Air Medal or two
Propane gas stove inop !
This resembles a wood stove -with a stovepipe, a glass front.
Is pretty simple-
D troop 3/5 Air Cav,( Bastard CAV) and 162 Assult Helicopter Co- (Vultures) South of Saigon, U Minh Forest, Delta, and all parts in between Last edited by afterburn 549; 09-15-2022 at 02:51 AM.. |
Brew Master
Check your inlet pressure to the gas valve. Should be a plug near the main gas line with an allen head. You'll need a gas pressure gauge. On propane systems you can have two gas pressure regulators. One at the tank stepping down the high pressure and then another that drops to your final pressure of around 12" water column. You could have a problem with inlet pressure.
Assuming when you mention you replaced the "regulator" you're talking about the main gas valve. Does it come converted to propane or did you have to install the correct spring to convert the valve?
Nick |
Air Medal or two
To assume or presume is always the wrong thing to do.
I did not replace the reg at the tank, but did replace the Robert Shaw regulator what ever it is under the stove. (Robertshaw) Brand new 600 bucks! none Chinese. It could be line pressure as that is all there is left. The other appliances work fine in the place running off the same tank. I am suspecting perhaps a defective Pile, that is my next guess B4 i call the prooofesionallls
D troop 3/5 Air Cav,( Bastard CAV) and 162 Assult Helicopter Co- (Vultures) South of Saigon, U Minh Forest, Delta, and all parts in between |
Brew Master
Pilot light works so that clears the thermocouple and the pilot side of the valve.
Next steps: Check inlet pressure at the gas valve. On LPG it should be around 11-13 inches water column Check main valve outlet pressure when there's a call for heat. On gas furnaces that's typically in the 11 inch range so I'd think your If you've replaced the valve, thermopile and thermocouple, you're left with a pressure problem. Could be as simple as a plugged burner orifice. But again knowing the inlet and outlet pressure at the valve will really help in troubleshooting. The main valve will only stay open for a very brief period before the flame sensor will close the valve absent any flame. But in that short time, if the main valve opens and you see pressure, the problem is then beyond the valve.
Nick |
Air Medal or two
tapping/wrapping on the regulator under the stove (Robertshaw) will make the thing come on and work normal after that until it shuts off and has to come back on.
I am going to replace the pile just one more time. then it is time for the pressure check
Brew Master
When you've got two gas valves (old and new) and two flame sensors (old and new) acting the same way, the odds of it being the valve or flame sensors is pretty slim. Not saying it's not possible... but the odds are pretty slim. Good luck!
Nick |
That Robertshaw control price is nuts. They are generally around $100...
Greg Lepore 85 Targa 05 Ducati 749s (wrecked, stupidly) 2000 K1200rs (gone, due to above) 05 ST3s (unfinished business) |
Air Medal or two
Thanx thus far folks -
I think I have learned something. I presumed all thermopiles or generators are the same, like thermocouples. Not so? From what I can gather there are different ones for different applications as strange as that seems. So I have ordered the correct part number for this unit. The one I bought the other day was just a generic off-the-shelf at the hardware store. Hope this works new one works on arrival.. If not I will get a pressure gauge and see what it is at the stove. thanx
Brew Master
I'm not well versed in the thermopiles but I think they produce different millivolt outputs.
Nick |
Air Medal or two
It has a pilot light all ok.
The burner will not fire off. Apparently, Thermopiles have different operating ranges depending on which one.
Brew Master
What's the model of the stove you're working on? I'm curious what generates the call for heat .
Nick |
Air Medal or two
Devore Stove.
It is a thermopile next to the pilot and a thermocouple on other side of it . The Tstat closes and the pile is supposed to generate enough electrical power to lift the valve for the propane to come in, and VILOA the burner fires off. No the worst problem in the world, just aggravating.
Ayo Irpin, Ukraine!
Harmlessly passing gas in the grassland away; Only dimly aware of a certain smell in the air |
Ayo Irpin, Ukraine!
Air Medal or two
IDK, they are all just a metal box with the same equipment in them that makes them work (basically)
Brew Master
If you have a V.O.M, check to see how many millivolts the thermopile is producing. It looks like the thermopile should be producing a minimum of 300 millivolts from what I've found.
Also, have you tried putting a jumper in place to bypass the thermostat? And looking at the pilot flame, is there good coverage of the thermopile?
Nick Last edited by cabmandone; 04-05-2022 at 04:23 AM.. |
If that checks out, suspect regulator or pressure. Also, some Robertshaw control units have internal regulators- make sure its set up for lp if that's what your using, or blank it off if using a low pressure regulator ahead of the unit. They sell a blanking plate for that. Went thru all of this with a greenhouse heater recently,.
Air Medal or two
Yes and thanx. the new Thermo flunked the test, that is when I discovered there are different calibrations to be had.
Who knew? Not I!
Air Medal or two
Update-
Fixed. Installed a whole new bracket with the thermocouple, pile, igniter, pilot tube and flame holder and all. This fixed it. Lesson=replace the cheap stuff first.
Brew Master
Was it a bad carryover wing on the old assembly not getting good flame to the new thermopile?
Glad you got it fixed!
Nick |
Thread Tools | |
Rate This Thread | |