit(s) the problem is occurring on. as in which individual breakers and which panel. if you are talking more than one circuit it would go back to the panel, if it is from both panels then you are talking either the fire switch (main breaker outside) or even the utility. if you are have problems with only one circuit then it is definitely possible that it could be happening in the walls, the more widespead the problem the less chance of that.
__________________
Chris
the more i learn, the less i know
Old 12-07-2011, 06:49 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #27 (permalink)
Registered
 
nostatic's Avatar
 
Join Date: Sep 2001
Location: SoCal
Posts: 30,318
Garage
It is more than one breaker - that much I know. And if I believe the labels it is on both the main and sub. But I don't know that I believe the labels. I'm home alone at the moment so I can't do the experiment of throwing a breaker and seeing what goes out. Sounds like it is at the panel though.
Old 12-07-2011, 06:53 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #28 (permalink)
Registered
 
peppy's Avatar
 
Join Date: Aug 2007
Location: Kenbridge VA
Posts: 4,318
plug a radio in and turn it up so you can hear it cut off.
__________________
Peppy
2011 BMW 335d
1988 Targa 3.4
2001 Jetta TDI dead
1982 Chevette Diesel SOLD
Old 12-07-2011, 06:56 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #29 (permalink)
UnRegistered User
 
billybek's Avatar
 
Join Date: Dec 2007
Location: Calgary
Posts: 8,091
Garage
Aluminum wire?
Can be trouble if not maintained or the wrong breakers/switches/fixtures used with it.
__________________
Bill K.
"I started out with nothin and I still got most of it left...."
83 911 SC Guards Red (now gone)
And I sold a bunch of parts I hadn't installed yet.
Old 12-07-2011, 07:01 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #30 (permalink)
Registered
 
wdfifteen's Avatar
 
Join Date: Mar 2008
Location: SW Ohio
Posts: 29,826
Garage
Quote:
Originally Posted by nostatic View Post
The landlord said there was never a problem before and that my music stuff must be the cause. I have very little gear in there and it is low current draw stuff (class D amp, etc). Plus if it was drawing too much it should trip a breaker which has never happened. Almost all of the built-in lights flicker and power cycle so seems there is something systemic wrong. The wiring at the new breaker box looks like crap.

Thoughts?
Landlord is giving you total BS. The only thing your equipment can do is overload the circuit, and if it does that the breaker will trip. What you are describing is bad connections in the system and they can lead to fires. This is serious and it isn't your fault. I know you are a responsible, can-do guy, but as a renter it isn't your responsibility to diagnose it or correct it.
__________________
.
Old 12-07-2011, 07:06 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #31 (permalink)
Registered
 
Join Date: Mar 2005
Location: Jersey Shore
Posts: 1,084
Garage
i have to hit the sack but if the problem does happen tonight listen, with the cover closed, for any popping or snapping sounds. my first place to listen would be at the main panel especially since the meter is right next to it. you have four connections that i am suspecting without more information. the main breaker connections ( not visible in your photos) the line and load of the meter socket and the taps (where the utility meets the housing wires. don't go moving wires in the box as it could make the problem worse. i'll check in the morning.
__________________
Chris
the more i learn, the less i know
Old 12-07-2011, 07:08 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #32 (permalink)
 
Registered
 
nostatic's Avatar
 
Join Date: Sep 2001
Location: SoCal
Posts: 30,318
Garage
She (the landlord) is just clueless. I knew that moving in though. Since her electrician didn't show and hasn't called I'll give until noon tomorrow at which point I'll call a guy that one of my work colleagues uses who knows his stuff. And whatever he charges to take a look will be deducted from next month's rent, and then I'll tell her that either her guy fixes it immediately or I'll pay my guy and deduct that from the rent as well. That's what I had to do to get the garage door fixed.

Always something...
Old 12-07-2011, 07:11 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #33 (permalink)
Registered
 
nostatic's Avatar
 
Join Date: Sep 2001
Location: SoCal
Posts: 30,318
Garage
Quote:
Originally Posted by carambola View Post
i have to hit the sack but if the problem does happen tonight listen, with the cover closed, for any popping or snapping sounds. my first place to listen would be at the main panel especially since the meter is right next to it. you have four connections that i am suspecting without more information. the main breaker connections ( not visible in your photos) the line and load of the meter socket and the taps (where the utility meets the housing wires. don't go moving wires in the box as it could make the problem worse. i'll check in the morning.
Funny you mention popping. I have a rack mounted power conditioner (that shows line voltage) in the music room. The other night when it was acting up I turned it off and then turned it back on. It's power indicator light flickered and popped/crackled on and off. I unplugged it from the wall.
Old 12-07-2011, 07:13 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #34 (permalink)
Banned
 
Join Date: May 2005
Location: Earth
Posts: 31,744
Could this have anything to do with the high winds last week. You're in Santa Monica, right?
I think several thousand people in LA are still without power.

