Two Circuits Sharing Ground Circuit

Electricians -

I have a receptacle circuit in one room that is not grounded (because it is powered by an old lighting circuit - weirdness of 100 y/o house). I've put a GFCI receptacle in first position on that circuit, to get some protection.

When I add receptacles to the adjacent room, I'll be able to pull a ground wire from the adjacent room circuit to serve as the ground for this currently ungrounded circuit. I read NEC, it seems to permit two circuits to share the same ground conductor, if the circuits originate in the same enclosure, which these do.

So . . . sound ok?

__________________
1989 3.2 Carrera coupe; 1988 Westy Vanagon, Zetec; 1986 E28 M30; 1994 W124; 2004 S211
What? Uh . . . “he” and “him”?
Old 03-19-2025, 08:43 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #1 (permalink)
Location: Galt's Gulch
 
Join Date: Jul 2019
Posts: 4,890
When it comes to spark-tricity I'm no help at all, but what I can do is share this






PS seems to me if you install a combo GFCI/AFCI outlet, you would have all the bases covered.
With a grain of salt.
Old 03-19-2025, 10:59 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #2 (permalink)
jyl jyl is online now
Registered
 
jyl's Avatar
 
Join Date: Jan 2002
Location: Nor California & Pac NW
Posts: 24,536
Garage
Is it better to do GFCI/AFCI protection at the breaker or at the receptacle?
__________________
1989 3.2 Carrera coupe; 1988 Westy Vanagon, Zetec; 1986 E28 M30; 1994 W124; 2004 S211
What? Uh . . . “he” and “him”?

Last edited by jyl; 03-19-2025 at 11:35 AM..
Old 03-19-2025, 11:28 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #3 (permalink)
Location: Galt's Gulch
 
Join Date: Jul 2019
Posts: 4,890
A little voice is telling me that I've already over-commented on this subject because of my limited expert-tease.
But what does he know.
Old 03-19-2025, 11:38 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #4 (permalink)
Back in the saddle again
 
masraum's Avatar
 
Join Date: Oct 2001
Location: Central TX west of Houston
Posts: 55,844
Quote:
Originally Posted by jyl View Post
Is it better to do GFCI/AFCI protection at the breaker or at the receptacle?
I'm not an electrician, and I am not a code expert.

I believe new/current code is that the protection should be at the breaker.

I assume that for practical purposes (protection of humans) as long as the GFCI works, it shouldn't matter which position it's in.

I don't know about the code-iness of having one ground for 2 circuits. It seems like it should work, and certainly be better than no ground.

I'm sure none of that really helps, but I'll be watching to see what the expert consensus is once it arrives.
__________________
Steve
'08 Boxster RS60 Spyder #0099/1960
- never named a car before, but this is Charlotte.
'88 targa SOLD 2004 - gone but not forgotten

Last edited by masraum; 03-19-2025 at 11:51 AM..
Old 03-19-2025, 11:47 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #5 (permalink)
Registered
 
Join Date: Oct 2012
Posts: 9,712
Garage
Quote:
Originally Posted by jyl View Post
Electricians -

I have a receptacle circuit in one room that is not grounded (because it is powered by an old lighting circuit - weirdness of 100 y/o house). I've put a GFCI receptacle in first position on that circuit, to get some protection.

When I add receptacles to the adjacent room, I'll be able to pull a ground wire from the adjacent room circuit to serve as the ground for this currently ungrounded circuit. I read NEC, it seems to permit two circuits to share the same ground conductor, if the circuits originate in the same enclosure, which these do.

So . . . sound ok?
Sounds fine to me from a technical perspective; can't comment on code in your area. In my area, depends where the circuit is. GFCI is only "required" in the kitchen/bathrooms for us and in the kitchen, EVERY outlet has to be GFCI (stupid).
__________________
Guy
'87 944 (first porsche/project car)
Old 03-19-2025, 11:56 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #6 (permalink)
 
Home of the Whopper
 
Join Date: Mar 2001
Location: Rocky Top, TN
Posts: 6,778
Garage
GFI's are touchy.
Definitely no shared neutrals.
Shared ground should be no big deal.
__________________
1968 912 coupe
1971 911E Targa rustbucket
1972 914 1.7
1987 924S
Old 03-19-2025, 12:35 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #7 (permalink)
Registered
 
Join Date: Jun 2003
Location: Fresno, CA
Posts: 7,768
I am not an electrician, but I would think that sharing a ground would be ok. In a normal, modern electrical box, all of the circuits use the same ground bar.

