clothes dryer vent rant !

I just finished pulling out the dryer and cleaning out the vent, I have to do this about twice a year. If I don't do this the " smart " dryer won't turn on. What a piece of $hit a dryer vent setup is In my case the gas pipe come up through the floor right where the vent should go ! So instead the flex vent ( more garbage ! ) has to take a right turn THEN make another turn to go through the floor. Now I'm in the basement looking up at the flex vent coming through the floor. It then takes another right angle and runs about 25 feet, then takes another right angle down THEN another right angle to horizontal where it runs for three feet and TAKES ANOTHER right angle out through the masonary wall to the outside. You have got to be kidding me this is the best the builder could come up with !!! Could have run the vent out the front and saved 20 foot of run and a crap load of turns ! I know I have to run it out the front but just haven't done it yet. And of course the space where the washer/dryer reside was designed in the mid 80's when apparently appliances were smaller. So not much wiggle room to pull them out. So how often do you have to clean the vent ? My wife cleans the internal filter in the front of the machine weekly and runs a vacumn cleaner hose down there weekly. Not sure how much more we can do ? Thanks for letting me vent

__________________
2002 Boxster S . Arctic silver + black top/int. Jake Raby 3.6 SS engine " the beast ". GT3 front bumper, GT3 side skirts and GT3 TEK rear diffuser. 1999 996 C4 coupe black/grey with FSI 3.8 engine . Rear diffuser , front spoiler lip with ducktail spoiler .
Old 12-06-2014, 07:15 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #1 (permalink)
Registered
 
Join Date: Feb 2000
Location: Dallas, TX
Posts: 4,612
Similar setup but ours goes to the roof. About once every 6 weeks, I have to go into the attic, disconnect the vent to the outside and clean the lint off the screen that prevents animals from coming in the house. Total pain in the ass too!
__________________
Neil
'73 911S targa
Old 12-06-2014, 07:21 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #2 (permalink)
Bill is Dead.
 
cashflyer's Avatar
 
Join Date: Jul 2005
Location: Alaska.
Posts: 9,633
You need to go green. No vent problems.
__________________
-.-. .- ... .... ..-. .-.. -.-- . .-.
The souls of the righteous are in the hand of God, and no torment will ever touch them.
Old 12-06-2014, 08:16 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #3 (permalink)
Get off my lawn!
 
GH85Carrera's Avatar
 
Join Date: Nov 2007
Location: Oklahoma
Posts: 84,720
Garage
Our vent hose is just three feet long. I have to replace the louvered cover every few years because the sun eats the plastic and turns it to powder. Other than that we clean the lint filter on the dryer for every load.
__________________
Glen
49 Year member of the Porsche Club of America
1985 911 Carrera; 2017 Macan
1986 El Camino with Fuel Injected 350 Crate Engine
My Motto: I will never be too old to have a happy childhood!
Old 12-06-2014, 09:14 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #4 (permalink)
Registered
 
Oh Haha's Avatar
 
Join Date: Oct 2003
Location: Michigan
Posts: 14,093
Seeing as how I am now the "laundry guy" :

I have to clean the pull-out lint catcher thingy every other session or it is full. I blow the rear vent pipe about every 6 months. Ours is only about 6 feet total and connected to the outside with only 2 slight bends.

Keeping the internal lint trap clean will improve the efficiency for faster drying.

I WILL be using our clothesline come summer!
__________________
1981 911SC ROW SOLD - JULY 2015
Pacific Blue

Wayne
Old 12-06-2014, 09:19 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #5 (permalink)
jyl jyl is online now
Registered
 
jyl's Avatar
 
Join Date: Jan 2002
Location: Nor California & Pac NW
Posts: 24,530
Garage
My dryer vent makes one turn, goes up three or four feet, then turns once more and exits the house immediately. Plenty of room to work. No flex hose. But I still complain about it. Face it, dryer vents just don't get much love.
Old 12-06-2014, 09:22 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #6 (permalink)
 
Registered
 
id10t's Avatar
 
Join Date: Mar 2003
Posts: 10,316
Quote:
Originally Posted by GH85Carrera View Post
Our vent hose is just three feet long. I have to replace the louvered cover every few years because the sun eats the plastic and turns it to powder. Other than that we clean the lint filter on the dryer for every load.
Ours too, and we only need about 8 inches of that 3 foot host.
__________________
“IN MY EXPERIENCE, SUSAN, WITHIN THEIR HEADS TOO MANY HUMANS SPEND A LOT OF TIME IN THE MIDDLE OF WARS THAT HAPPENED CENTURIES AGO.”
Old 12-06-2014, 10:36 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #7 (permalink)
Registered
 