Maybe it's Edison and the grid, not your house specifically. Has it been going on for more than 6 or 7 days. That was when the winds screwed a lot of thing up.
Old 12-07-2011, 07:25 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #35 (permalink)
Registered
 
Zeke's Avatar
 
Join Date: Jan 2002
Location: Long Beach CA, the sewer by the sea.
Posts: 38,261
Red88Carrera has had this nailed all along. In his panel it's the center lug with the 3 large wires coming down. The service cables are almost always AL and get loose. Now, Todd, I know you're not going to grab your 3/8ths Allen wrench and bear down on that sucker, but that's all it takes. Make sure when your guy shows up that you video him putting a turn on that. Give his bill to the landlord, don't deduct. He can collect if he has to, but the video should take care of it.

Do the feeds in the sub panel too.

BTW, a power company guy told me (in another state where I was working) to tighten down the lugs after 30 days on a new service.

Yeah, right, Bubba. There is no disconnect in front of the meter and you have to pull the meter to disconnect the load side. Not me.
Old 12-07-2011, 07:33 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #36 (permalink)
Registered
 
Join Date: Feb 2004
Location: Western NY
Posts: 4,311
As others said don't do anything on a live circuit, it can KILL you, unless you know what you are doing

Dollars to donuts a bad connection on one leg of the feed line, or a bad main breaker, if it was the neutral it would effect all circuits (except 220v). It could be at the meter, main disconnect or at the main breaker in the panel.

One sure way to tell is if the effected circuits are served by every OTHER breaker.

One word of caution, don't just check the tightness, as the screws can seize and appear tight, LOOSEN first, then re-tighten to be sure.
__________________
Richard 2010 F800GS '04 R11BXA, '01 F650GS, '98 CBR600F3 track bike, '75 RE-5, '76 RE-5, '81 GS400E.
Also residing in the barn my son's bikes:
'89 GS500ES, Ducati Monster 620 dark
Old 12-07-2011, 07:53 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #37 (permalink)
Senior Member
 
Superman's Avatar
 
Join Date: Mar 2000
Location: Lacey, WA. USA
Posts: 25,312
Quote:
Originally Posted by Red88Carrera View Post
Can't tell much from the photos because we can't see the main connections. I'd like to meet the guy that did that work. He shouldn't have a license, or probably doesn't have one. This is a pic of the panel I installed when I built my house. You don't have to touch anything to see where the wires run.
Sounds like some people here know their stuff, much more than I do. I'm not an electrician and I didn't sleep at a Holiday Inn last night, but this ^^^ is an outstanding installation. Anyone with sense will smile on workmanship like above. The electrical inspectors I have worked with would usually not fail an installation that looks ugly, but they can. And sometimes they do.

Nostatic is not going to be giving any boxes the haircuts they need, but he could just make sure the connections are tight. A good electrical connection is all about having a 'tight,' airless connection. To get that, you compress metal onto metal. Just see if those big screw connections are tight. Aluminum wiring is notorious for shrinking and becoming loose. The big multi-strand stuff like incoming power should be coated with that anti-oxidant stuff and screwed TIGHT.

Then again, I didn't sleep at a Holiday Inn last night.
__________________
Man of Carbon Fiber (stronger than steel)

Mocha 1978 911SC. "Coco"
Old 12-07-2011, 10:09 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #38 (permalink)
1966 - 912 - SOLD
 
lane912's Avatar
 
Join Date: May 2008
Location: oak grove, OREGON
Posts: 3,193
Quote:
Originally Posted by Red88Carrera View Post
Can't tell much from the photos because we can't see the main connections. I'd like to meet the guy that did that work. He shouldn't have a license, or probably doesn't have one. This is a pic of the panel I installed when I built my house. You don't have to touch anything to see where the wires run.
NEC 110.12-----

all work shall be done in a neat and workman like manner---


this is what they are talking about----
__________________
i was too tired to be pretty last night!
Old 12-08-2011, 05:33 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #39 (permalink)
Senior Member
 
Join Date: Jun 2000
Location: N. Phoenix AZ USA
Posts: 28,977
Quote:
Originally Posted by Red88Carrera View Post
Can't tell much from the photos because we can't see the main connections. I'd like to meet the guy that did that work. He shouldn't have a license, or probably doesn't have one. This is a pic of the panel I installed when I built my house. You don't have to touch anything to see where the wires run.
Mine looks about like the above photo. Do not like the "mix and match" of wiring in your main box and truthfully would wonder if the person who wired this really had a license or not.

This needs to be fixed and now. My first gut feeling was also the neutral side...

__________________
2021 Subaru Legacy, 2002 Dodge Ram 2500 Cummins (the workhorse), 1992 Jaguar XJ S-3 V-12 VDP (one of only 100 examples made), 1969 Jaguar XJ (been in the family since new), 1985 911 Targa backdated to 1973 RS specs with a 3.6 shoehorned in the back, 1959 Austin Healey Sprite (former SCCA H-Prod), 1995 BMW R1100RSL, 1971 & '72 BMW R75/5 "Toaster," Ural Tourist w/sidecar, 1949 Aeronca Sedan / QB
Old 12-08-2011, 06:11 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #40 (permalink)
Reply


 


All times are GMT -8. The time now is 03:23 AM.


 
Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2026, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2025 Pelican Parts, LLC - Posts may be archived for display on the Pelican Parts Website -    DMCA Registered Agent Contact Page
 

DTO Garage Plus vBulletin Plugins by Drive Thru Online, Inc.