I too have an old house that I just acquired. I have noticed that many of my electrical receptacles have a separate ground wire that is attached to a plumbing pipe. This is where the original wiring is knob and tube with no separate ground. I will slowly replace a lot of the wiring with romex as I have access to the main floor electrical from the basement and so this project won't be too difficult. The upstairs will be another issue.
Old 03-19-2025, 01:26 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #8 (permalink)
Moderator
 
Bill Verburg's Avatar
 
Join Date: Dec 2000
Posts: 26,395
Garage
All the grounds both white and bare are connected at the breaker box, the connection is the central strip between the 2 hot sides and bonded to the box and a rod in the ground

all the hots, black or red, are connected on one side or the other of the braker box
__________________
Bill Verburg
'76 Carrera 3.6RS(nee C3/hotrod), '95 993RS/CS(clone)
| Pelican Home |Rennlist Wheels |Rennlist Brakes |
Old 03-19-2025, 01:52 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #9 (permalink)
Banned
 
Join Date: Feb 2008
Posts: 18,646
Quote:
Originally Posted by gacook View Post
Sounds fine to me from a technical perspective; can't comment on code in your area. In my area, depends where the circuit is. GFCI is only "required" in the kitchen/bathrooms for us and in the kitchen, EVERY outlet has to be GFCI (stupid).
I concur.

Also the breaker box and therefore all circuits share the same ground bar.
Old 03-19-2025, 02:27 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #10 (permalink)
jyl jyl is online now
Registered
 
jyl's Avatar
 
Join Date: Jan 2002
Location: Nor California & Pac NW
Posts: 24,536
Garage
Quote:
Originally Posted by Tidybuoy View Post
I am not an electrician, but I would think that sharing a ground would be ok. In a normal, modern electrical box, all of the circuits use the same ground bar.

I too have an old house that I just acquired. I have noticed that many of my electrical receptacles have a separate ground wire that is attached to a plumbing pipe. This is where the original wiring is knob and tube with no separate ground. I will slowly replace a lot of the wiring with romex as I have access to the main floor electrical from the basement and so this project won't be too difficult. The upstairs will be another issue.
Upstairs, running NM cable under the baseboards and receptacle boxes mounted behind openings in the baseboards makes it easy to wire outlets around a room - you just have to find one central place where you can run a bunch of NM cable up from basement to second floor - like a stairwell or something - and then from that central place run one cable to the nearest corner of each upstairs room. If baseboards are too small, well tall baseboards look better anyway. Don't go fishing cable through walls, any more than you have to. Abandon the old wiring in the walls. Get all new NM cable and all tied to the panel ground.
__________________
1989 3.2 Carrera coupe; 1988 Westy Vanagon, Zetec; 1986 E28 M30; 1994 W124; 2004 S211
What? Uh . . . “he” and “him”?

Last edited by jyl; 03-19-2025 at 03:22 PM..
Old 03-19-2025, 03:18 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #11 (permalink)
jyl jyl is online now
Registered
 
jyl's Avatar
 
Join Date: Jan 2002
Location: Nor California & Pac NW
Posts: 24,536
Garage
Man, GFCI breakers are expensive. CAFCI/GFCI breakers are really expensive. $50-100 a pop. That's like $2,000 just in breakers!
__________________
1989 3.2 Carrera coupe; 1988 Westy Vanagon, Zetec; 1986 E28 M30; 1994 W124; 2004 S211
What? Uh . . . “he” and “him”?
Old 03-19-2025, 03:20 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #12 (permalink)
Registered
 
Join Date: Mar 2004
Location: Los Angeles
Posts: 17,337
Around here, AFCI breakers will break the piggy bank. I cheat on my rentals. We install AFCI required for breakers throughout house but the kitchen. Just about all are GFCII there. AFter final inspection, out the AFCI and back in with the cheap typical breakers just like all houses had for the past 80 years. Yep, we create solutions to problems we do not have.
Old 03-19-2025, 05:48 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #13 (permalink)
Registered
 
Join Date: Mar 2004
Location: Los Angeles
Posts: 17,337
I don't know about code up there but it is OK here technically. GFI wouldn't work without a ground. It will trip
Old 03-19-2025, 05:50 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #14 (permalink)
Registered
 
Join Date: Oct 2000
Location: Nearby
Posts: 79,768
Garage
Send a message via AIM to fintstone
Quote:
Originally Posted by jyl View Post
Electricians -

I have a receptacle circuit in one room that is not grounded (because it is powered by an old lighting circuit - weirdness of 100 y/o house). I've put a GFCI receptacle in first position on that circuit, to get some protection.

When I add receptacles to the adjacent room, I'll be able to pull a ground wire from the adjacent room circuit to serve as the ground for this currently ungrounded circuit. I read NEC, it seems to permit two circuits to share the same ground conductor, if the circuits originate in the same enclosure, which these do.