Join Date: Jan 2001
Location: So. Cal.
Posts: 9,100
I'm surprised you haven't had real problems with that long of a run and that many turns - especially if most of it is that accordion like flex vent tubing. I can't imagine keeping that all cleaned out. For safety's sake, I would reroute it and try to put in as much smooth ridged tubing as I could. Sound like a real project.
__________________
Marv Evans
'69 911E
Old 12-06-2014, 10:39 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #8 (permalink)
Registered
 
chapo's Avatar
 
Join Date: Aug 2003
Posts: 1,401
Sounds like some of you gifts need the dryer vent clean out. It is plastic with a clear cover and mounts in the wall behind the dryer. They are mandatory for any vent that goes up through the roof. You can see when it needs to be emptied, easy
__________________
Patrick
Old 12-06-2014, 10:48 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #9 (permalink)
least common denominator
 
scottmandue's Avatar
 
Join Date: Aug 2001
Location: San Pedro,CA
Posts: 22,506
Quote:
Originally Posted by jyl View Post
Face it, dryer vents just don't get much love.
You just don't understand! I love my vent and we will be happy together!

But seriously... previous owner ran the vent up and sideways fifteen feet to the side of the building. No doubt so it would be "out of sight and out of mind" however that made for clog city. I ran steel pipe up, over, and out in front of the laundry. Nary a clog since.

Ironically my wife just had me install a clothesline... she is old school.
__________________
Gary Fisher 29er
2019 Kia Stinger 2.0t gone
1995 Miata Sold
1984 944 Sold
I am not lost for I know where I am, however where I am is lost. - Winnie the poo.
Old 12-06-2014, 10:53 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #10 (permalink)
Registered
 
rfuerst911sc's Avatar
 
Join Date: Dec 2002
Location: Dahlonega , Georgia
Posts: 14,567
Quote:
Originally Posted by Evans, Marv View Post
I'm surprised you haven't had real problems with that long of a run and that many turns - especially if most of it is that accordion like flex vent tubing. I can't imagine keeping that all cleaned out. For safety's sake, I would reroute it and try to put in as much smooth ridged tubing as I could. Sound like a real project.
The entire run is steel 4 " pipe/elbows except the flex pipe going from the dryer through the floor. The flex pipe is probably 2 ' long but makes two turns in that 2 ' I believe that is the most restriction in the run. I just need to get off my butt and reroute it to the front of the house. I may install a tee where the flex pipe comes through the floor, my thoughts are maybe I can pop a cap off the tee and run a vacumn cleaner hose up from the basement to clean out the flex pipe. As I get older my desire to wrestle the dryer is less and less
__________________
2002 Boxster S . Arctic silver + black top/int. Jake Raby 3.6 SS engine " the beast ". GT3 front bumper, GT3 side skirts and GT3 TEK rear diffuser. 1999 996 C4 coupe black/grey with FSI 3.8 engine . Rear diffuser , front spoiler lip with ducktail spoiler .
Old 12-06-2014, 12:17 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #11 (permalink)
Registered
 
Join Date: Mar 2004
Location: Los Angeles
Posts: 17,325
Too long and too many bends. A fan (or inline fan) to pull the heat/moisture out of there from the other end maybe necessary. It will aid drying so your dryer wouldn't have to work as hard. The booster fan will sense air pressure and kick on automatically. Fan tech makes an inline booster for dryers. They are the best, quiet and powerful.
Old 12-06-2014, 04:33 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #12 (permalink)
Registered
 
Grog's Avatar
 
Join Date: Dec 2005
Location: Longview, Wa
Posts: 417
That run is too long. I'm surprised that you haven't had a fire yet. I don't remember the exact specs, but I think a dryer vent run can't be more than 30 feet if it is straight. You have to subtract length for 90 degree elbows and 45's.
__________________
1972 Dodge Challenger
2011 Raptor
2013 Road King 110th Anniversary
2014 Corvette Z51 stingray
Single after 27 years married.
Old 12-06-2014, 05:51 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #13 (permalink)
Registered
 
BE911SC's Avatar
 
Join Date: Aug 2009
Location: PNW
Posts: 2,977
My home's laundry is upstairs, second floor. Vent goes into the wall, makes a 90 and drops straight down 15 feet or so under the house (no basement), makes another 90 and goes about 20 feet to the wall where it vents outside. I have a coiled up section of 3" plastic hose that I connect to my industrial portable shop vac, feed the hose in from the outside wall and suck out a huge lint ball every six months or so. I also feed the 3" hose down from the top. My clue for needing to clean it out is that laundry starts taking longer to dry. High-end house built in the mid-1980s, not jerry-rigged. Coincidentally, the dryer just croaked after ten years so another gets delivered on Sunday.
__________________
'84 Carrera Cabriolet
Old 12-06-2014, 05:51 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #14 (permalink)
Did you get the memo?
 
onewhippedpuppy's Avatar
 
Join Date: Mar 2003
Location: Wichita, KS
Posts: 32,263
For starters, I would (and do) empty the internal filter with every load. And I would definitely re-route before you have a fire. I have never needed to clean out my vent tubing, and have lived here for 7 years.
__________________
‘07 Mazda RX8-8
Past: 911T, 911SC, Carrera, 951s, 955, 996s, 987s, 986s, 997s, BMW 5x, C36, C63, XJR, S8, Maserati Coupe, GT500, etc
Old 12-06-2014, 08:11 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #15 (permalink)
Registered
 
Join Date: Nov 2004
Location: Charleston, SC
Posts: 2,357
I clean the screen from the dryer every time I run a load through it. As far as the actual duct, I think I was the first person in years to have cleaned it when I did it about a month ago. I put the leaf blower in there and fired it up, quick and easy. It's cheap flex line and runs about 20 feet with two 90 degree bends + a 45 and dumps out into the bushes. Not a great design.

The washer and dryer are in the garage addition - typical for the 1970s when it was done. I plan on moving them indoors when I redo the master bedroom/bathroom/closets early next year. The only concern I have is with noise. The washer and dryer work great but will probably be too loud unless I can figure out a way to make the laundry room more quiet.
__________________
'87 924S (Sold)
Old 12-07-2014, 04:40 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #16 (permalink)
Banned
 
URY914's Avatar
 
Join Date: Aug 2001
Location: Jacksonville FL
Posts: 50,449
Our vent pipe is PVC and goes from the wall to being cast in the slab and exits low on the outside wall. It has 2 90 degree bends. I found using a long vacuum hose (I duct tape several together) on a shop vac to both blow and suck the lint out works for me.
Old 12-07-2014, 04:55 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #17 (permalink)
You do not have permissi
 
john70t's Avatar
 
Join Date: Aug 2001
Location: midwest
Posts: 39,820
The OP's setup sounds like a downhill run.

Get rid of that flex portion. Make it smooth.

To clean:
Attach a high-flow lightweight round nozzle to a flexible section of hose to a compressor, using fittings.
Take out the filter and run the dryer on low.
Feed hose through the run until it reaches exhaust exit.
Repeat.
Old 12-07-2014, 06:52 PM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #18 (permalink)
Slippery Slope Victim
 
NY65912's Avatar
 
Join Date: Oct 2001
Location: Brooklyn, NY USA
Posts: 4,384
I ran 4" lightwall aluminum tubing and long radius elbows, coupled by hi temp silicone couplings. The line is buried for the most part in the ceiling from an interior wall out straight through to the out side wall. I have two 90°s and then straight out. It still builds a lot of lint. I clean out twice a year.

To the OP....you can get a booster fan to help suck/push through specifically for dryer vent.

I think the lint problem is due to crappy clothing.
__________________
Mike˛

1985 M491

Last edited by NY65912; 12-08-2014 at 04:15 AM..
Old 12-08-2014, 04:11 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #19 (permalink)
UnRegistered User
 
billybek's Avatar
 
Join Date: Dec 2007
Location: Calgary
Posts: 8,016
Garage
That vinyl drier ducting should be outlawed.
Incredible pressure drop through the length even when it is run in a straight line.
Lowers the velocity through the vent. Drier works harder and vent temps are hotter. Results in a fire.
As mentioned before, remove that crap and install a hard vent line with as few fittings as possible.
Tape the fittings together with foil tape and avoid using screws. I know this should be pretty obvious but put the fittings together in the direction of flow so the air enters the fitting or length of pipe without running into an edge. Pipe would slide into the fitting on the entering air side of the fitting.

__________________
Bill K.
"I started out with nothin and I still got most of it left...."
83 911 SC Guards Red (now gone)
And I sold a bunch of parts I hadn't installed yet.
Old 12-08-2014, 04:25 AM
  Pelican Parts Catalog | Tech Articles | Promos & Specials    Reply With Quote #20 (permalink)
Reply

Thread Tools
Rate This Thread
Rate This Thread:

 