So . . . sound ok?
I would say that as long as both receptacles are the same 15A (not one 15 and one 25), you are ok, but if I were pulling a ground from the adjoining room, I would just pull the power from there as well while I was pulling wires (and disconnect it form the light), keeping outlets on the outlet circuits and lights on a lighting circuit. Then you can use the single GFCI to protect both circuits.
__________________
74 Targa 3.0, 89 Carrera, 04 Cayenne Turbo
http://www.pelicanparts.com/gallery/fintstone/
"The problem with socialism is that you eventually run out of other people's money"
Some are born free. Some have freedom thrust upon them. Others simply surrender
Old 03-20-2025, 07:09 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #15 (permalink)
Registered
 
Rapewta's Avatar
 
Join Date: May 2011
Posts: 926
Your house shares the same ground throughout. It is not considered a current carrying conductor. The only time it does is during a momentary short. Hopefully the shorted breaker trips open.
The GFCI has to have the dedicated neutral (white) for it to work correctly.
Get on line and order the "Ugly"s" electrical references booklet. It is perfect for homeowners that want to safely do some simple electrical troubleshooting around the house. Keeps you out of trouble.
It is a small pocket book size.
__________________
67 396 corvette coupe. Sold
66 351 AC Cobra kit. Sold
99 996 man coupe
2001 911 Turbo man coupe
Old 03-20-2025, 09:07 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #16 (permalink)
jyl jyl is online now
Registered
 
jyl's Avatar
 
Join Date: Jan 2002
Location: Nor California & Pac NW
Posts: 24,536
Garage
Quote:
Originally Posted by fintstone View Post
I would say that as long as both receptacles are the same 15A (not one 15 and one 25), you are ok, but if I were pulling a ground from the adjoining room, I would just pull the power from there as well while I was pulling wires (and disconnect it form the light), keeping outlets on the outlet circuits and lights on a lighting circuit. Then you can use the single GFCI to protect both circuits.
That makes sense!
__________________
1989 3.2 Carrera coupe; 1988 Westy Vanagon, Zetec; 1986 E28 M30; 1994 W124; 2004 S211
What? Uh . . . “he” and “him”?
Old 03-20-2025, 02:44 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #17 (permalink)
Registered
 
Join Date: Jun 2010
Location: beaux arts, wa
Posts: 1,312
Garage
I also have an old house with many two prong outlets. Solution when replacing those nasty outlets was a gfi at the first outlet in each room, this protects all the downstream outlets and code says all the 3 prong but groundless outlets need a sticker saying no ground but gfi.

In your case if I understand correctly you’ll be adding a ground wire to the gfi outlet, which I think means that one outlet can now live without the sticker.

I’ve read homeowners books about code and I’d put the ground on that gfi but I’d also like to know the answer from an actual expert. There’s some deep knowledge that went into the code and I love learning the whys.
Old 03-20-2025, 03:31 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #18 (permalink)
 
jyl jyl is online now
Registered
 
jyl's Avatar
 
Join Date: Jan 2002
Location: Nor California & Pac NW
Posts: 24,536
Garage
Quote:
Originally Posted by zakthor View Post
I also have an old house with many two prong outlets. Solution when replacing those nasty outlets was a gfi at the first outlet in each room, this protects all the downstream outlets and code says all the 3 prong but groundless outlets need a sticker saying no ground but gfi.

In your case if I understand correctly you’ll be adding a ground wire to the gfi outlet, which I think means that one outlet can now live without the sticker.

I’ve read homeowners books about code and I’d put the ground on that gfi but I’d also like to know the answer from an actual expert. There’s some deep knowledge that went into the code and I love learning the whys.
Currently the room is like yours: no ground, GFCI in first position. Eventually I’ll ground the first receptacle, and all the subsequent receptacles have ground wires connected to the first.

Or, I’ll power and ground that room’s receptacles from the adjoining room.

Here is a table of the different circuit conditions and their risks.

__________________
1989 3.2 Carrera coupe; 1988 Westy Vanagon, Zetec; 1986 E28 M30; 1994 W124; 2004 S211
What? Uh . . . “he” and “him”?
Old 03-20-2025, 04:42 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #19 (permalink)
Registered
 
CurtEgerer's Avatar
Quote:
Originally Posted by jyl View Post
Man, GFCI breakers are expensive. CAFCI/GFCI breakers are really expensive. $50-100 a pop. That's like $2,000 just in breakers!
My brother has been making a small fortune for a few years re-selling new-in-the-box breakers on eBay he sources from Habitat, etc. The mains and obsolete stuff really bring crazy $$.

__________________
1983 AUDI Turbo Ur quattro
1987 PORSCHE 944 turbo
Old 03-21-2025, 04:20 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #20 (permalink)
Reply


 


All times are GMT -8. The time now is 12:55 AM.


 
Powered by vBulletin® Version 3.8.7
Copyright ©2000 - 2025, vBulletin Solutions, Inc.
Search Engine Optimization by vBSEO 3.6.0
Copyright 2025 Pelican Parts, LLC - Posts may be archived for display on the Pelican Parts Website -    DMCA Registered Agent Contact Page
 

DTO Garage Plus vBulletin Plugins by Drive Thru Online, Inc.